Default Clothes Dryer Circuits in Ontario

I just wanted to pass on some info I recently received in case there are some Ontario inspectors who may not already be aware of it.
Three of the last five homes I inspected, all 70's and 80's vintage, had dryer circuits comprised of 40A breakers and #10 copper wire. I called for further evaluation because a 40A breaker requires #8 wire, but I also thought this was too much of a coincidence so I contacted the ESA.
They advised that, over some period in the 70's and 80's, it was acceptable to the ESA to have a 40A breaker on #10 wire for this application. The reason - some very powerful dryers were being produced over that period causing nuisance tripping of 30A breakers.
Dryers now must consume 24A or less and therefore only 30A breakers are allowed for the #10 wire used today.
It still leaves me a little confused about what I should be writing when next I find a 40A breaker on #10 wire in an older house.
Reply With Quote
  #2  
Old 11/29/08, 2:53 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clothes Dryer Circuits in Ontario

Since those dryers with nuisance tripping would be long gone now we could just note that it is recommended a 30 amp breaker be installed at some point when we see #10 wire. A short explanation, verbal and in the report as to why we comment on it this way. Good point to bring up.
Reply With Quote
  #3  
Old 11/29/08, 6:56 PM
dcook1's Avatar
dcook1 dcook1 is offline
Active Poster
 
Join Date: Feb 2007
Location: Stayner, On
Posts: 949
Please Note: dcook1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clothes Dryer Circuits in Ontario

Quote:
Originally Posted by cboyd View Post
Since those dryers with nuisance tripping would be long gone now we could just note that it is recommended a 30 amp breaker be installed at some point when we see #10 wire. A short explanation, verbal and in the report as to why we comment on it this way. Good point to bring up.
Charles got it on the first try.... definitely explain to the client they should change it for safety. Remember, if they don't (and probably won't) at least you have told them.
Reply With Quote
  #4  
Old 12/1/08, 2:06 PM
William R. DeVries, CMHI's Avatar
William R. DeVries, CMHI William R. DeVries, CMHI is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Ont,
Posts: 1,018
Default Re: Clothes Dryer Circuits in Ontario

Quote:
Originally Posted by jallingham View Post
I just wanted to pass on some info I recently received in case there are some Ontario inspectors who may not already be aware of it.
Three of the last five homes I inspected, all 70's and 80's vintage, had dryer circuits comprised of 40A breakers and #10 copper wire. I called for further evaluation because a 40A breaker requires #8 wire, but I also thought this was too much of a coincidence so I contacted the ESA.
They advised that, over some period in the 70's and 80's, it was acceptable to the ESA to have a 40A breaker on #10 wire for this application. The reason - some very powerful dryers were being produced over that period causing nuisance tripping of 30A breakers.
Dryers now must consume 24A or less and therefore only 30A breakers are allowed for the #10 wire used today.
It still leaves me a little confused about what I should be writing when next I find a 40A breaker on #10 wire in an older house.
As this is not a code specific inspection, during the 1970 -1980's the Electric safety Standards allowed the Branch circuit have 40amp on a #10 gauge wire. It's reason as per ESA was the dryers then were less efficient and had a much heaver consumption. Todays dryers are " Energy Star" Compliant and inasmuch use less electricity. If your current dryer is an "energy Star " Compliant model it is recommended to have this circuit changed to todays electrical codes. Recommend electrician repair or replace as needed. This is for your information



ASNT Certified Level II Thermographer
Certified Mold Inspector (Pro-Lab)
Certified Mold Inspector IAC2
Certified Home Inspector INACHI 07040201
Commercial Property Inspection
Certified Master Home Inspector
2008 InterNACHI member of the year



Magnum Property Inspection
Inspect it before you buy it
613 813 2353 mobile
We use and recommend
Home Inspector Pro Software
HomeGauge Software
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Dryer sheets potential hazard badair Miscellaneous Discussion for Inspectors 15 7/9/11 2:39 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 9 9/9/07 7:02 PM
Tarion, Ontario New Home Warranty Program. ccrooker Canadian Inspectors 0 2/9/07 7:46 PM


All times are GMT -4. The time now is 6:49 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts