Hey guys, I'm fairly new at this so pardon the silly question but, on a 3 wire service drop( 3 insulated wires wrapped around a bare stranded metal wire ) is that bare wire a ground or is it just supporting the other wires? Thanks very much Brian
Last edited by Brian Robertson; 6/18/07 at 1:17 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
Glen Mortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
The neutral wire can act as a support, but if you have three insulated wires coming in and its a 240V service, it is likely just a support.
|
|
#3
|
|||
|
|||
|
Sounds like a 3 phase service.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#4
|
|||
|
|||
|
Please Note:
Glen Mortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
||||
|
||||
|
sounds like a standard 240 volt, 2 blacks and a white neutral. the wire strand is the support cable or it can also be a neutral as well.
at one house i did the other day there was 4 blacks one white and a wrapped cable, they were connected as 2 black to each connection at the mast and both the white and strand were tied in to the white. 200 amp service at the main. Hydro confirmed the installation as ok ASNT Certified Level II Thermographer Certified Mold Inspector (Pro-Lab) Certified Mold Inspector IAC2 Certified Home Inspector INACHI 07040201 Commercial Property Inspection Certified Master Home Inspector 2008 InterNACHI member of the year Magnum Property Inspection Inspect it before you buy it 613 813 2353 mobile We use and recommend Home Inspector Pro Software HomeGauge Software |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
What you describe is properly called "aerial quadraplex cable". Three insulated conductors and one bare stranded would typically be used for a 3-phase service to an establishment, or an overhead 4-wire feeder to an outbuilding. In the case of the feeder, the bare stranded conductor will be the equipment ground, and in the case of the service drop, the bare stranded conductor will be the neutral.
In nearly every case in which you'll observe aerial cable, this cable is of the ACSR type. You'll sometimes hear overhead cable generically referred to as ACSR, which stands for 'Aluminium Conductor, Steel Reinforced'. The bare stranded conductor is mostly all aluminium strands, except for the center-most strand or two. In this manner, this bare conductor can also serve the additional function of properly supporting the entire cable. It is for this reason that you'll see the service bail (aka, 'dead end grip', 'wedge grip', etc) attached to this bare conductor at each end. |
|
#7
|
|||
|
|||
|
Please Note:
Brian Robertson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you all for your responses. I'm inclined to think now that ots just a support cable because its just feeding a fairly small house. Thanks again
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Service Drop Dropped While at Inspection!! | mlong | Electrical Inspections | 9 | 10/20/07 6:20 AM |
| Service Drop Clearances | jhagarty | Electrical Inspections | 12 | 8/15/07 8:31 PM |
| Service Drop Q | alarsen1 | Electrical Inspections | 11 | 2/25/07 9:45 AM |
| Service Drop Clearance Over Roof | mlong | Electrical Inspections | 6 | 12/19/06 7:39 AM |
| Service Drop Run Over Balcony? | jtedesco1 | Electrical Inspections | 0 | 5/31/06 5:23 AM |