Default QOD- 8/28/2007 - Electrical

QUESTION -

The dedicated equipment space for electrical equipment that is required for panelboards is measured from the floor to a height of _______ above the equipment, or to the structural ceiling, whichever is lower.

a.) 3 ft
b.) 6 ft
c.) 12 ft
d.) 30 ft



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #2  
Old 8/29/07, 11:54 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

OK guys........read the question. Some are seeming to assume WIDTH or DEPTH in this question...it refers to HEIGHT only.......STOP...BREATH and READ!



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #3  
Old 8/29/07, 5:31 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,037
Default Re: QOD- 8/28/2007 - Electrical

Quote:
Originally Posted by pabernathy
QUESTION -

The dedicated equipment space for electrical equipment that is required for panelboards is measured from the floor to a height of _______ above the equipment, or to the structural ceiling, whichever is lower.

a.) 3 ft
b.) 6 ft
c.) 12 ft
d.) 30 ft
Hey Paul,
I read it three times before I "voted" based on the above words (in red). Maybe the question is confusing others???
Reply With Quote
  #4  
Old 8/29/07, 8:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

It should not....the question was CLEARLY stated from the floor to the space ABOVE the panel or structual ceiling...not out from it.....or from side to side....again it states:

Quote:
is measured from the floor to a height of _______ above the equipment, or to the structural ceiling, whichever is lower.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 8/29/07, 8:03 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

Now...where the h*ll someone got 12' from lord only knows....lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 8/29/07, 8:32 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

Ok.....this was my last QOD guys......hope you enjoyed it and best of luck in the future.

Oh...the answer was 6'........which is Answer b.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 8/29/07, 10:08 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,307
Default Re: QOD- 8/28/2007 - Electrical

Paul

Electronics and electrical has been my profession since I was able to melt solder in 1952

The logical order of things - the on and off - way - what this area of science has done for mankind etc.

I wish others would become knowledgeable in this area of physics -- it would change how they argue - fight and vote

Sorry to see that you are know longer going to post QOD - I have learned even with all that I already know -

BTW Why no more QOD's -- you can PM me if you wish

rlb
Reply With Quote
  #8  
Old 8/29/07, 10:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

lol...just lost the desire to have anything to do with the so called Education Committee. I will leave that to the others and respectfully ask Mr. Gromicko to remove my name from the committee....

It appears that the need for educators itself within this association is going by the wayside so I just prefer to dedicate my time and efforts somewhere else right now. I will leave the QOD's to our resident educational authorities.

But now you KNOW i love a good conversation old friend....so lets chat VOLTAGE anytime.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 8/29/07, 10:20 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,307
Default Re: QOD- 8/28/2007 - Electrical

And to you sir -- Fair winds and following seas

Catch you later down the line

rlb
Reply With Quote
  #10  
Old 8/30/07, 12:50 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: QOD- 8/28/2007 - Electrical

Quote:
Originally Posted by pabernathy
Ok.....this was my last QOD guys......hope you enjoyed it and best of luck in the future.
Don't be such a sorehead Paul. Your questions are fine.
Reply With Quote
  #11  
Old 8/30/07, 12:51 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

lol...sorehead...lol...me not wanting to post anymore QOD has nothing to do with the questions...lol.....but has all to do with the fact no real education committee really exists....so frankly I got better things to do....nothing more.

Actually I may do another QOD...but if I do another one at some point I will SURLY make it so that everyone can see how everyone else posts.....so the guy who picked 30' can leave the industry....lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 8/30/07, 3:03 AM
W. Michael Chris's Avatar
W. Michael Chris W. Michael Chris is offline
InterNACHI Member
 
Join Date: May 2005
Location: Santa Clara, UT
Posts: 1,115
Default Re: QOD- 8/28/2007 - Electrical

Paul,

I think the guys answering 30' was just messy with ya. Thanks for all you done, many of us appreciate your QOD . . . good luck to you.



Mike Chris, Santa Clara, Utah
NACHI: #05051385
HouseNspect@gmail.com
www.housenspect.com
activerain

"A man's home is his castle . . . until the queen arrives."
Reply With Quote
  #13  
Old 8/30/07, 9:53 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

Thats the point...NACHI does not take Electrical Issues or Safety seriously.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 8/30/07, 11:27 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: QOD- 8/28/2007 - Electrical

Quote:
Originally Posted by pabernathy
Thats the point...NACHI does not take Electrical Issues or Safety seriously.
I hope that is not true Paul. The recent hazards course does show that there is a concern for the safety of NACHI and non-NACHI inspectors IMHO.
Reply With Quote
  #15  
Old 8/30/07, 11:36 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: QOD- 8/28/2007 - Electrical

Safety as a whole yes.....Electrical Safety in General....nope. It should be a fundamental demand to gain higher knowledge of all things and Electrical Issues should be at the TOP of the heap in my opinion.

Based on the MANY calls I get....it is far from the top of the heap but then again it is only my opinion and basically another reason the education committee is non-existant really.

Again...all opinions.....but alas......it is not just the HI industry as even electricians who are technically qualified lack education in electrical safety as required by the NEC.....so not really a one picture thing....just an observation really.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical Inspections 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM