View Poll Results: Dryer Vents
15 Feet 2 8.70%
20 Feet 2 8.70%
25 Feet 19 82.61%
31 Feet 0 0%
Voters: 23. You may not vote on this poll

Reply
 
LinkBack Thread Tools
  #1  
Old 9/9/10, 7:24 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Qod 9-9-2010

A dryer vent should extend no more than ___ feet.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/9/10, 8:15 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Qod 9-9-2010

Quote:
Originally Posted by gbell View Post
A dryer vent should extend no more than ___ feet.
Generally speaking, but there are always exceptions, for longer and shorter runs.
Reply With Quote
  #3  
Old 9/9/10, 10:57 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Qod 9-9-2010

irc and imc have a 10' difference
bottom of this page



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #4  
Old 9/9/10, 11:56 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Qod 9-9-2010

25 based on IRC. Reduce 5ft for each 90 and 2 1/2ft for each 45 bend.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #5  
Old 9/9/10, 12:43 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Qod 9-9-2010

Quote:
Originally Posted by badair View Post
irc and imc have a 10' difference
bottom of this page
too bad 35' is not a choice smarty pants......

Hey Barry.
Reply With Quote
  #6  
Old 9/9/10, 1:05 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Qod 9-9-2010

Follow the manfacture specifications ..



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 9/9/10, 1:17 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Qod 9-9-2010

Quote:
Originally Posted by bkelly2 View Post
too bad 35' is not a choice smarty pants......

Hey Barry.
Sometimes it is.
M1501.3 IRC
Where the make and model of the clothes dryer to be installed is known and the manufacturer's installation are provided, the maximum length of the exhaust duct, shall be in accordance with the dryer manufacrturer instructions.
More and more newer dryers are capable of more than the 25'.

And here is a dryer box Barry is talking about.

Reply With Quote
  #8  
Old 9/9/10, 1:49 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Qod 9-9-2010

Quote:
504.6.4.1 Specified length. The maximum length of the
exhaust duct shall be 35 feet
(10 668 mm) from the connection
to the transition duct from the dryer to the outlet
terminal. Where fittings are used, the maximum length
of the exhaust duct shall be reduced in accordance with
Table 504.6.4.1 http://www.dryerbox.com/convertions/...haust_Duct.pdf
TABLE

I believe Barry was referring to this at the bottom of the page.
Reply With Quote
  #9  
Old 9/9/10, 2:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Qod 9-9-2010

I know, I read it.
I was showing what a dryer box was and why at occasions, the dryer vent can exceed 25 ft.
Manufactures instructions dictate that.

Now for a scenario, Maine has mostly cellars, or basements, and that is where you have the dryers most of the time.
Now using the 25 foot rule, that means if the dryer is not installed against the exterior foundation wall at all times with its back to, it will not meet that requirement.
25' is the rule of thumb or code per IRC, so now deduct two 90's, that is 10', and deduct another 90, cause the flex is crumbled and pinched in the back of the dryer hook-up, and that is another 5'.

So you are left with a 10' straight section of duct that you can use.

I will tell you right now that over 75% of dryers in this area do not meet that criteria.
The dryer box saves on the lineal footage and eliminates pinching.

Manufacturer's instructions will prevail on the installation and I am careful on calling out this as a defect, since we can not site Code or should not.
Reply With Quote
  #10  
Old 9/9/10, 2:21 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Qod 9-9-2010

Quote:
Originally Posted by rcooke View Post
Follow the manfacture specifications ..
I agree.

http://www.appliance411.com/faq/dryer-vent-length.shtml



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 9/9/10, 2:23 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Qod 9-9-2010

Check this out here, might think different about the IRC requirement part that we are limited to 25'.

http://www.appliance411.com/faq/drye...th.shtml#chart
Reply With Quote
  #12  
Old 9/9/10, 8:21 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Qod 9-9-2010

IRC Code says says 25' or Manufactures Instructions, so calling out Manufacutrers Instructions is Citing Code in a round about way.



M1502.4.4 Duct length. The maximum allowable exhaust
duct length shall be determined by one of the methods
specified in Section M1502.4.4.1 or M1502.4.4.2.
Quote:
M1502.4.4.1 Specified length. The maximum length
of the exhaust duct shall be 25 feet (7620 mm)from the
connection to the transition duct from the dryer to the
outlet terminal. Where fittings are used, the maximum
length of the exhaust duct shall be reduced in accordance
with Table M1502.4.4.1.

M1502.4.4.2 Manufacturer’s instructions. The size
and maximum length of the exhaust duct shall be determined
by the dryer manufacturer’s installation instructions.
The code official shall be provided with a
copy of the installation instructions for the make and
model of the dryer at the concealment inspection
. In the
absence of fitting equivalent length calculations from
the clothes dryer manufacturer, Table M1502.4.4.1
shall be used.
Reply With Quote
  #13  
Old 9/9/10, 8:28 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,798
Default Re: Qod 9-9-2010

Never new that installing something per Manufacturers installation manual was a round about Code.
That is a new one on me Brian.

Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/9/10, 8:31 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Qod 9-9-2010

Quote:
Originally Posted by mcyr View Post
Never new that installing something per Manufacturers installation manual was a round about Code.
That is a new one on me Brian.

Good discussion, gets me thinking...I do not have an 09 IRC copy yet myself and will have to get one.

I do not recall seeing this requirement before either....

Quote:
M1502.4.5 Length identification. Where the exhaust
duct is concealed within the building construction, the
equivalent length of the exhaust duct shall be identified
on a permanent label or tag. The label or tag shall be
located within 6 feet (1829mm) of the exhaust duct connection.
Reply With Quote
  #15  
Old 9/9/10, 8:33 PM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Re: Qod 9-9-2010

It is great to see so much discussion over what I thought was such a simple question.

Thanks to all of you that participated.



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
InterNACHI booth at Wood Fair 2010 in Guangzhou, China in March 26-28, 2010. gromicko Green Building Inspections 3 11/13/09 12:45 PM
FLORIDA HI licensing/ 2010 jacaron Legislation, Licensing & Legal Issues for Inspectors 5 9/7/09 5:07 PM


All times are GMT -4. The time now is 12:51 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts