Default Access to Electrical Panel in Ontario by HVAC Contractors

The HVAC industry succeeded last fall in getting a clarification from the Ontario Ministry of Training, Colleges and Universities (MTCU) on the matter of accessing the electrical panel. Director of Apprenticeship Rob Easto concluded that refrigeration mechanics (and residential AC mechanics) are trained sufficiently to do limited work in the electrical panel (in residences only) in a safe and competent manner.

This interpretation was challenged late in 2006 by the electrical contracting sector, which has alleged that HVAC contractors are not properly qualified to do this work and that it should only be done by licensed electricians. The outcome of this issue will have an impact on the requirement imposed by the Electrical Safety Authority (ESA) for any contractor who applies for electrical permits (including HVAC contractors) to be registered under their new Electrical Contractor Registry Authority (ECRA). Registration with ECRA currently requires that contractors employ a Master Electrician. If the MTCU decision stands, this requirement for an electrician will be removed for HVAC contractors. The ESA agreed to extend the registration deadline (originally January 1, 2007) indefinitely, pending a decision from the MTCU. HVAC contractors are still awaiting a final decision.

In March, electrical contractors (led by the Ontario Electrical League) initiated an aggressive letter-writing campaign, urging member contractors to write to their MPPs with the message that public safety will be threatened if HVAC contractors are permitted to do this work.

Meanwhile, ESA has reaffirmed that their approach to the HVAC sector will continue to be “business as usual” until a decision from the MTCU is received. According to Peter Marcucci (ESA Vice President, Regulatory Affairs):

“Until this decision is made and implemented, ESA will continue its current practices associated with the issuance of permits to HVAC contractors. Once a decision has been made with respect to the licensing requirements for HVAC contractors we will provide the appropriate direction and allow time to make any needed transition.”

Nalliah Thayabharan
Expert Building Inspections Ltd
Markham ON
Reply With Quote
  #2  
Old 4/19/07, 3:50 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Thanks...Nalliah
Interesting information... Roy Cooke
Reply With Quote
  #3  
Old 4/19/07, 7:22 AM
Douglas Cossar Douglas Cossar is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Whitby, On
Posts: 805
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Sounds like the electrical contractors took a page out of the CAHPI book
But they made it mandatory!

oh well.....................



Doug Cossar CMI, PHPI
Accurate Home Inspection
Services Inc.
Whitby Ontario
www.accuratehomeinspections.ca
05021384
Reply With Quote
  #4  
Old 4/19/07, 8:39 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

..and inspectors are not modifying or installing they are only removing cover plates and visually examining. Got to love Unions eh!
Reply With Quote
  #5  
Old 4/19/07, 9:22 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Quote:
Originally Posted by rwand1
..and inspectors are not modifying or installing they are only removing cover plates and visually examining. Got to love Unions eh!
This had nothing to do with the Electrical union .
This is an ESA decision .
If this gets in forced it sure could remove a lot of liability of the Ontario Home Inspectors .
In Court Why did you not identify the Aluminum wire ,
Sorry sir the law states I am not allowed to remove any covers . End of story .
This is now going to be harder for insurance companies to charge more or refuse to give insurance to homes with aluminum wire .
When they ask does the home have Aluminum wire sorry sir no way to confirm if the home has aluminum or does not have aluminum.
I also do no think AC installers should be doing electric wiring . I have found two where they have run two feeds of #14 as they did not have any # ten wire .
I have found many where they have just tied the AC feed into the Mains .
This gives protection to the AC feed of 100 or 200 amps depending on size of service.
The law also says a home owner can do work on his own home if he gets a permit first ,Yea like this is going to happen .
The law also says all new water heater tank instillations require a balancing valve .
Have not seen one yet on a replacement tank instillation .
Roy Cooke

Roy Cooke
Reply With Quote
  #6  
Old 4/19/07, 9:49 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Quote:
In March, electrical contractors (led by the Ontario Electrical League) initiated an aggressive letter-writing campaign, urging member contractors to write to their MPPs with the message that public safety will be threatened if HVAC contractors are permitted to do this work.
Okay Electrical League which is a body which represent electrical workers.
Reply With Quote
  #7  
Old 4/19/07, 10:26 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Quote:
Originally Posted by rwand1


Okay Electrical League which is a body which represent electrical workers.
No it is not ,the electrical league represents Electrical contractors.

(IBEW)... International brotherhood of Electrical Workers represent the Electricians .
I am a retired Member in good standing of the IBEW .

In most cases they are on exact opposite sides of each other.
</IMG>.
There are many electricians who do not belong to the Union .
There are many contractors who do not use Union labour.

Roy Cooke
Reply With Quote
  #8  
Old 4/19/07, 10:35 AM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, Ab
Posts: 1,146
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

I did an inspection yesterday and found 5 double taps. 2 breakers had 14/3 connected and the other three had 14/2.
Who are these guyes protecting when this kind of stuff is forbidden to be found during the home inspection.
We all work to protect our terf. It's the dump assed government that makes this garbage law that is the problem.
Reply With Quote
  #9  
Old 4/19/07, 10:37 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Quote:
Originally Posted by vmitchinson
I did an inspection yesterday and found 5 double taps. 2 breakers had 14/3 connected and the other three had 14/2.
Who are these guyes protecting when this kind of stuff is forbidden to be found during the home inspection.
We all work to protect our terf. It's the dump assed government that makes this garbage law that is the problem.
Exactly and they are trying to do it to the Canadian Home Inspection Industry also .
Roy Cooke
Reply With Quote
  #10  
Old 5/20/07, 10:24 PM
Nalliah Thayabharan Nalliah Thayabharan is offline
New User
 
Join Date: Mar 2007
Location: Markham Ontario
Posts: 29
Please Note: Nalliah Thayabharan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

MTCU Director of Apprenticeship, Rob Easto, announced that he will not adjust the interpretation he provided in October. In making this decision, Easto cited a number of factors which guided the Ministry’s decision:

"First, and perhaps foremost, the Ministry is satisfied that O. Reg. 75/05 (Refrigeration and Air Conditioning Mechanic) provides for mechanics to perform specific electrical work. I refer to section 3 of that regulation – scope of trade. The Ministry’s interpretation sets out the electrical work involved in refrigeration unit installation and start up and establishes limits with regards to who can perform this work. Mechanics are not permitted to perform electrical work beyond the conditions set out in the interpretation. Specifically, the residential mechanic is permitted to perform electrical work (connect to the panel) where there is existing capacity but is not permitted to modify an existing panel."

"The Ministry is satisfied that this work is being performed safely by qualified mechanics. The Refrigeration and Air Conditioning Mechanic (commercial and residential) training and curriculum standards already include substantive electrical training. Given the concerns raised by the Electrician PAC, the Ministry will undertake to work with industry to review all training material and make changes as necessary to ensure there is no ambiguity with regards to training to perform this specific work."

This decision will not eliminate the requirement for HVAC contractors to register with the Electrical Safety Authority (ESA) under their new Electrical Contractor Registry Authority (ECRA). However, it will have an impact on the requirement imposed by ESA that contractors who register must employ a Master Electrician. The MTCU decision means this requirement for an electrician will be removed for HVAC contractors, provided they work within the limits described in the MTCU decision.
Immediately after the MTCU decision was issued, ESA stated the following: “We have not yet had a chance to determine how we will operationalize this decision from a contractor licencing perspective. So, until such time as we do, the same direction previously provided… will apply.”
The previous direction from ESA was that HVAC contractors could continue to pull electrical permits and schedule inspections without registering under ECRA until further notice.
HVAC contractors are now working with ESA to ensure that the registration procedure for HVAC contractors will be workable and will reflect the Ministry’s decision.
Nalliah Thayabharan
Markham ON
Reply With Quote
  #11  
Old 5/21/07, 4:01 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Access to Electrical Panel in Ontario by HVAC Contractors

Roy:

The law also says all new water heater tank instillations require a balancing valve

Do you mean a temperature control or "mixing" valve to add cold water to the hot to prevent scalding?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
It's not necassary to remove Electrical Panel Cover. dvalley Electrical 13 7/3/07 4:22 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 4:05 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts