Question STC Ratings

Does anyone know if in the NBC it states a requirement for a specific STC rating between walls or hallways in a residential apartment building? Thanks guys!



Rodney Misener
Trinity Inspection Services Ltd.
Pictou County, Nova Scotia
http://www.trinitymaintenance.com

Certified Home Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT Certified Inspector
IAC2 Radon/Mold Certified
Infrared Certified
Reply With Quote
Find an InterNACHI certified Quebec Home Inspector (and anywhere else in North America)
  #2  
Old 10/15/09, 9:14 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,352
Default Re: STC Ratings

Rodney, I don't know how this relates to Home Inspections, because it is way above the SOP.
Usually, around here it is all part of the design by the Architect for those particular buildings.

Here is a link that might help you out though on the subject;
http://www.stcratings.com/ratings.html

I don't know if it is different over there, but it shouldn't, it is all part of building science for sound control.
Might not answer your question, but might help.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #3  
Old 10/15/09, 10:12 PM
Claude Lawrenson's Avatar
Claude Lawrenson Claude Lawrenson is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Tecumseh-Windsor, ON
Posts: 1,567
Default Re: STC Ratings

Yes it can be found in volume 2 NBC 2005 and A-9.11.2.1 of volume 1
Minimum at least 50 for every dwelling unit - ASTM E413

Tables for fire ans sound resistance can be located in volume 2 - Appendix A - division B



Cheers, Claude Lawrenson NACHI03121515
Inspection Support Services Inc.

"It is not the strongest of the species that survives nor the most intelligent, but the one most responsive to change." -Charles Darwin
Reply With Quote
  #4  
Old 10/30/09, 5:21 PM
Gerald T. Moore Gerald T. Moore is offline
InterNACHI Member
 
Join Date: Oct 2009
Posts: 1
Default Re: STC Ratings

In addition to the 50 required between suites and common areas there are more stringent requirements for elevator or garbage shafts. They are required to be 55.

Gerald Moore
RSM Building Consultants.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
span ratings cfuoco Structural 6 11/11/06 12:04 AM
A/C SEER Ratings mjohnson3 Misc. Discussion 0 4/23/06 8:49 PM
Max fuse ratings dmacy HVAC 15 1/20/06 12:35 AM


All times are GMT -4. The time now is 5:15 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts