#16
|
||||
|
||||
|
It was a great question Greg, thank you for posting it.
|
| Need a home inspection in Idaho? Check out InterNACHI's listing of Idaho certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#17
|
||||
|
||||
|
That's how inventions are made Greg, talking about it.
Big difference on slab living and Basements. Utilities all end up in a basement, and conditions are not allways conducive to the IRC, so other means of adaption are necessary like design around Manufactures specifications and sometimes adding inline fans made for dryer exhaust. The last condo I inspected the exhaust duct was concealed and the run was about 40' and was disconnected in the wall behind the dryer. The client was the Assistant Chief of the Fire Department for my Town. All he said was "Wow". LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#18
|
||||
|
||||
|
On a recent commercial job I saw a 50 foot dryer vent approved on the plans with a certain residential dryer listed. I don't remember the manuf. but it was a residential unit.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#19
|
||||
|
||||
|
I just want to point out that even though there are other options you have to choose what would be the correct answer from the ones available. Many tests given for certification have similar questions that have several answers that are not listed on the test.
Greg Bell Titusville, Fl 02111507 Serving Central Florida
|
|
#20
|
|||
|
|||
|
Please Note:
James Smith 6418 is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am a licensed contractor in the state of California. There is the IRC and the IMC. However we are sup post to go by cities codes and the city where i am from goes by CMC. Which is a different company. I have checked other cities and they go by the same. Which is 14 feet Not counting two elbows.Only two elbows are allowed. However when i spoke to the city inspector.He said there is exceptions. The inspector will not pass anything different. Unless You have an engineer sign's off on it. If the engineer signs saying it will work. The inspectors are forced to sign it two. The problem with this is it really does not work for most dryers. Some dryers have really strong air flow and some do not. If you install a venting system for a Maytag (just examples).But that person sells the house and someone uses a roper(just example).That is where there becomes a problem. Where the maintenance costs are higher to maintain that system. Are you have to do a reroute. I find some systems that are signed off.That uses 6 inch and goes 35 to 40 feet. And no dryer will work very well even brand new. I have customers tell me they bought the house brand new. And it took and hour to dry the cloths. That is just wrong. They leave the customer stuck with a problem on a new house. Something needs to be done to stop this from continuing.Thank you and i hope this help.If you have any questions just let me know. I would be glad to help. I work with inspectors in my area to help.
|
|
#21
|
||||
|
||||
|
I came up with this:
The International Mechanical Code article 504.6 stipulates the requirements for Domestic clothes dryer ducts. In brief, the maximum length of duct permitted is 25 ft. This maximum length should be reduced by 2.5 ft for each 45-degree bend and 5 ft. for each 90-degree bend. The duct should be a minimum nominal size of 4 inches in diameter and shall have a smooth interior finish. Drew Levy NJ# 24GI00101400 Radon # MET12929 Homespect LLC (609) 668-7588 http://www.homespectllc.com http://www.philadelphiahomeinspection.net http://www.southjerseycommercialinspection.com http://www.haddonfieldhomeinspection.com http://www.abseconhomeinspection.com http://www.willingborohomeinspector.com http://www.thehomeinspectioninstitute.com |
|
#22
|
||||
|
||||
|
Appears the 2009 edition changed it;
504.6.4.1 Specified length. The maximum length of the exhaust duct shall be 35 feet (10 668 mm) from the connection to the transition duct from the dryer to the outlet terminal. Where fittings are used, the maximum length of the exhaust duct shall be reduced in accordance with Table 504.6.4.1 LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#23
|
||||
|
||||
|
Quote:
ahh Marcel, this is not from the IRC my friend. |
|
#24
|
||||
|
||||
|
The correct answer is 25 ft.
Greg Bell Titusville, Fl 02111507 Serving Central Florida
|
![]() |