I conducted a home warranty inspection and discovered no baffles in the attic. The blown fibreglass insulation had been displaced 4-5 feet away from the perimeter of the attic wherever the soffit vents were located. Does any inspector know the code in Ontario. Is a builder mandated to use baffles, and what is the code for how close the insulation must remain around the perimeter of the attic?
|
|
#2
|
||||
|
||||
|
Jamie, there are no specific requirements for the clearances of attic insulation, other than in 9.19.1.3 (2) and 9.25.2.5 (5) (a) basically saying that insulation should not block air passage from the soffits or restrict an air flow through the vents. Installing baffles is a common building practice to ensure that this requirement is fulfilled.
Yuri Olhovsky CMI, CEA, PHPI, RASDT National Home Inspector NHICC #00372 Richmond Hill, ON Canada NACHI ID 04070207 www.homeinspections4u.biz |
|
#3
|
||||
|
||||
|
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| California Home Inspections | whandley | Miscellaneous Discussion for Inspectors | 17 | 6/4/08 12:28 AM |
| Buckeye Home Inspections Service Area | sboyd2 | Miscellaneous Discussion for Inspectors | 3 | 9/4/06 7:21 PM |
| Common Defects List by Age of House | trausch | Inspection Education & Training | 10 | 6/12/06 4:52 AM |
| New Hampshire Real Estate Agents Are Upset! | fcarrio | General Inspection Discussion | 8 | 2/11/06 1:35 PM |
| No Ashi / Nachi Conflict!! | fcarrio | Legislation, Licensing & Legal Issues for Inspectors | 5 | 2/11/06 1:32 PM |