Default QOD- 5/31/2007 - Electrical

Q:
The service disconnecting means shall plainly indicate whether it is in ______________ position.

a.) open or closed
b.) tripped
c.) up or down
d.) correct



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #2  
Old 6/1/07, 1:29 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 5/31/2007 - Electrical

missionary?
Reply With Quote
  #3  
Old 6/1/07, 11:05 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 5/31/2007 - Electrical

lololol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 6/2/07, 11:06 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 5/31/2007 - Electrical

240.81 Indicating.
Circuit breakers shall clearly indicate
whether they are in the open "off" or closed "on" position.
Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the "up" position of
the handle shall be the "on" position.

So while some others seem plausible ( lol..I said some..) the answer I was looking for is - A.) Open or Closed





Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 6/2/07, 6:58 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 5/31/2007 - Electrical

Quote:
Originally Posted by pabernathy
240.81 Indicating.


Circuit breakers shall clearly indicate
whether they are in the open "off" or closed "on" position.
Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the "up" position of
the handle shall be the "on" position.

So while some others seem plausible ( lol..I said some..) the answer I was looking for is - A.) Open or Closed




Alright! Today I feel smarter than 11 other people
Reply With Quote
  #6  
Old 6/2/07, 8:49 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 696
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Question Re: QOD- 5/31/2007 - Electrical

Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the "up" position of
the handle shall be the "on" position.

I think this means a standard 240 volt service panel should never be mounted sideways, because you can only put breakers in the lower slots so "up" is "on".
I imagine they are talking single switch panels here? Must be.
Reply With Quote
  #7  
Old 6/2/07, 8:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 5/31/2007 - Electrical

Quote:
Originally Posted by jkogel
I imagine they are talking single switch panels here? Must be.
Most modern panels you can mount "upside down" or "right side up", and comply with the code. Most modern 8 and 12 circuit panels, for instance, must be mounted right side up to comply with the code due to the direction that the breakers operate.

There were panels in the past there the breakers plugged on in two horizontal rows. The top row meets today's operational requirement, but the bottom row is non compliant. Do you all call these out?
Reply With Quote
  #8  
Old 6/2/07, 9:05 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 5/31/2007 - Electrical

John,

Basically they are giving the foundation here for ON being in the UP position and horizontals simply are fine......as for the mounting of a panel sideways...well here is some verbiage on that....

240.33 Vertical Position.
Enclosures for overcurrent devices
shall be mounted in a vertical position unless that is
shown to be impracticable. Circuit breaker enclosures shall be
permitted to be installed horizontally where the circuit breaker
is installed in accordance with 240.81. Listed busway plug-in
units shall be permitted to be mounted in orientations corresponding
to the busway mounting position.

cryptic huh....lol......so lets look at 240.81 to clarify....

240.81 Indicating.
Circuit breakers shall clearly indicate
whether they are in the open "off" or closed "on" position.
Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the "up" position of
the handle shall be the "on" position.

SO basically....an enclosure that contains a single circuit breaker can be mounted horizontally, but an enclosure containing a panelboard/loadcenter with multiple circuit breakers would have to be mounted vertically...based on the nature of the way the OCPD's are in a panel/loadcenter...

Did that clear that up any for ya...




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 6/3/07, 1:30 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 696
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 5/31/2007 - Electrical

Yes thanks. Apparantly plain English is prohibited for code lingo!?
Reply With Quote
  #10  
Old 6/3/07, 4:50 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 5/31/2007 - Electrical

If you mount your distribution panel inside the kitchen cabinet between the shelves behind the vent pipe for the range hood, does that mean it's ok to mount it sideways?
Reply With Quote
  #11  
Old 6/3/07, 5:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 5/31/2007 - Electrical

lol...no it means you have violated the work space before you even got a chance to actually MOUNT it....so you end up putting it somewhere else...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 6/4/07, 3:40 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 5/31/2007 - Electrical

I know!! In the attic!! That way, I can just roll the romex out and drop it where I want it! BTW, I actually ran across this once. The listing in the rag said, "wiring completely updated!!!"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 3:24 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts