  #1  
Old 6/2/07, 10:52 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default QOD- 6/2/2007 - Electrical

Can you tell me what is wrong with this picture.....?

Helpful- yes, It is in a shower Area
Helpful- yes, The recess light is IC Rated

My question is this, Of the factors involved and we know what is allowed and what is not....what would concern you the "MOST" about this install.

See Image Attached. ( Visual Question Of The Day )
P.S. Multiple Answers are allowed....and lets keep it simple folks....no hypotheticals please.
Attached Images
File Type: jpg showerlight.jpg (10.8 KB, 89 views)



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 6/2/07 at 10:56 AM..
Reply With Quote
  #2  
Old 6/2/07, 12:15 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 6/2/2007 - Electrical

answer edited out.... should give people a chance first.
Reply With Quote
  #3  
Old 6/2/07, 5:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 6/2/2007 - Electrical

Give em time fella....we know you know the answer but they are the ones whom it is directed too....which is why I want to keep the HYPOTHETICALS out of it...no what if's...just base it on what they see.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 6/2/07, 5:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: QOD- 6/2/2007 - Electrical

Water splashing on a hot bulb.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #5  
Old 6/2/07, 5:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 6/2/2007 - Electrical

lol.....atleast that WOULD cool it down......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 6/2/07, 6:06 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: QOD- 6/2/2007 - Electrical

...plus it looks like the ceiling (and light) is less than 7' considering the height of typical shower head is 6' 6"/6' 8" or so...wet location rated?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER

Last edited by lkage; 6/3/07 at 10:03 AM..
Reply With Quote
  #7  
Old 6/2/07, 6:07 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 6/2/2007 - Electrical

I said no hypotheticals fella....lol...just the obvious ( FYI...recesses can be within that area under specific conditions )

Notice it says nothing about recess lights or surface mounted lights......other than they must be rated for....well if I said it I would give away 50% of the question....lol





Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 6/2/07 at 6:16 PM..
Reply With Quote
  #8  
Old 6/4/07, 4:22 PM
smedina's Avatar
smedina smedina is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Bolingbrook, IL
Posts: 67
Default Re: QOD- 6/2/2007 - Electrical

I guess my main concern would be cool water splashing on the bulb causing it to burst.
Reply With Quote
  #9  
Old 6/4/07, 5:21 PM
GARY L. RUSK GARY L. RUSK is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 143
Default Re: QOD- 6/2/2007 - Electrical

Light should have a moisture proof/resident cover on it.
Reply With Quote
  #10  
Old 6/4/07, 6:00 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 6/2/2007 - Electrical

fixture not rated for wet location (no lens/cover)
Reply With Quote
  #11  
Old 6/4/07, 11:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 6/2/2007 - Electrical

ok It is late an I am to tired to post tonight...BUT Is no one concerned that a regular bulb is in this fixture that is designed for a reflector bulb...the heat from a standard bulb can cause BIG problems....

I will elaborate more tomorrow.....got back late from the DPOR in Richmond,VA



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 6/5/07, 12:00 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: QOD- 6/2/2007 - Electrical

Paul

I have splashed H2O on IR heat lamps is said holders and taken a shower in glass

Real fun if one is in ones bare feet

Problem is the bulb and the complete rig not for a wet location

I have the same problem in my own bath room but can't make the room larger

Perhaps I just decommission all lights

rlb
Reply With Quote
  #13  
Old 6/5/07, 6:22 AM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: QOD- 6/2/2007 - Electrical

Quote:
Originally Posted by rbennett
Paul

I have splashed H2O on IR heat lamps is said holders and taken a shower in glass

Real fun if one is in ones bare feet

Problem is the bulb and the complete rig not for a wet location

I have the same problem in my own bath room but can't make the room larger

Perhaps I just decommission all lights

rlb
You should have had it inspected NACHI style before you moved in. LOL
Reply With Quote
  #14  
Old 6/5/07, 9:20 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: QOD- 6/2/2007 - Electrical

Ok...sorry for the delay..

1.) The luminare needs to be rated for Damp Locations and we can't really determine that because we can't see inside ( no hypo's ) so as a good inspector suggesting a Vapor Trim to ensure it is rated for damp locations would be the best course of action....now in regards to that bulb...it will not radiate heat out away from the fixture as it should with a standard bulb in it...this is a fire hazard.....it should be replaced with a reflector type bulb of proper wattage ( usally 65W to 75W ..but depends on the luminare )....anyway a standard bulb should never be in a recess light.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 6/5/07, 9:35 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: QOD- 6/2/2007 - Electrical

Good info Paul, I never thought about the bulb heat before.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Some good questions that always need answers jtedesco1 Electrical 5 6/16/06 10:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 8:50 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts