Default Home Warranty Attic Insulation Question

I conducted a home warranty inspection and discovered no baffles in the attic. The blown fibreglass insulation had been displaced 4-5 feet away from the perimeter of the attic wherever the soffit vents were located. Does any inspector know the code in Ontario. Is a builder mandated to use baffles, and what is the code for how close the insulation must remain around the perimeter of the attic?
Reply With Quote
  #2  
Old 12/4/06, 12:38 AM
Yuri Olhovsky's Avatar
Yuri Olhovsky Yuri Olhovsky is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Richmond Hill, ON
Posts: 484
Default Re: Home Warranty Attic Insulation Question

Jamie, there are no specific requirements for the clearances of attic insulation, other than in 9.19.1.3 (2) and 9.25.2.5 (5) (a) basically saying that insulation should not block air passage from the soffits or restrict an air flow through the vents. Installing baffles is a common building practice to ensure that this requirement is fulfilled.



Yuri Olhovsky CMI, CEA, PHPI, RASDT
National Home Inspector NHICC #00372
Richmond Hill, ON Canada
NACHI ID 04070207
www.homeinspections4u.biz
Reply With Quote
  #3  
Old 12/4/06, 1:54 AM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 2,087
Default Re: Home Warranty Attic Insulation Question

Quote:
Originally Posted by jhawes
I conducted a home warranty inspection and discovered no baffles in the attic. The blown fibreglass insulation had been displaced 4-5 feet away from the perimeter of the attic wherever the soffit vents were located. Does any inspector know the code in Ontario. Is a builder mandated to use baffles, and what is the code for how close the insulation must remain around the perimeter of the attic?
The code calls for a minimum of R30 for the whole attic.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
California Home Inspections whandley Miscellaneous Discussion for Inspectors 17 6/4/08 12:28 AM
Buckeye Home Inspections Service Area sboyd2 Miscellaneous Discussion for Inspectors 3 9/4/06 7:21 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM
New Hampshire Real Estate Agents Are Upset! fcarrio General Inspection Discussion 8 2/11/06 1:35 PM
No Ashi / Nachi Conflict!! fcarrio Legislation, Licensing & Legal Issues for Inspectors 5 2/11/06 1:32 PM


All times are GMT -4. The time now is 2:27 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts