Default Electrical Puzzle!

I'd appreciate your opinions on this situation:
While looking at a 42 circuit electric panel rated for 200 amps, with the deadfront off, my left hand was touching the left side of the panel box as I moved aside an ungrounded conductor (a black wire) with my right hand to better view some connections of the grounding wires. I got a pretty good zap! The black plastic insulation did not appear cracked or damaged in any way and I was nowhere near the stripped end. I was standing on a dry lino-covered wood floor over a crawlspace. I used a volt meter between the body of the panel and a separate independant ground to see if the panel body was energized and it was not.
So why did I get zapped??
Thanks for your thoughts!
Keith



Keith F. Broad
Broad Spectrum Inspections
www.broadspectruminspections.com
Reply With Quote
  #2  
Old 10/29/06, 1:53 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 360
Default Re: Electrical Puzzle!

Can't think of any reason you got zapped...but two things kinda jump out here. One- you shouldn't be sticking those bare little pinkies in there in the first place, naughty naughty. Two - definitely don't ground yourself to the panel while doing it If you must move live wiring at least use some type of non-conductive plastic insulated device.


</IMG>



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #3  
Old 10/29/06, 1:37 AM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 819
Send a message via Yahoo to gpallotta
Default Re: Electrical Puzzle!

Even though the wires are insulated there is a enough electrical magnetic force in the box that if you ground yourself to the panel you become the conductor. 1. you ever use a volt probe and even before you get to the live wire it lights up or beeps thats electricity in the air. 2. Thats why your supposed to use electricians gloves so if you accidentally ground yourself you don't kill yourself.

My friend you don't know how lucky you were.

Gerry
Reply With Quote
  #4  
Old 10/29/06, 8:29 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

Were your hands moist? The insulative jacket could have a hairline crack?
Reply With Quote
  #5  
Old 10/29/06, 8:40 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

Quote:
Originally Posted by kbroad
I'd appreciate your opinions on this situation:
While looking at a 42 circuit electric panel rated for 200 amps, with the deadfront off, my left hand was touching the left side of the panel box as I moved aside an ungrounded conductor (a black wire) with my right hand to better view some connections of the grounding wires. I got a pretty good zap! The black plastic insulation did not appear cracked or damaged in any way and I was nowhere near the stripped end. I was standing on a dry lino-covered wood floor over a crawlspace. I used a volt meter between the body of the panel and a separate independant ground to see if the panel body was energized and it was not.
So why did I get zapped??
Thanks for your thoughts!
Keith
Big Tip ....use left hand to turn all switches of and on.
If something goes bad flash passes your left side not in your face .
Put one hand in pocket then if you are carless enough to get into a hot wire the current does not go through the heart less apt to die that way .
Not Jokeing had two disconects explode I heard bells in the head for a few days but no lasting damage .
Reply With Quote
  #6  
Old 10/29/06, 8:49 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

How can you use one hand to hold the panel and turn the screws. You need both hands?
Reply With Quote
  #7  
Old 10/29/06, 8:53 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

Quote:
Originally Posted by rwand1
How can you use one hand to hold the panel and turn the screws. You need both hands?
Thats the beauty of the cover you can not get your fingers in where they should not be .
I give You Raymond permission to now use two hands .
Enjoy Roy
Reply With Quote
  #8  
Old 10/29/06, 3:13 PM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, Ab
Posts: 1,146
Default Re: Electrical Puzzle!

Quote:
Originally Posted by rcooke
I heard bells in the head for a few days but no lasting damage .
Are you sure there was no permanent damage?

Just joking!

Last edited by vmitchinson; 10/29/06 at 3:18 PM..
Reply With Quote
  #9  
Old 10/29/06, 3:25 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

Quote:
Originally Posted by vmitchinson
Are you sure there was no permanent damage?

Just joking!
Excuse me I have to answer the phone ,17 times today and they always hang up when I answer.
I know I am a sicky tooooo
Roy Cooke
Reply With Quote
  #10  
Old 10/29/06, 3:43 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

I have had some minor mishaps with electrical panels.

1. Putting screw back into panel cover the screw hit a live wire. (Pointed screw)
2. Putting screw back on panel and receiving shock from panel.
3. Client in bare feet leans on basement refrigerator and gets zapped.
4. Putting panel cover back on and hitting something live and causing sparks, no shock.

This is over a sixteen year span.
Reply With Quote
  #11  
Old 10/29/06, 3:54 PM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,115
Default Re: Electrical Puzzle!

Putting a pointed cover screw back into a panel.

Do you still do that???



--

Erby Crofutt
B4U Close Home Inspections
Georgetown, Kentucky

KY Lic# HI-2041
www.b4uclose.com
http://www.kentuckyradon.com
Kentucky Home Inspections
Kentucky Home Inspectors
NACHI02090301

Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector

Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice!
Reply With Quote
  #12  
Old 10/29/06, 4:08 PM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 360
Default Re: Electrical Puzzle!

What amazes me is that no rocket scientist at the factory that makes these electrical panels, has thought of bending that little bump of metal to the exterior so the screws go through to the outside of the panel?:shocked:

Wouldn't take much would it...



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #13  
Old 10/29/06, 4:13 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

I've also wondered why they don't bend it to the outside. I suppose its because if the correct screw was used there shouldn't be a problem.
Reply With Quote
  #14  
Old 10/29/06, 4:16 PM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 819
Send a message via Yahoo to gpallotta
Default Re: Electrical Puzzle!

More than likely they discovered the mistake afterwards and would cost to much to retool.

Gerry
Reply With Quote
  #15  
Old 10/29/06, 4:20 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Puzzle!

Erby

I was waiting for someone to ask that question.

Yes I put the screw back in because that is the way I found the panel. The rest of the screws were all inappropriate too. I reported the problem in the report, and I told the agent, and I left the breaker off and marked it for the electrcian, and put the panel cover back on.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Download the videos here all about physics and electricity jtedesco1 Electrical 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 6:54 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts