Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by alarsen1
Thanks Roy! I didn't send it off until this morning (holding off until I received a more definitave answer from the gallery), and as such sent this off about half an hour ago:
2.7 No microwave present at this time, however the breaker for the refrigerator circuit is inter-connected with the breaker for the microwave circuit. It is my understanding that these appliances should be on their own circuits... and while the two "circuits" may be separate, as the breakers are inter-connected, you can not help but trip both should one or the other overload.

To be on the safe side, and as there are still contractors on site, I recommend further evaluation by a licensed Electrical contractor to ensure that this arrangement is acceptable.

Thanks again, Roy.

Arne
Is Ray Roy or Roy Ray?



Chuck Crooker I.M.M., Canadian Home Inspectorhttp://www.crookerhancox.com "Not just an inspection, an Education!!!"
Reply With Quote
  #17  
Old 4/3/07, 12:23 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

You can call me Ray, you can call me Raymond, you can call me Raymondo, but you don't have to call me Roy!
Reply With Quote
  #18  
Old 4/3/07, 2:13 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by mkyriacou
For the life of me I can't figure out why an electric clock is OK.
So that if the breaker trips and power is lost to the fridge it will also stop the clock. That way you can look at the time on the clock and see how long the power has been shut off to the fridge. You will know then if its safe to eat the balony sandwich or not
Reply With Quote
  #19  
Old 4/3/07, 2:32 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by rwand1
You can call me Ray, you can call me Raymond, you can call me Raymondo, but you don't have to call me Roy!
I did that for a while. Ray is Roy and Roy is Ray. It's confusing if you are like me. I'm dyslexic that's my excuse what's your excuse Arne?
</IMG></IMG></IMG></IMG></IMG></IMG></IMG></IMG>





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #20  
Old 4/3/07, 2:40 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

If I recall correctly ( I think I am old enough) way back when (late 50's) Ontario Hydro use to deliver electricity at a different voltage and cycle? Then they switched to 60 cycle. To announce the change they gave away free electric wall clocks that had an little red dot beneath 12 o'clock that would drop down indicating if the power had been off.
Reply With Quote
  #21  
Old 4/3/07, 3:28 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by rwand1
Its not wise to quote code, unless you are a code expert or you have been hired to document for litigation purposes the defects and what the code calls for.

In the end the electrical authority has the last call and may have approved the upgrade even though the code was not fully complied with.

As to the recessed outlet for a clock the current to run the clock is irrelevant in the scheme of power draw. The recess is so the clock hangs vertically on the wall.
Excellent advise Ray!!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #22  
Old 4/9/07, 3:49 PM
William R. Devries William R. Devries is offline
New User
 
Join Date: Mar 2007
Location: Elginburg
Posts: 2
Please Note: William R. Devries is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

i always thought the reason for the clock was to tell ya that the power was out on the fridge if ya happen to be walking by. but then i have been knowen to be wrong before
Reply With Quote
  #23  
Old 4/9/07, 3:58 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

William,

I thought the sour milk would tell you that?
Reply With Quote
  #24  
Old 4/12/07, 1:36 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Calling all Canadian Electricians

Quote:
Originally Posted by rwand1
You can call me Ray, you can call me Raymond, you can call me Raymondo, but you don't have to call me Roy!
DOH! Sorry I meant Ray! Roylly I did!!!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Today's Canadian Daily Door Prize. You must be a Canadian to win. Pass if you are not gromicko Canadian Inspectors 20 8/18/07 1:43 PM
Canadian Member of the Year Award Progam mcyr Canadian Inspectors 0 3/11/07 4:55 PM


All times are GMT -4. The time now is 11:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts