Default Radon mitigation system outlet

Decided to create new thread.

1 year warranty inspection.

Radon piping runs behind garage door header.

What would you report and why?

Attached Thumbnails



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 4/20/09 at 11:07 AM..
Reply With Quote
Find an InterNACHI certified South Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 4/20/09, 10:18 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by mlarson View Post
Decide to create new thread.

1 year warranty inspection.

Radon piping runs behind garage door header.

What would you report and why?

Attached Thumbnails
Mike,

I've never seen a radon pipe system go through a garage.

Does this pipe penetrate a slab/basement floor?

Where's the fan system?

The terminating vent should be above the roof line.
Reply With Quote
  #3  
Old 4/20/09, 10:21 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,896
Default Re: Radon mitigation system outlet

The termination not going through the roof line is the only thing I see with it too. Practically, i don't see that as being an issue where it is, although technically its wrong.
Reply With Quote
  #4  
Old 4/20/09, 11:06 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by dvalley View Post
Mike,

I've never seen a radon pipe system go through a garage.

Does this pipe penetrate a slab/basement floor?

Where's the fan system?

The terminating vent should be above the roof line.
Yes,


I posted this thread for the purpose of discussion and clarification.
Attached Thumbnails
radon-mitigation-system-outlet-img_3964-medium-.jpg.jpg
Views:	29
Size:	44.4 KB
ID:	28096   radon-mitigation-system-outlet-img_3965-medium-.jpg.jpg
Views:	28
Size:	61.4 KB
ID:	28097   radon-mitigation-system-outlet-img_3990-medium-.jpg.jpg
Views:	44
Size:	36.5 KB
ID:	28098  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 4/20/09, 11:50 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Radon mitigation system outlet

Ok, I see that the fan is operating normally.

The only thing that stands out is.... the vent should terminate above the roof line.
Reply With Quote
  #6  
Old 4/20/09, 12:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by dvalley View Post
Ok, I see that the fan is operating normally.

The only thing that stands out is.... the vent should terminate above the roof line.
Agreed but what do you tell the client to back that up

And

Above the first or second roof line?
Attached Thumbnails
radon-mitigation-system-outlet-img_3927-medium-.jpg.jpg
Views:	30
Size:	78.4 KB
ID:	28099  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 4/20/09 at 12:35 PM..
Reply With Quote
  #7  
Old 4/20/09, 12:35 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by mlarson View Post
Agreed but what do you tell the client to back that up

And

Above the first or second roof line?
Mike,

I would imagine the second (higher) roof line would be better than a lower roof line installation. A lower roof line installation would be improper venting due to the proximity of the sidewall.

I wouldn't necessarily tell my client which roof line. I would simply note that a properly installed radon mitigation system must termite above the roof line. I would then recommend a radon mitigation specialist to evaluate and estimate costs of bringing the termination to proper levels.

Last edited by dvalley; 4/20/09 at 12:38 PM..
Reply With Quote
  #8  
Old 4/20/09, 12:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by dvalley View Post
Mike,

I wouldn't necessarily tell my client which roof line. I would simply note that a properly installed radon mitigation system must termite above the roof line. I would then recommend a radon mitigation specialist to evaluate and estimate costs of bringing the termination at proper levels.
David, I added a pic to the previous post.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #9  
Old 4/20/09, 12:47 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by mlarson View Post
David, I added a pic to the previous post.
Mike,

The highest roof line would be the only solution to this upgrade. The lower roof line will not allow proper ventilation with that wall next to it.


http://www.epa.gov/radon/rrnc/index.html
Reply With Quote
  #10  
Old 4/20/09, 12:47 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,692
Default Re: Radon mitigation system outlet

I think the wording is eave, not rake.

Distance to adjacent windows must be considered.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 4/20/09, 12:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Radon mitigation system outlet

From ASTM 1465


Attached Thumbnails
radon-mitigation-system-outlet-6_5_4a.jpg   radon-mitigation-system-outlet-6_5_4b.jpg   radon-mitigation-system-outlet-6_5_4c.jpg  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #12  
Old 4/23/09, 1:57 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,581
Default Re: Radon mitigation system outlet

http://www.nachi.org/comsop.htm#18

18.7.9

Although I think the real issue here is does the radon pipe in the garage compromise the firewall if/where it passes through to the home. And unlike a mere firewall compromise... a radon fan is pulling 270 cfm... and so makes for a nice fire flue.



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"

Last edited by gromicko; 4/23/09 at 2:03 AM..
Reply With Quote
  #13  
Old 4/23/09, 10:08 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Radon mitigation system outlet

Quote:
Originally Posted by gromicko View Post
http://www.nachi.org/comsop.htm#18

18.7.9

Although I think the real issue here is does the radon pipe in the garage compromise the firewall if/where it passes through to the home. And unlike a mere firewall compromise... a radon fan is pulling 270 cfm... and so makes for a nice fire flue.
Yes it is an issue to be aware of but if you look at pic 1 in the first post you will see that the appropriate fire stop is in place where it penetrates the living space just as it is in this photo.




"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radon Testing Kansas City dmoriconi Ancillary Services & Additional Topics 1 1/11/09 4:11 PM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Let's talk ESOP rcooke General Inspection Discussion 231 2/22/08 9:55 PM
Radon mitigation exhaust sfalvey General Inspection Discussion 10 2/21/06 3:18 PM


All times are GMT -4. The time now is 12:21 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts