Default Radon Fan

The DIY'er that installed this wad very proud of himself. He said he saved $400 by installing this system himself.
Attached Thumbnails
radon-fan-radon-discharge.jpg   radon-fan-fan-installed-basement.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #2  
Old 12/7/09, 10:07 AM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,948
Default Re: Radon Fan

My guess would be that, his intake air would pull from the dryer vent, when it was running.
I'd wonder about moisture being pumped under the foundation...




Steven Waskewicz

Professional Building Analyst, BPI
Colorado Springs, Colorado
719-510-7703
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time





Reply With Quote
  #3  
Old 12/7/09, 11:05 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Radon Fan

I can't tell from ther picture, but was the fan blowing the right way?

Also, did you ask him if he even looked up the mitigation protocols?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 12/7/09, 12:56 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is online now
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Radon Fan

Sorry about the spelling, I meant to say GUY!!!!! He did not think it was wrong!!!!



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #5  
Old 12/7/09, 4:35 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Radon Fan

Quote:
Originally Posted by bhartley View Post
Sorry about the spelling, I meant to say GUY!!!!! He did not think it was wrong!!!!
Please explain more about the Radon fan,what was wrong and what should be done.

Why would it pull air from the dryer?
Reply With Quote
  #6  
Old 12/7/09, 4:48 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Radon Fan

Quote:
Originally Posted by belliott View Post
Please explain more about the Radon fan,what was wrong and what should be done.

Why would it pull air from the dryer?
The only way it would pull air from the dryer is if the fan was mounted upside down. That would then blow outside air, down below the slab, increasing the sub slab air pressure, and forcing more soil gas up into the home, likely increasing the radon levels...

Assuming it is mounted in the correct direction and blowing the air from the sub slab soil to the exterior, then the issue is the discharge location. This should not terminate on the side of the home, but proceed up, through the roof, and discharge above the roof line. Having it exit the home at this location is probably fine, as long as it continues up the side of the house to discharge above the roof. I would also recommend that they install a water tube gauge to visually ensure that the fan is operating at any given time.

I've seen similar shortcuts myself, and always recommend a radon test. Many states have no requirements to follow the EPA recommendations, therefor there would be no requirement to fix the "defect". I've found that in many cases, even though the discharge is not in the proper location, the radon levels test under the desired 2.0 level as it is.

I then inform the client of the fact that the system is installed incorrectly. I also inform them of their current radon levels and recommend that they continue to monitor them and upgrade the system properly if the levels exceed their comfort level. Of course if the levels are more than 2 or definately if they are greater than 4, I recommend additional mitigation steps (preferably by a professional.)



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #7  
Old 12/7/09, 5:02 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Radon Fan

Ok I figured the reverse part of it but why is sidewall discharge an issue ?

Will people start glowing if they walk by or catch lung cancer if they pretend it is a big bong.
Whats the big deal?
Reply With Quote
  #8  
Old 12/7/09, 5:29 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is online now
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Radon Fan

The fan was discharging to the outside, right at the deck level.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #9  
Old 12/7/09, 5:31 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is online now
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Radon Fan

You are right, Mark, there was no manometer installed. The system should discharge above the roof line.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #10  
Old 12/7/09, 5:37 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Radon Fan

Quote:
Originally Posted by belliott View Post
Ok I figured the reverse part of it but why is sidewall discharge an issue ?

Will people start glowing if they walk by or catch lung cancer if they pretend it is a big bong.
Whats the big deal?
EPA standards call for venting above the roof line...

Here's the issues as I see them:

1) High radon levels will be at this area, and perhaps re-enter the home via the dryer duct, windows, soffit vents, and doors.

2) This would be in a location where humans would be (at least occasionally).

Think of it this way. You've got someone smoking a pack or two of cigarettes at this location every day. Do you want that class A carcinogen smoke here all the time? Probably not for a number of reasons, health being number one. Same thing with the radon gas.

Practically speaking, it's not a huge deal in and of itself. You can walk through the radon gas at very high levels and probably never have an ill effect. However, just like tobacco smoke, the more of it around, and the more you live in it, the higher your chances of lung cancer.

So it's not right, should be noted, new tests run, and leave the now educated buyer to make their own decisions...



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #11  
Old 12/7/09, 5:38 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Radon Fan

Quote:
Originally Posted by bhartley View Post
... manometer ...
That's the word I couldn't come up with... thanks



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #12  
Old 12/7/09, 11:07 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Radon Fan

It's a mess. Read: http://www.nachi.org/comsop.htm#18 It includes an inspection reporting form.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #13  
Old 12/8/09, 12:39 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Radon Fan

Quote:
Originally Posted by bhartley View Post
The fan was discharging to the outside, right at the deck level.
Ok
I thought this stuff dissipated quickly outside .
Kind of like if I was smoking a cigarette outside and the only harm to passer by would be psychological.

After all I thought the issue was long term exposure and doubt that people would be hanging out around the dryer vent.

Just guessing but I would think that would even be worse.
Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #14  
Old 12/8/09, 1:17 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Radon Fan

18.7.9 http://www.nachi.org/comsop.htm#18



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #15  
Old 12/8/09, 7:43 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Radon Fan

Do you know the state of Florida and a person within the Florida Health Department FORBIDS inspectors to mention, evaluate, or discuss the installation of a Radon Mitigation System. She says we are not trained and do not legally have any say in the fact. Hell they even allow people who INSTALL the system to test the system.

I have talked with her at length about this and what did I get? OOOO you want to renew your license...well I need the 128 forms from 2 years ago..blah blah blah...so needless to say...she wins! Gotta love the government!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Documents on which InterNACHI's radon course content is based: gromicko IAC2 Indoor Air Forum 4 1/18/09 6:53 AM
Radon Testing Kansas City dmoriconi Ancillary Inspection Services & Additional Topics 1 1/11/09 3:11 PM
Final review of Newman's radon references! Caoimhín P. Connell Ancillary Inspection Services & Additional Topics 12 10/4/08 12:23 PM
Radon Class in Oakville and Ottawa mkyriacou Canadian Inspectors 9 2/2/08 11:48 PM


All times are GMT -4. The time now is 7:51 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts