Default Almost ended up in a fist fight with contractor

Hi Guys!

I did a home inspection yesterday that almost ended up in a fist fight between me and the contractor. see the pics below and tell me what is wrong here

ok, first ting : flooring. presswood is good for flooring he said....then i said show me de drawing (plans) and he did. on the plan it was mentionned : use plywood 5/8 thick....then he went nuts....

for the other pics , tell me what you see....

(Client was REALLY HAPPY)



almost-ended-up-fist-fight-contractor-2010_07230028.jpg

almost-ended-up-fist-fight-contractor-2010_07230026.jpg

almost-ended-up-fist-fight-contractor-2010_07230027.jpg

almost-ended-up-fist-fight-contractor-2010_07230034.jpg

almost-ended-up-fist-fight-contractor-2010_07230033.jpg
Reply With Quote
Need a home inspection in British Columbia? Check out InterNACHI's listing of British Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/24/10, 1:22 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by pmassie View Post
Hi Guys!

I did a home inspection yesterday that almost ended up in a fist fight between me and the contractor.

Immediately.......take INACHI's self-defense series of courses!!!!


see the pics below and tell me what is wrong here

ok, first ting : flooring. presswood is good for flooring he said....then i said show me de drawing (plans) and he did. on the plan it was mentionned : use plywood 5/8 thick....then he went nuts....

He is nuts if he substituted the subfloor material without a change order. It's not like OSB board is a bad subfloor but to try to slip in a cheaper product without the homeowner's permission......NUTS, he is!!

for the other pics , tell me what you see....

(Client was REALLY HAPPY)



Attachment 38126

Attachment 38127

Attachment 38128

Attachment 38129

Attachment 38130
Looks like the butcher.......er......plumber should be in the meat trade.

Was installing an HRV in a new home for an aquaintance 3 years ago. The plumber......er...butcher had cut though 3- 2x8" floor joist for his 3" toilet drain. Called the owner who called the inspector and a fix was agreed on. The plumber was a part-timer whose day job was.......you guessed it....a butcher at a local supermarket!
Reply With Quote
  #3  
Old 7/24/10, 3:15 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Almost ended up in a fist fight with contractor

Should note that duct tape plumbing repairs should not be made until the house is at least 10 years old.
Reply With Quote
  #4  
Old 7/24/10, 3:18 PM
Curtis M. Vilt's Avatar
Curtis M. Vilt Curtis M. Vilt is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palmetto Florida
Posts: 890
Default Re: Almost ended up in a fist fight with contractor

I would think 3/4" T&G OSB is better than 5/8 ply. Looks like the only good thing he did
Reply With Quote
  #5  
Old 7/24/10, 3:33 PM
Bert B. de Haan Bert B. de Haan is offline
InterNACHI Member
 
Join Date: May 2010
Location: Arthur Ontario Canada
Posts: 122
Default Re: Almost ended up in a fist fight with contractor

I have no problem with T&G OSB subfloor. Not if the specs call for plywood though. Some of the other defects are great. I especially like the notch in the beam.



Benchmark Home Inspection Services.
http://www.KitchenerWaterlooHomeInspector.ca Kitchener-Wateroo and Guelph area Home Inspection
Serving Kitchener-Waterloo, Guelph, Orangeville, Mount Forest and surrounding areas.
Reply With Quote
  #6  
Old 7/24/10, 4:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by bdehaan View Post
I have no problem with T&G OSB subfloor. Not if the specs call for plywood though. Some of the other defects are great. I especially like the notch in the beam.
Though allowed in I joists.
Reply With Quote
  #7  
Old 7/24/10, 4:07 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is online now
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by belliott View Post
Though allowed in I joists.
A notch?



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #8  
Old 7/24/10, 5:29 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by rnewland View Post
A notch?
No,of course not.
I was referring to the web.
Reply With Quote
  #9  
Old 7/24/10, 5:31 PM
Bert B. de Haan Bert B. de Haan is offline
InterNACHI Member
 
Join Date: May 2010
Location: Arthur Ontario Canada
Posts: 122
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by belliott View Post
No,of course not.
I was referring to the web.
I was looking at the notch in the first picture.



Benchmark Home Inspection Services.
http://www.KitchenerWaterlooHomeInspector.ca Kitchener-Wateroo and Guelph area Home Inspection
Serving Kitchener-Waterloo, Guelph, Orangeville, Mount Forest and surrounding areas.
Reply With Quote
  #10  
Old 7/24/10, 5:44 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by bdehaan View Post
I was looking at the notch in the first picture.
What makes it laughable is that right next to his DIY patch job is a slice clear through the bottom of that Ibeam.
I am glad not to see those type beams around here much.

First minute I saw the darn pic I had to figure out why they had joists going perpendicular to each other before I realized it was a cheapo version of a real beam (haha) .(sorry I hate those I beams)
Reply With Quote
  #11  
Old 7/24/10, 5:58 PM
wnapier's Avatar
wnapier wnapier is offline
Active Poster
 
Join Date: Mar 2010
Location: Knoxville- Powell , TN
Posts: 344
Please Note: wnapier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Almost ended up in a fist fight with contractor

But it's a NEW house, what could be wrong to need an inspection?

Bwahahahahahahahaha...............

Al (have heard that many times in the last 20 years) in TN
Reply With Quote
  #12  
Old 7/24/10, 8:43 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by belliott View Post
What makes it laughable is that right next to his DIY patch job is a slice clear through the bottom of that Ibeam.
I am glad not to see those type beams around here much.

First minute I saw the darn pic I had to figure out why they had joists going perpendicular to each other before I realized it was a cheapo version of a real beam (haha) .(sorry I hate those I beams)

Bob,

Are those Gluelan, Laminated Timber that much cheaper than those real Ibeam?

Curious mind wants to know,



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #13  
Old 7/24/10, 8:56 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Almost ended up in a fist fight with contractor

Quote:
Originally Posted by pmassie View Post
I did a home inspection yesterday that almost ended up in a fist fight between me and the contractor. see the pics below and tell me what is wrong here

ok, first ting : flooring. presswood is good for flooring he said....then i said show me de drawing (plans) and he did. on the plan it was mentionned : use plywood 5/8 thick....then he went nuts....
I do see what appear to be defects in notching of the joists.

However, I hope you didn't use the term "presswood" in your report or oral conversations with the contractor/client. It's OSB, as in Oriented Strand Board and it is much more commonly used than plywood these days.

Number 2: If you aren't an engineer with special training in wood characteristics, I don't think you're qualified to call out as a defect the use of OSB as a flooring material, even if it does contradict the plans. (If that were the case, 95% of the homes here are defective. Here's a good article about OSB vs. Plywood.) Does your jurisdiction have a code enforcement office? Just a thought, but perhaps you should have just documented what you saw and called them to inquire about the acceptability of this material. Or, referred the buyer to the home designer about the apparent contradiction and the ramifications of it.

Number 3: The holes in the I-joists, with some exceptions, are permitted. Just because the hole isn't cut beautifully isn't necessarily a defect. Unless you already know the manufacturer's specifications, a little research in this area may have been prudent before scaring the buyer.

Inspectors have to be very careful, especially when inspecting new construction. Times are hard and buyers are hard to come by. If the deal falls apart based on unsubstantiated or inaccurate allegations from a home inspector, a pissed off builder with the proper financial resources could put you out of business by tying you up in court for years to come.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 7/24/10 at 9:00 PM..
Reply With Quote
Need a home inspection in British Columbia? Check out InterNACHI's listing of British Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/24/10, 8:57 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Almost ended up in a fist fight with contractor

Notched beam at bottom with a piece of protective wood was a nice touch. Square opening in TJI was nice, as was the splintered look of the opening this idiot put in the adjacent TJI. But, from a purely technical standpoint, all may be okay.

Backpitch to the ABS was a beautiful thing, but not as great as substituting what the plans called for in the way of OSB flooring for plywood. OSB is an accepted flooring material, BTW.

I'll bet dollars to doughnuts that squash blocks werent installed at TJIs beneath point loads and bearing partitions...

BUT... Mr. Funderbunk's commentary is spot-on...

Quote:
Inspectors have to be very careful, especially when inspecting new construction. Times are hard and buyers are hard to come by. If the deal falls apart based on unsubstantiated or inaccurate allegations from a home inspector, a pissed off builder with the proper financial resources could put you out of business by tying you up in court for years to come.


Love the commentary, Big Joe... Bravo.

Last edited by jfarsetta; 7/24/10 at 9:03 PM..
Reply With Quote
  #15  
Old 7/24/10, 9:02 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Almost ended up in a fist fight with contractor

Another strange thing: all that ABS piping. 99.99% of what's used here is PVC now.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Beware the thermal imaging contractor phenderson Thermal Imaging, Infrared Cameras & Energy Audits 29 2/8/09 4:48 PM
John McKenna and Nick Gromicko debate licensing and have a fist fight caught on tape! gromicko Legislation, Licensing & Legal Issues for Inspectors 10 4/24/08 10:06 AM
Go & Get 3 Bids, Advice Article written by Ed Ed Fako Exterior Inspections 2 5/25/07 7:58 PM


All times are GMT -4. The time now is 6:36 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts