Default HVAC Question

This is a 3 yr old Heil oil furnace with side wall venting and the vent looks like a liner. This is exposed and very hot and yes (my client touched it). Other than a safety hazard and the compromising of a whole whack of floor joists can anybody tell by my crappy pictures if this is proper venting for oil. I sure as heck don't like it but want to base my report on facts not my preferences.
Attached Thumbnails
heating-venting-air-conditioning-question-dscf7346.jpg   heating-venting-air-conditioning-question-dscf7328.jpg   heating-venting-air-conditioning-question-dscf7327.jpg   heating-venting-air-conditioning-question-dscf7330.jpg  
Reply With Quote
Need a home inspection in Ontario? Check out InterNACHI's listing of Ontario certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/18/10, 8:35 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: HVAC Question

To many things I do not like I would pass this on to qualified , Furnace ,and structer peole . No way I want to have my name saying this is Ok.
I am sure there are other things beside cut joices and drilled holes in Joices for me to be concirned on... Please keep us posted ... Roy
Is that Black plastic I see for exhaust?



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 11/18/10, 9:20 PM
Chris E. Donofrio's Avatar
Chris E. Donofrio Chris E. Donofrio is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Sault Ste Marie Ontario
Posts: 117
Default Re: HVAC Question

Thats part of my question Roy as I have not run across this setup before but I think the black is fan induced air to act as a suction right near the exit point. Do you think the other looks like liner material. Yes I told my client to call in an hvac tech to inspect and explain the install but NOT the same one that installed this mess.
Reply With Quote
  #4  
Old 11/18/10, 9:58 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

That is liner material, could be damaged easily and not noticed until everyone wakes up dead from carbon monoxide. I hope there is no ceramic tile above the joists. Since when did hvac guys start comprimising structure? It used to be only plumbers.
Reply With Quote
  #5  
Old 11/18/10, 10:00 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Fourth pic looks a litle close to level too for exhaust. Could be just the pic.
Reply With Quote
  #6  
Old 11/18/10, 10:03 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Quote:
Originally Posted by cdonofrio View Post
Thats part of my question Roy as I have not run across this setup before but I think the black is fan induced air to act as a suction right near the exit point. Do you think the other looks like liner material. Yes I told my client to call in an hvac tech to inspect and explain the install but NOT the same one that installed this mess.
There is a good chance it is approved as part a sidewall vent system that may go by the generic name of "sealed combustion, direct vent" system. The flex duct seen in the Maritimes serving oil-fired boilers/furnaces approved for direct venting is actually an insulated tube-in-tube version. See www.kerrenergysystems.com under products- Direct Vent. There is an animation of its operation.
Reply With Quote
  #7  
Old 11/18/10, 10:06 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Would that type of direct vent system be ok to be level then Brian?
Reply With Quote
  #8  
Old 11/18/10, 10:15 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Quote:
Originally Posted by cboyd View Post
Would that type of direct vent system be ok to be level then Brian?
Kerr do recommend the 1/4"/foot upward slope that is typical of naturally vented-by-chimney systems but the through the wall system section is installed horizontally. Since the Kerr is a burner fan driven system, it really doesn't need the upward slope as does a naturally vented system...... it's airtight and the strong burner fan can blow the exhaust gases horizontally or even downward!! These direct vent systems are a new creature altogether!
Reply With Quote
  #9  
Old 11/21/10, 6:33 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Came across this on a 30 year old wood furnace on friday, could not tell if it was double wall. WETT certification coming up for it and main floor wood stove anyways, no liner in the clay flue etc.
heating-venting-air-conditioning-question-pb190155.jpg
Reply With Quote
  #10  
Old 11/21/10, 7:30 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Quote:
Originally Posted by cboyd View Post
Came across this on a 30 year old wood furnace on friday, could not tell if it was double wall. WETT certification coming up for it and main floor wood stove anyways, no liner in the clay flue etc.
Attachment 40292
A 30 year old wood furnace might not have ULC or CSA certification.

The flex liner is not considered appropriate smoke pipe for a wood installation. Flue pipe shall be 26 ga for 6" diameter and under; 24 ga for 6" to 10" diameter; engineered over 10" diameter

Hopefully the wood furnace and wood stove are on separate flues!
Reply With Quote
  #11  
Old 11/21/10, 8:33 PM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Surprisingly had a ULC label, brass one, very tarnished but it was there. I advised the client that the furnace may not be insurable as per wett inspection. And if it was, not for long. I'm sure the flex pipe was a handyman idea. There was an oil fired boiler about 4 years old heating an addition with radiant and a coil in the forced air wood furnace. I recommended he finish the rest of the main floor with radiant.
Yes, the stove was on it's own insulated chimney.

There was also a 200 amp main breaker in 150 amp panel, they figured they needed it when they ran a 40 amp service to the garage
Reply With Quote
  #12  
Old 11/21/10, 9:33 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Quote:
Originally Posted by cboyd View Post
Surprisingly had a ULC label, brass one, very tarnished but it was there. I advised the client that the furnace may not be insurable as per wett inspection. And if it was, not for long.* I'm sure the flex pipe was a handyman idea. There was an oil fired boiler about 4 years old heating an addition with radiant and a coil in the forced air wood furnace. I recommended he finish the rest of the main floor with radiant.
Yes, the stove was on it's own insulated chimney.

There was also a 200 amp main breaker in 150 amp panel, they figured they needed it when they ran a 40 amp service to the garage
That'll kill the insurance quickly!!

Were the boiler and furnace sharing the same flue?

*PS- there are a strict set of clearances to combustibles for hot /return air plenums and ducting if not tested and stated on the unit.........may become another insurance issue.

Last edited by Brian A. MacNeish; 11/21/10 at 9:38 PM..
Reply With Quote
  #13  
Old 11/22/10, 5:25 AM
cboyd cboyd is offline
Active Poster
 
Join Date: Jul 2007
Location: North Augusta, On
Posts: 451
Please Note: cboyd is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Separate flues, boiler had a nice stainless insulated.
I think the wood furnace was being used as an air handler for the most part, it was in tact and wood stored in the basement so we have to assume it is being used for backup or to save on oil. Lots of little things, jet pump not hard wired, just plugged in. Vermiculite is being tested,some new window inserts with rot in the old brick mold and sills etc.
Reply With Quote
Need a home inspection in Ontario? Check out InterNACHI's listing of Ontario certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/22/10, 5:48 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: HVAC Question

Quote:
Originally Posted by cboyd View Post
Separate flues, boiler had a nice stainless insulated.
I think the wood furnace was being used as an air handler for the most part, it was in tact and wood stored in the basement so we have to assume it is being used for backup or to save on oil. Lots of little things, jet pump not hard wired, just plugged in. Vermiculite is being tested,some new window inserts with rot in the old brick mold and sills etc.
SO, the mentioned coil was in the supply duct of the wood furnace and not in the firebox/heat exchange area of the wood furnace. I misunderstood that........should not be a problem!
Reply With Quote
  #15  
Old 11/22/10, 7:50 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: HVAC Question

From what I read Charles I would be concerned big time sounds to me like a rub goldbelg set up .
I would recommend further valuation on any of these serious concerns .
And I expect there are many, impossible for me to do an inspection from a distance ,
and I think you seem to also feel there are many concerns.
All the best ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM
Room size requirement for HVAC supply kweiss Inspecting HVAC Systems 3 6/9/07 6:58 PM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 10 5/21/07 3:01 PM
Commerical HVAC code question sbyrnes Inspecting HVAC Systems 19 11/15/06 10:08 PM


All times are GMT -4. The time now is 7:06 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts