Default Calling all Canadian Electricians

Sorry... no emergency... but wanted to ask any of you fine gentlemen who are UP on current Canadian electroical code, if it is a requirement for a microwave to be on an independant circuit?

I inspected a new (built in 1989 - fully renovated and re-modeled the whole building) vacant apartment today and found that the microwave & refrigerator were on the same circuit. This may be okay, but not how I would have done it were it my own home, so wanted to know what THE LAW said. Thanks! Off to number TWO... inspection that is...
Reply With Quote
  #2  
Old 4/2/07, 5:23 PM
Rob A. Parker Rob A. Parker is offline
InterNACHI Member
 
Join Date: May 2004
Location: London, ON
Posts: 407
Send a message via ICQ to rparker
Default Re: Calling all Canadian Electricians

Arne here in Ontario the micro and the fridge each have their own circuit as far as I know.



Rob Parker RHI CMI
ITC Level 1 Thermographer
Thamespec Inc.
www.thamespec-inspections.com
Reply With Quote
  #3  
Old 4/2/07, 7:24 PM
Bill Redfern, CHI Bill Redfern, CHI is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Bedford, NS
Posts: 40
Default Re: Calling all Canadian Electricians

Micro gets its own in NS as well.

regards,
Bill
Reply With Quote
  #4  
Old 4/2/07, 8:03 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by alarsen1
Sorry... no emergency... but wanted to ask any of you fine gentlemen who are UP on current Canadian electroical code, if it is a requirement for a microwave to be on an independant circuit?

I inspected a new (built in 1989 - fully renovated and re-modeled the whole building) vacant apartment today and found that the microwave & refrigerator were on the same circuit. This may be okay, but not how I would have done it were it my own home, so wanted to know what THE LAW said. Thanks! Off to number TWO... inspection that is...
Arne

Here are the Electrical Codes 26-720 [a] Each receptacle installed for a refrigerator shall be supplied by a branch circuit that does not supply any other outlet, except a recessed clock receptacle intended for use with an electric clock:

26-720 [d] Each receptacle installed in a cupboard, wall cabinet or enclosure for the use of a microwave oven in accordance with rule 26-710 [i] shall be supplied by a branch circuit that does not supply any other outlets and this circuit shall not be considered as forming part of the circuits required under rule 26-722 [b]

For the life of me I can't figure out why an electric clock is OK. And it has to be a recessed receptacle at that. I have only seen them[receptacle] in homes built in the 60's

Hope this helps
</IMG>





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #5  
Old 4/2/07, 8:28 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Calling all Canadian Electricians

Mario;

The clock is OK because it usually runs on a AA battery.

As long as another device can not overload that circuit the clock should be alright.

Just loggical thinking there Mr. Watson. ha. ha.
Talking through my hat on this one, but it sounded good. ha. ha.

Marcel
Reply With Quote
  #6  
Old 4/2/07, 9:04 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Calling all Canadian Electricians

Just to add to this without the codes, Central Vac needs to have a dedicated circuit,as well as the laundry room, utility room.

I'm not an electrician Arne but I know my codes from an electrical course that I did.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #7  
Old 4/2/07, 9:11 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by mcyr
Mario;

The clock is OK because it usually runs on a AA battery.

As long as another device can not overload that circuit the clock should be alright.

Just loggical thinking there Mr. Watson. ha. ha.
Talking through my hat on this one, but it sounded good. ha. ha.

Marcel
Marcel

In newer homes I don't see the recessed outlet [receptacle] for a clock. I guess our Electrical code is dated!!
</IMG></IMG></IMG></IMG>





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #8  
Old 4/2/07, 10:58 PM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Thanks for all the responses guys... I "thought" as much, but wanted to be sure.

The Condo is a renovation... but not just a re-modelling of the individual unit, but a total reno of the whole place, all the common areas and every unit... new flooring... new cabinets... new appliances... new fixtures... Even the elevator doesn't smell funny!

In my mind - if they are going to that extreme with everything about the building - I would think that the electrical would have to be up to current code. In my way of thinking (I could be wrong) the only way I could see them getting away with having these two appliances share the same circuit would be if that was okay back when the building was first constructed in 1989, and that they didn't have to have an electrical permit as part of the current renovation... which would seem odd.

But even in '89, common sense would seem to dictate to me that two appliances like a microwave (which in '89 were massive wattage pigs) and a refrigerator (not a light-weight appliance either) shouldn't be inter-connected. My mothers old kitchen is like that... and if she runs the micro when the toaster is on, pops a breaker.

Maybe I'll track down the project Super and ask if any electrical permits were required as part of the reno. Thanks again all.

Arne
Reply With Quote
  #9  
Old 4/3/07, 1:02 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Upon closer examination... it is possible that the two branch circuits were separate. I say "possible" because as the two breakers were tied together, it was not possibly to trip one without tripping the other. Hmm...

Being willing to look the fool as opposed to having the gal go through grief, I called it like this:
2.7 No microwave present at this time, however the breaker for the refrigerator circuit is inter-connected with the breaker for the microwave circuit. Current electrical code (26 - 720 a & d) states that a refrigerator can only share a branch circuit with a recessed clock, and that a microwave circuit shall not share a branch circuit with any thing else... and while the two "circuits" may be separate, as the breakers are inter-connected, you can not help but trip both should one or the other overload.
To be on the safe side, and as there are still contractors on site, I recommend further evaluation by a licensed Electrical contractor to ensure that this arrangement is acceptable.
Thoughts and critique always welcome!

As the project isn't completely finished yet, there are still guys with hard hats still on site - so she shouldn't be out of pocket for getting one of them to check this out. If she is, I'll cover the cost and consider it a lesson learned.
Reply With Quote
  #10  
Old 4/3/07, 7:43 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Its not wise to quote code, unless you are a code expert or you have been hired to document for litigation purposes the defects and what the code calls for.

In the end the electrical authority has the last call and may have approved the upgrade even though the code was not fully complied with.

As to the recessed outlet for a clock the current to run the clock is irrelevant in the scheme of power draw. The recess is so the clock hangs vertically on the wall.
Reply With Quote
  #11  
Old 4/3/07, 9:54 AM
wjung wjung is offline
New User
 
Join Date: Oct 2003
Location: Port Burwell, ON
Posts: 75
Please Note: wjung is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Arnie,
Ray is correct you should never quote code in your report, unless you are code qualified and in fact have been retained by your client to perform a code compliance inspection. You are entering some very dangerous waters by portraying yourself as a code expert and potentially exposing yourself to some heavy liability.
Best regards
Wolf
Reply With Quote
  #12  
Old 4/3/07, 11:27 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by wjung
Arnie,
Ray is correct you should never quote code in your report, unless you are code qualified and in fact have been retained by your client to perform a code compliance inspection. You are entering some very dangerous waters by portraying yourself as a code expert and potentially exposing yourself to some heavy liability.
Best regards
Wolf
Okay... thanks Ray & Wolf... got it... avoid code (even paraphrasing)... but you didn't answer my question. Did I call it correctly or not? As the two breakers are tied together, and as one tripping will take the other one with it, is there an issue here?
Reply With Quote
  #13  
Old 4/3/07, 11:53 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Arne
Yes you called it correctly but in lieu of quoting code, you could have said,

The breaker for the refrigerator circuit "appears" to be inter-connected with the breaker for the microwave circuit. Current installation requirements state that a refrigerator can only share a branch circuit with a recessed clock outlet, and that a microwave circuit shall not share a branch circuit with any other load... and while the two "circuits" may be separate, as the breakers are inter-connected, you can not help but trip both should one or the other overload.

I recommend further evaluation by a licensed Electrical contractor to ensure that this arrangement is acceptable.

Thats how I would write up the concern/finding.
Cheers,
Reply With Quote
  #14  
Old 4/3/07, 11:59 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by rwand1
Arne
Yes you called it correctly but in lieu of quoting code, you could have said,

The breaker for the refrigerator circuit "appears" to be inter-connected with the breaker for the microwave circuit. Current installation requirements state that a refrigerator can only share a branch circuit with a recessed clock outlet, and that a microwave circuit shall not share a branch circuit with any other load... and while the two "circuits" may be separate, as the breakers are inter-connected, you can not help but trip both should one or the other overload.

I recommend further evaluation by a licensed Electrical contractor to ensure that this arrangement is acceptable.

Thats how I would write up the concern/finding.
Cheers,
Thanks Roy! I didn't send it off until this morning (holding off until I received a more definitave answer from the gallery), and as such sent this off about half an hour ago:
2.7 No microwave present at this time, however the breaker for the refrigerator circuit is inter-connected with the breaker for the microwave circuit. It is my understanding that these appliances should be on their own circuits... and while the two "circuits" may be separate, as the breakers are inter-connected, you can not help but trip both should one or the other overload.

To be on the safe side, and as there are still contractors on site, I recommend further evaluation by a licensed Electrical contractor to ensure that this arrangement is acceptable.
Thanks again, Roy.

Arne
Reply With Quote
  #15  
Old 4/3/07, 12:04 PM
wjung wjung is offline
New User
 
Join Date: Oct 2003
Location: Port Burwell, ON
Posts: 75
Please Note: wjung is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Arnie,
sounds ok to me.
Wolf
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Today's Canadian Daily Door Prize. You must be a Canadian to win. Pass if you are not gromicko Canadian Inspectors 20 8/18/07 1:43 PM
Canadian Member of the Year Award Progam mcyr Canadian Inspectors 0 3/11/07 4:55 PM


All times are GMT -4. The time now is 11:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts