Default Question for Roy Cooke - Electrical

Hi Roy

I have an electrical question that I'm sure you will be able to answer. (I understand that you have a wee bit of experience with electrical issues)

A friend just had a kitchen re-do that involved the grounding wire being disconnected. His (master) electrician told him that he could ground to any copper pipe (hot or cold) near his panel and that his house would be adequately grounded. I said that he had to go back to the copper main from the municipality (upstream of the meter). Or, alternativley, he could drive a grounding rod to serve the same purpose.

Or, at a minimum, he would have to install a jump across the meter and ground to a cold water pipe near the panel.

Am I wrong here?

Let me know what you think.

And......... welcome back.

Joe



Joe Skrypka MBA RHI CMI
The Home Inspection Guy Inc.
Hamilton, Ontario Canada
Membership No. NACHI050062193
Reply With Quote
  #2  
Old 3/6/08, 5:55 PM
Mark Leonard Mark Leonard is offline
New User
 
Join Date: Feb 2005
Posts: 17
Please Note: Mark Leonard is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Roy Cooke - Electrical

Hello Joe

You are right about having a ground clamp on either side of the water meter. In new construction you would use a ground plate or three ground rods if the main water was plastic. But if it wasn't you would ground the panel to the street side of the water meter.

In older homes with fuse panels it is usually grounded to the nearest copper pipe but be sure that the meter is jumpered.


Mark
Reply With Quote
  #3  
Old 3/7/08, 6:55 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,613
Default Re: Question for Roy Cooke - Electrical

Quote:
Originally Posted by jskrypka
Hi Roy

I have an electrical question that I'm sure you will be able to answer. (I understand that you have a wee bit of experience with electrical issues)

A friend just had a kitchen re-do that involved the grounding wire being disconnected. His (master) electrician told him that he could ground to any copper pipe (hot or cold) near his panel and that his house would be adequately grounded. I said that he had to go back to the copper main from the municipality (upstream of the meter). Or, alternativley, he could drive a grounding rod to serve the same purpose.

Or, at a minimum, he would have to install a jump across the meter and ground to a cold water pipe near the panel.

Am I wrong here? Let me know what you think.
And......... welcome back. Joe
Hy Joe please do not think I am ignoring you . I am so busy I have not been able to get on the BB much .
Send Email to me for a quicker answer .
Thanks for ( WELCOME BACH )
Jumpers should be on all meters if the are copper in and out .
That was along time ago that you could just ground a plug to copper pipe like 50~ years now they require two wire with a grnd to all receptacles.
The panel ground has to go to the incoming copper to the home .
If it is Plastic then it requires a plate ground ( used to be Grnd Rods).
remember I have been out of the trade for about 20 years.
Roycooke@sympatico.ca



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
You Asked for it, Mr. Tedesco. Here it is.... jbushart Miscellaneous Discussion for Inspectors 0 1/23/08 4:24 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 1:14 PM
Need help with electrical Question?? rkuenkel Electrical Inspections 6 12/2/06 8:25 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 9:10 PM


All times are GMT -4. The time now is 12:14 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts