Default Double Taps

I had a realtor tell me today that electricians are getting peeved at home inspectors for calling out double taps. Yet in the home that was inspected there were three double taps, with room for more breakers. I called it out and suggested the vendor repair prior to closing of title. The building permit was okay, and there was a ESA orange sticker on the panel, but no dates or anyother mark on it.

So what is the story, I like to think those electricians are wrong, because double taps lead to nuisance trips because you have doubled the load?

If the building permit is signed off, and the panel was done by an electrician is it right? I know the electricians are left to their good discretion, but I also know ESA inspectors only inspect a representitive number of new homes, not all of them, they entrust the electrican?

Confused.
Reply With Quote
  #2  
Old 3/10/06, 7:43 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Taps

I write them up also. I also inform the client about how common (I didn't say correct) it is.
Reply With Quote
  #3  
Old 3/10/06, 8:14 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Double Taps

Quote:
Originally Posted by rwand1
So what is the story, I like to think those electricians are wrong, because double taps lead to nuisance trips because you have doubled the load?
This seemed like a good explanation that I pulled from somewhere:

Double tapping and lugging can create hot spots on breakers and neutral bars if not tightened to the correct torque and especially if two different size conductors are used. Because the hot and neutral wires are current carrying conductors, the chance is then greater for potential hot spots. If the double tap or lug becomes lose, it begins to arc. As it arcs it builds up carbon. Carbon is then resistance and with the more carbon buildup the more difficult it is for the conductor to make contact....thus increasing the current. End result can be the breaker tripping because of the loose conection (excessive current exceeding the rating of the breaker), or signs of overheating such as discolored wires, melted wires, etc, or worse yet...fire!

110.14(A)..."Terminals for more than one conductor and terminals used to connect aluminum shall be so identified."
Reply With Quote
  #4  
Old 3/10/06, 8:58 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,613
Default Re: Double Taps

Quote:
Originally Posted by rwand1
I had a realtor tell me today that electricians are getting peeved at home inspectors for calling out double taps. Yet in the home that was inspected there were three double taps, with room for more breakers. I called it out and suggested the vendor repair prior to closing of title. The building permit was okay, and there was a ESA orange sticker on the panel, but no dates or anyother mark on it.

So what is the story, I like to think those electricians are wrong, because double taps lead to nuisance trips because you have doubled the load?

If the building permit is signed off, and the panel was done by an electrician is it right? I know the electricians are left to their good discretion, but I also know ESA inspectors only inspect a representitive number of new homes, not all of them, they entrust the electrican?

Confused.
I would expect the ESA sticker was put there by the electrictian who did the job. They now only inspect a very small amount of the homes that are wired by an established contractor. It might be a simple thing for the purchaser to call the original contractor and state that a home inspector said that double taps are not allowed in most cases ( SQ D is one ) and that they are wondering if they should call the local hydro authority. I expect the original contractor will fix it for free as he does not want ESA to know he scewed up .
Roy Cooke .... RHI........... Cahpi-on
A HAPPY NACHI member.
Reply With Quote
  #5  
Old 3/11/06, 12:15 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Double Taps

Quote:
Originally Posted by lkage
This seemed like a good explanation that I pulled from somewhere:

Double tapping and lugging can create hot spots on breakers and neutral bars if not tightened to the correct torque and especially if two different size conductors are used. Because the hot and neutral wires are current carrying conductors, the chance is then greater for potential hot spots. If the double tap or lug becomes lose, it begins to arc. As it arcs it builds up carbon. Carbon is then resistance and with the more carbon buildup the more difficult it is for the conductor to make contact....thus increasing the current. End result can be the breaker tripping because of the loose conection (excessive current exceeding the rating of the breaker), or signs of overheating such as discolored wires, melted wires, etc, or worse yet...fire!

110.14(A)..."Terminals for more than one conductor and terminals used to connect aluminum shall be so identified."
Many Square panels allow two same size conductors.
Reply With Quote
  #6  
Old 3/11/06, 6:14 AM
twheeler
Guest
 
Posts: n/a
Please Note: is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Taps

Quote:
Originally Posted by bkelly2
Many Square panels allow two same size conductors.
But only if the load is not maxed out



I always make note of the fact that there is double tapped circuits, and make recommendation that the electrical panel be inspected by a licensed electrician.
Reply With Quote
  #7  
Old 3/11/06, 7:01 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Double Taps

Double tapping and lugging can create hot spots on breakers and neutral bars if not tightened to the correct torque and especially if two different size conductors are used.

Quote:
Originally Posted by bkelly2
Many Square panels allow two same size conductors.
It does say "and"...relating to double tapping/lugging hot spots but you're correct many Sq. D breakers allow two same size conductors.

Last edited by lkage; 3/11/06 at 9:27 AM..
Reply With Quote
  #8  
Old 3/11/06, 7:39 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Taps

Thanks guys. I will be contacting ESA this week and see if I can get a policy statement from them in regards to double taps.

Unfortunately it is the realtors who have to take the word of a licenced electrician over that of a home inspector. Still don't understand how a Square D double tap can be any different from any other double tapped breaker as it is still possible to double the load, thus resulting in tripping.

Thanks again.
Reply With Quote
  #9  
Old 3/11/06, 7:47 AM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Taps

Quote:
Originally Posted by rwand1
Thanks guys. I will be contacting ESA this week and see if I can get a policy statement from them in regards to double taps.
Raymond, If they provide you with a statement please post it for all to see.
Reply With Quote
  #10  
Old 3/11/06, 7:51 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Taps

To quote Roy Cooke Sr., "you bet ya!"
Reply With Quote
  #11  
Old 3/11/06, 9:32 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Double Taps

Quote:
Originally Posted by rwand1
Still don't understand how a Square D double tap can be any different from any other double tapped breaker as it is still possible to double the load, thus resulting in tripping.
Most breakers aren't made for two wires like this Sq. D pic:

I can go by what I see such as whether the manufacturer allows 2 wire on a breaker but I don't do load calculations for the 2 wire loads.
Attached Thumbnails
double-taps-twowirebreaker.jpg  

Last edited by lkage; 3/11/06 at 9:36 AM..
Reply With Quote
  #12  
Old 3/11/06, 9:41 AM
jwortham jwortham is offline
Active Poster
 
Join Date: May 2004
Location: Bolingbrook, IL
Posts: 272
Please Note: jwortham is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Double Taps

I call out the double-taps.

If the electrician then says they are fine, and signs off on them, not my concern. I've done my job advising my client.

I don't tell a realtor how to sell a house. They don't get to tell me how to inspect one.
Reply With Quote
  #13  
Old 3/11/06, 2:44 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Double Taps

Quote:
Originally Posted by lkage
Most breakers aren't made for two wires like this Sq. D pic:

I can go by what I see such as whether the manufacturer allows 2 wire on a breaker but I don't do load calculations for the 2 wire loads.

Nice picture Larry, many times you can read the wiring diagram in the panel showing whether two conductors are allowed or not. I believe if they are allowed than it is not a double tap.
Reply With Quote
  #14  
Old 3/11/06, 3:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Double Taps

Quote:
Originally Posted by bkelly2
I believe if they are allowed than it is not a double tap.
Same here, Brian. I don't care to pay for the electricians trip out for no reason.
Reply With Quote
  #15  
Old 3/11/06, 8:02 PM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 2,087
Default Re: Double Taps

Rule 6-212 & 12-3034 Says "It is not correct to connect two or more wires to a circuit breaker or fuse."
From 7th edition of Alberta Book 1, Electrical code simplified (residential wiring)
Based on the 18th edition of the Canadian electrical code and Alberta amendments.
This code was printed in 1999. It may have changed in later editions.
I drought it. If anyone has a later edition that says something different I would like to hear it.
Anytime I see a double tap I flag it for a licensed electrician the repair.



Vern Mitchinson_CCHI_CMI
Registar
AlbertaNACHI
International Association of Certified Home Inspectors of Canada
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Double Tap Questions jkogel Electrical Inspections 6 6/28/07 9:46 PM
Square D double taps abishop Electrical Inspections 3 10/29/06 9:01 AM
Double Taps... Here we go again rwand1 Canadian Inspectors 12 10/28/06 3:55 PM
Double taps Mike Parks Electrical Inspections 11 5/28/06 1:52 PM
Double Taps psmothers Electrical Inspections 3 3/9/06 10:04 PM


All times are GMT -4. The time now is 12:10 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts