I just wanted to pass on some info I recently received in case there are some Ontario inspectors who may not already be aware of it.
Three of the last five homes I inspected, all 70's and 80's vintage, had dryer circuits comprised of 40A breakers and #10 copper wire. I called for further evaluation because a 40A breaker requires #8 wire, but I also thought this was too much of a coincidence so I contacted the ESA. They advised that, over some period in the 70's and 80's, it was acceptable to the ESA to have a 40A breaker on #10 wire for this application. The reason - some very powerful dryers were being produced over that period causing nuisance tripping of 30A breakers. Dryers now must consume 24A or less and therefore only 30A breakers are allowed for the #10 wire used today. It still leaves me a little confused about what I should be writing when next I find a 40A breaker on #10 wire in an older house. |
|
#2
|
|||
|
|||
|
Please Note:
cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Since those dryers with nuisance tripping would be long gone now we could just note that it is recommended a 30 amp breaker be installed at some point when we see #10 wire. A short explanation, verbal and in the report as to why we comment on it this way. Good point to bring up.
|
|
#3
|
||||
|
||||
|
Please Note:
dcook1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#4
|
||||
|
||||
|
Quote:
ASNT Certified Level II Thermographer Certified Mold Inspector (Pro-Lab) Certified Mold Inspector IAC2 Certified Home Inspector INACHI 07040201 Commercial Property Inspection Certified Master Home Inspector 2008 InterNACHI member of the year Magnum Property Inspection Inspect it before you buy it 613 813 2353 mobile We use and recommend Home Inspector Pro Software HomeGauge Software |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Dryer sheets potential hazard | badair | Miscellaneous Discussion for Inspectors | 15 | 7/9/11 2:39 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| What is a 'condenser' dryer ?? | rcooke | Canadian Inspectors | 9 | 9/9/07 7:02 PM |
| Tarion, Ontario New Home Warranty Program. | ccrooker | Canadian Inspectors | 0 | 2/9/07 7:46 PM |