  #1  
Old 12/5/09, 9:21 AM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Ballast Disconnects

When you guys are doing commercial inspections, do you have to check the ballast for disconnects? It has been an NEC code on retrofits since Jan of 08.

I find it odd how many times I talk to commercial property owners that are un-aware of this code. I am guessing because it is only required on retrofits.

Here is what they look like

http://www.aikencolon.com/Luminaire-...cts_c_741.html

Basically it is a safety issue to protect against shock and/or potential falls. It sits in line and makes a "quick connect" type of connection, instead of just two wire nuts.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Energy Audit

Blower Door
Laser Level
Miller Fall Protection

Last edited by jkaylor; 12/7/09 at 9:35 AM..
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #2  
Old 12/5/09, 3:56 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Ballast Disconnects

If someone is checking for that they have a lot of time on their hands.
Reply With Quote
  #3  
Old 12/5/09, 6:40 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Ballast Disconnects

So when you guys do inspections you do not have to worry about new code items (on any system)? Or do you only have to worry about the larger safety type code items.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Energy Auditor

Blower Doors
Laser Levels
MK Tile Saw

Last edited by jkaylor; 12/7/09 at 9:36 AM..
Reply With Quote
  #4  
Old 12/5/09, 6:59 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Ballast Disconnects

Quote:
Originally Posted by jkaylor View Post
So when you guys do inspections you do not have to worry about new code items (on any system)? Or do you only have to worry about the larger safety type code items.

JJ
Are you selling tools for easy testing?

Which do you feel would be useful?

Personally I think that switch idea is overboard.
If you are an Electrician you know how to change wire nuts (live)
Reply With Quote
  #5  
Old 12/6/09, 11:23 AM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Ballast Disconnects

No, I am more trying to figure out exactly what type of items in a commercial inspection are addressed. I have a very good idea of how a home inspection is performed, but the commercial ones I am very vague on.

Dealing with code items is a good niche for suppliers, so I am trying to figure a new angle of marketing for items like the ballast disconnect. It would be pretty easy to get a list of new commercial property owners, but if items like the ballast disconnect are not addressed during a commercial inspection it would be a waste of time to market it through those means.

Thanks for the info.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Energy Audits

Blowerdoor
Line Level
MK Saw

Last edited by jkaylor; 12/7/09 at 9:47 AM..
Reply With Quote
  #6  
Old 12/6/09, 11:28 AM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Ballast Disconnects

First of all has this area adopted the new code. I know many areas are not because of the new upgrades are very costly in a down market. I know Florida has not adopted it and may just skip it for now. You can't make people update stuff that was never required. I do like you thoroughness and attention to detail.
Reply With Quote
  #7  
Old 12/6/09, 1:12 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Ballast Disconnects

wow, states do not have to adapt NEC codes? Or heck any federal type codes for that matter. I never knew that.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Fluke Ti32

TSI 8371
UEI Combustion Analyzer
Alnor Flow Hood

Last edited by jkaylor; 12/7/09 at 9:45 AM..
Reply With Quote
  #8  
Old 12/6/09, 1:24 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Ballast Disconnects

Quote:
Originally Posted by jkaylor View Post
wow, states do not have to adapt NEC codes? Or heck any federal type codes for that matter. I never knew that.

JJ
True
Local AHJ 's usually follow codes that are several years behind or more from what I read.

NEC is more of a suggestion (not a law)

That's why we are not code Inspectors, as we would need to learn the codes of every little town.
Reply With Quote
  #9  
Old 12/6/09, 6:54 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Ballast Disconnects

Quote:
Originally Posted by jkaylor View Post
wow, states do not have to adapt NEC codes? Or heck any federal type codes for that matter. I never knew that.

JJ
States, counties, cities... can adopt all the NEC, a portion of the NEC or none of the NEC. Think about it, the day it comes out you think its mandatory? What about people LEARNING whats in the code first. Federal Code? This is not a FEDERAL CODE! As far as I know there is no such thing as a Federal Code..
Reply With Quote
  #10  
Old 12/6/09, 7:49 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Ballast Disconnects

I just meant federal in the sense that it is a country wide code rather than a state or local code, although it can be chose to be adopted or not adopted by a local or state governing body.

What I do not understand behind this one (NEC) in particular is that it is actually put out by the NFPA. I would think that would be a major concern for property owners, considering if someone were to be injured in a fire and their building was not 100% NEC complaint, they could be potentially be held liable.

This is going a lot deeper than my orignal question, but it is definately interesting conversation.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Infrared Camera

Blower Door
Combustion Analyzer
Flow Hood
Construction Laser

Last edited by jkaylor; 12/11/09 at 3:58 PM..
Reply With Quote
  #11  
Old 12/6/09, 9:23 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Ballast Disconnects

Jason - I do understand, but you cannot account for each and every situation that COULD occur. So should every house have a centralized sprinkler system installed? I mean that would save lives, stop the spread of fire to other house and maybe even save some household items.

I do understand your point, I just don't want you to make statements that are not true and would not make you look 100% Proficient. I have done this in the past myself, state something that isn't true to your jurisdiction. There is nothing more exciting for a licensed tradesman to do then to make a home inspector look incompetent. Just be sure what you mention is fact and if you don't know...this is the place to ask, some very smart people on this chat board....
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
2 Service Disconnects tlarsen Electrical Inspections 11 8/21/09 8:41 AM
A question on outside disconnects acassady Electrical Inspections 2 5/15/09 8:30 PM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
Two disconnects bsmith Electrical Inspections 4 4/20/06 10:19 PM


All times are GMT -4. The time now is 7:57 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts