Default 30 amp service

I inspected a house today with a main panel (upstream of the distribution panel) which had been sealed shut by an electrical authority...... so I could not open the box to examine the supply mains or the fuses.

However, the front of the box had a label that identified the maximum design amperage as 50 amps. So I have to assume that the service to the house is 30 amps. (can't be 60)

The house has an air conditioner, electric stove, and electrical service to the detached garage.

All of the wiring is un-grounded. No knob and tube visible.

How plausible is it that the service is really 30 amps?
Reply With Quote
  #2  
Old 5/30/08, 8:27 AM
William R. DeVries, CMHI's Avatar
William R. DeVries, CMHI William R. DeVries, CMHI is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Kingston
Posts: 998
Default Re: 30 amp service

it's my understanding that with less then 100amp the home would be un insurable? but from what you have in front of you , you may have found a home that fell between the cracks



ASNT Certified Level II Thermographer
Certified Mold Inspector (Pro-Lab)
Certified Mold Inspector IAC2
Certified Home Inspector INACHI 07040201
Commercial Property Inspection
Certified Master Home Inspector
2008 InterNACHI member of the year



Magnum Property Inspection
Inspect it before you buy it
613 561 5327 office
613 929 9919 mobile
We use and recommend
Home Inspector Pro Software
HomeGauge Software
Reply With Quote
  #3  
Old 5/30/08, 8:58 AM
Joseph D. Skrypka's Avatar
Joseph D. Skrypka Joseph D. Skrypka is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Hamilton, ON
Posts: 147
Default Re: 30 amp service

Hi Bill

I suspect that the previous owner (deceased) lived in this house for the last 40+ years. So the insurer probably did not question his electrical system during the annual renewal process.

But now that it's changing hands, it'll come up.
Reply With Quote
  #4  
Old 5/30/08, 9:30 AM
Bill Mullen Bill Mullen is offline
Active Poster
 
Join Date: Jan 2004
Location: Sarnia, ON
Posts: 1,426
Please Note: Bill Mullen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30 amp service

Joe:

Why do you say 30 Amp and not 50 Amp ??

We still have a few 50 Amp cottages in Sarnia.

Bill Mullen
Reply With Quote
  #5  
Old 5/30/08, 9:38 AM
Joseph D. Skrypka's Avatar
Joseph D. Skrypka Joseph D. Skrypka is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Hamilton, ON
Posts: 147
Default Re: 30 amp service

Thanks Bill

I've never seen a 50 amp install.

Always an education.
Reply With Quote
  #6  
Old 6/1/08, 3:31 AM
William R. DeVries, CMHI's Avatar
William R. DeVries, CMHI William R. DeVries, CMHI is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Kingston
Posts: 998
Default Re: 30 amp service

Bill you have just widened the crack,



ASNT Certified Level II Thermographer
Certified Mold Inspector (Pro-Lab)
Certified Mold Inspector IAC2
Certified Home Inspector INACHI 07040201
Commercial Property Inspection
Certified Master Home Inspector
2008 InterNACHI member of the year



Magnum Property Inspection
Inspect it before you buy it
613 561 5327 office
613 929 9919 mobile
We use and recommend
Home Inspector Pro Software
HomeGauge Software
Reply With Quote
  #7  
Old 6/1/08, 7:51 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: 30 amp service

I want to see 100 Amps minimum or it simply gets deferred.
Reply With Quote
  #8  
Old 6/4/08, 1:24 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30 amp service

A mobile home I inspected recently had a 50 Amp main breaker. My clients negotiated for and got a new service installation.

John Kogel
www.allsafehome.ca

Last edited by jkogel; 6/4/08 at 1:41 AM..
Reply With Quote
  #9  
Old 6/5/08, 12:51 AM
Charles R. N. Crooker's Avatar
Charles R. N. Crooker Charles R. N. Crooker is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Brantford, ON
Posts: 822
Default Re: 30 amp service

Quote:
Originally Posted by jskrypka
Thanks Bill

I've never seen a 50 amp install.

Always an education.
70 Amp are around too!! Agents call them 100 as that is what is printed on the front.



Chuck Crooker I.M.M., Canadian Home Inspectorhttp://www.crookerhancox.com "Not just an inspection, an Education!!!"
Reply With Quote
  #10  
Old 6/5/08, 9:42 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: 30 amp service

Quote:
Originally Posted by ccrooker
70 Amp are around too!! Agents call them 100 as that is what is printed on the front.
That's funny.

I get a lot of R/E agents and Buyers telling me that the electrical (coming into the home) is 220 Amps.

I then explain the difference between volts and amperage.
Reply With Quote
  #11  
Old 6/5/08, 9:50 AM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is online now
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,105
Default Re: 30 amp service

Quote:
Originally Posted by jskrypka
I inspected a house today with a main panel (upstream of the distribution panel) which had been sealed shut by an electrical authority...... so I could not open the box to examine the supply mains or the fuses.

However, the front of the box had a label that identified the maximum design amperage as 50 amps. So I have to assume that the service to the house is 30 amps. (can't be 60)

The house has an air conditioner, electric stove, and electrical service to the detached garage.

All of the wiring is un-grounded. No knob and tube visible.

How plausible is it that the service is really 30 amps?
It does not appear to be a 30A service by your description, as I recall 30A services were 2-wire 120V systems, it has been a long time since I saw one mind you.



"By three methods we may learn wisdom: First, by reflection, which is noblest; Second, by imitation, which is easiest; and third by experience, which is the bitterest." -Confucius


Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
  #12  
Old 6/6/08, 1:48 AM
dcook1's Avatar
dcook1 dcook1 is offline
Active Poster
 
Join Date: Feb 2007
Location: Stayner, On
Posts: 949
Please Note: dcook1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30 amp service

Quote:
Originally Posted by jkogel
A mobile home I inspected recently had a 50 Amp main breaker. My clients negotiated for and got a new service installation.

John Kogel
www.allsafehome.ca
John states 50 Amp main breaker Those panels and breaker were made in Manitoba for a few years. THere are 50 AMP sevices out there.
If it less than 100 AMP service, just mention you recomend an upgrade, but advise the client an insurance company may demand an upgrade.
Reply With Quote
  #13  
Old 6/9/08, 1:47 PM
Vern Mitchinson, CMI's Avatar
Vern Mitchinson, CMI Vern Mitchinson, CMI is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 1,998
Default Re: 30 amp service

As per the 19th edition of the Canadian Electrical Code A 60 amp main breaker is acceptable for any house up to 861 Sq ft (80 sqM).
A 100 amp is required from 861 sq ft to 3875 Sq ft.
Above 3875 size is not listed.
If electrical heating then the size goes up to meet the heating demand.
I warn all clients when the breaker is less than 100 that the insurance co may object to less then 100 amp.
PS How is it that the insurance co can over ride the code?
Reply With Quote
  #14  
Old 6/9/08, 9:12 PM
dplummer dplummer is offline
Active Poster
 
Join Date: Dec 2003
Location: Collingwood, ON
Posts: 236
Please Note: dplummer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30 amp service

State Farm Insurance doesn't seem to have a problem with cottages that have a 50 amp service.Lot's of them in Wasaga Beach.
Doug
Reply With Quote
  #15  
Old 6/9/08, 9:29 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 30 amp service

Quote:
Originally Posted by vmitchinson
As per the 19th edition of the Canadian Electrical Code A 60 amp main breaker is acceptable for any house up to 861 Sq ft (80 sqM).
A 100 amp is required from 861 sq ft to 3875 Sq ft.
Above 3875 size is not listed.
If electrical heating then the size goes up to meet the heating demand.
I warn all clients when the breaker is less than 100 that the insurance co may object to less then 100 amp.
PS How is it that the insurance co can over ride the code?
They are writing a financial contract with the client and since there are holding most of the cards in this game, they call the shots. Can always go beyond code........the least we let them get away with!!!!

Last year had an engineer vendor who was going to challenge the insurance industry after I found about 50-60% K&T wiring in his house.

I said it would cost from $7-10 grand to replace it and patch/paint any damaged surfaces. He had the local POCO inspect it and pass it! That really got his back up and he stated even stronger that he would fix this!!

About 3 days later the house sold for $10,000 off the previously agreed to price!!! So much for fighting some things!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 9:16 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 8:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 11:41 PM


All times are GMT -4. The time now is 4:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts