An Investor I have done many inspections for emailed me this question yesterday, I looked at the NFPA website and did not see the answer doing a quick search, maybe somebody here might know.

This is an office building with 6 suites, two stories, but none of the suites are two stories.

Dale,

Here is the question…

The building is 28278sf (two stories) and has an office space on the second story with 4251Sf. The office has only a primary entrance, while the adjacent office has a primary entrance and a rear stairwell. So a door connecting the two offices was put in, to allow access from office 1 to the rear door of office two.

Questions:

1. How large does an office need to be to require a second door (or how far from the front door?)
2.If a second door is needed, can it be to the front lobby (same side of building as primary door?)

Thanks,
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #2  
Old 9/21/08, 2:44 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,294
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: Fire Exit Question

Dale,
I seem to remember that there is a distance thing from interior to exits. I will keep an eye on this post



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 9/21/08, 2:58 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,067
Larry D. Kage .
Default Re: Fire Exit Question

From:
http://www.nachi.org/comsop

(I haven't done much commercial so there may be more to what you're asking than this.)


6.5.12 Life-safety
I. The inspector should:
A. Inspect fire access roads and report on any obstructions or overhead wires lower than 13 feet 6 inches.
B. Inspect the address or street number to determine that it is visible from the street with numbers in contrast to their background.
C. Inspect and determine that a 3-foot clear space exists around the circumference of fire hydrants.
D. Verify that hinged shower doors open outward from the shower and have safety glass conformance stickers or indicators.
E. Inspect to determine that the storage of flammable and combustible materials are orderly, separated from heaters by distance or shielding so that ignition cannot occur, and not stored in exits, boiler rooms, mechanical rooms, or electrical equipment rooms.
F. Inspect to determine that a "No Smoking" sign is posted in areas where flammable or combustible material is stored, dispensed, or used.
G. Inspect for the presence of fire alarm systems.
H. Inspect for alarm panel accessibility.
I. Inspect for the presence of portable extinguishers and determine that they are located in conspicuous and readily available locations immediately available for use and not obstructed or obscured from view.
J. Inspect to determine that a portable fire extinguisher exists within a 30 foot travel distance of commercial-type cooking equipment that uses cooking oil or animal fat.
K. Inspect to determine that manual actuation devices for commercial cooking appliances exist near the means of egress from the cooking area, 42-48 inches above the floor, 10-20 feet away, and clearly identifying the hazards protected.
L. Inspect to determine that the maximum travel distance to a fire extinguisher is 75 feet.
M. Inspect for the presence of sprinkler systems and determine if they were ever painted other than at the factory.
N. Inspect for the presence of emergency lighting systems.
O. Inspect for exit signs at all exits and inspect for independent power sources such as batteries.
P. Inspect for the presence of directional signs where exit location is not obvious.
Q. Inspect for the presence of signs over lockable exit doors stating "This Door Must Remain Unlocked During Business Hours."
R. Inspect for penetrations in any walls or ceilings that separate the exit corridors and/or stairwells from the rest of the building.
S. Inspect for fire separation doors that appear to have been blocked or wedged open or that do not automatically close and latch.
T. Inspect exit stairwell handrails.
U. Inspect for exit trip hazards.
V. Inspect for the presence of at least two exits to outside or one exit that has a maximum travel distance of 75 feet.
W. Inspect exit doorways to determine that they are not less than 32 inches in clear width.
X. Inspect to determine that the exit doors were not locked from the inside, chained, bolted, barred, latched or otherwise rendered unusable at the time of the inspection.
Y. Inspect to determine that the exit doors swing open in the direction of egress travel.
Z. Inspect the storage at the time of the inspections to determine if it is potentially obstructing access to fire hydrants, fire extinguishers, alarm panels, or electric panel boards, or if it is obstructing aisles, corridors, stairways or exit doors, or if it is within 18 inches of sprinkler heads or if it is within 3 feet of heat generating appliances or electrical panel boards at the time of the inspection.



"An Education, not just an Inspection"


Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525



Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 9/21/08, 3:21 PM
Robert E. Elliott's Avatar
Robert E. Elliott Robert E. Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 5,712
Robert E. Elliott .
Default Re: Fire Exit Question

Haaha
Watching my Bears , but search here.


http://www.facilityzone.com/search.a...&submit=Search
Reply With Quote
  #5  
Old 9/21/08, 3:55 PM
Mark Jones Mark Jones is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Roundlake Beach, IL
Posts: 212
Mark Jones is well trusted Mark Jones is well trusted Mark Jones is well trusted
Default Re: Fire Exit Question

Bob,
I'm watching the Bears, NASCAR, Message board and pizza rolls in oven.
How's that for multi tasking?



Mark Jones
Allmark Home Inspection Services Inc.
Serving all of Northern Illinois

Phone: 847 651 2053
E-Mail: AllmarkInspect@aol.com

www.AllmarkHomeInspection.com
Reply With Quote
  #6  
Old 9/21/08, 4:32 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 178
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Re: Fire Exit Question

Dale. it depends on several different items. Distance to exit, number of employees, type of occupancy etc. If you need a difinitive answer give me a call and we will nail it down.
Reply With Quote
  #7  
Old 9/21/08, 5:01 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,624
Dale Duffy .
Default Re: Fire Exit Question

Quote:
Originally Posted by gheller View Post
Dale. it depends on several different items. Distance to exit, number of employees, type of occupancy etc. If you need a difinitive answer give me a call and we will nail it down.
Hi Gary,

Just returned from my Sunday inspections-------, this is getting old, 7 days a week--

Yes I know all of the above statements, and after I posted the investors email to me I realized that I should go there and take some measurements, and look at the building for a fee, his question is too vague...

My brain is like someone put it in a blender---
Reply With Quote
  #8  
Old 9/21/08, 5:05 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,624
Dale Duffy .
Default Re: Fire Exit Question

Thanks everyone, I called him and told him I need measurements and too look at exactly what he's talking about, so I will go there this week (for a fee---).
Reply With Quote
  #9  
Old 9/21/08, 5:10 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 8,917
Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute
Default Re: Fire Exit Question

Quote:
Originally Posted by dduffy View Post
An Investor I have done many inspections for emailed me this question yesterday, I looked at the NFPA website and did not see the answer doing a quick search, maybe somebody here might know.

This is an office building with 6 suites, two stories, but none of the suites are two stories.

Dale,

Here is the question…

The building is 28278sf (two stories) and has an office space on the second story with 4251Sf. The office has only a primary entrance, while the adjacent office has a primary entrance and a rear stairwell. So a door connecting the two offices was put in, to allow access from office 1 to the rear door of office two.

Questions:

1. How large does an office need to be to require a second door (or how far from the front door?)
2.If a second door is needed, can it be to the front lobby (same side of building as primary door?)

Thanks,

Hi. Dale;

Hey, this is not a typical Home Inspector question buddy. ha. ha.

This would be more well directed to an Architectural Consultant.

To answer your question, a copy of the IBC and the NFPA would be a necessity. None of which I have for reference.

What I do know from your description, is that the building would be classified as a Class II or Group B. And this is all from memory and use.

Your answer can be found in the IBC Chapter 3

Every facility, building, structure, or portion thereof shall be provided with exits as required per it's classification.

Exit is a continuous and unobstructed means of egress to a public way and shall include intervening aisles, doors, doorways, gates, corridors, exterior exit balconies, ramps, stairways, smoke-proof enclosures, horizontal exits, exit passage ways, exit courts, and yards.

MINIMUM EGRESS REQUIREMENTS

MINIMUM OF TWO EXITS OTHER THAN ELEVATORS ARE REQUIRED WHERE NUMBER OF OCCUPANTS IS AT LEAST

50

In every facility, building, or structure, exits shall be so arranged and maintained as to provide free and unobstructed egress from all parts of the facility, building, or structure at all times when it is occupied. No lock or fastening device to prevent free evacuation from the inside of any room, space, facility, building, structure or portion thereof, shall be installed.

When serving an occupant load of fifty (50) or less, the corridor width may be reduced to thirty six (36) inches.

Stairways serving an occupant load of forty-nine (49) or less, the stairway width may be reduced to thirty-six (36) inches.

The capacity of means of egress for any floor, balcony, tier, mezzanine, or other occupied space shall be sufficient for the occupant load.

The occupant load shall be the maximum number of persons that may be in the space at any time. The maximum occupant load other than assembly use shall not exceed the capacity of the exits. The occupant load for an assembly building or portion thereof may be increased when approved by building official and the appropriate requirements are met.

If only two (2) exits are required, they shall be placed a distance apart equal to not less than one-half (1/2) of the length of the maximum overall diagonal dimension of the facility, building, structure, or area to be served measured in a straight line between exits.

I believe that one of your questions might be answered here, but not sure.

Rooms may have one (1) exit through an adjoining or intervening room, where such adjoining rooms or areas are accessory to the area served, which provides a direct, obvious, and unobstructed means of travel to an exit corridor, exit enclosure, or until egress is provided from the facility, building, or structure.
In other than dwelling units, exits shall not pass through kitchens, rest rooms, closets, or spaces used for similar purposes.
EXCEPTIONS: Rooms with a cumulative occupant load of ten (10) or less may exit through more than one (1) intervening room.

I believe you could verify all this with the IBC.

I would strongly urge you to consult with the AHJ or a local Architect.

Hope this helps a bit anyways.

Marcel



Cyr Home Inspections
IAC2 Certified
NACHI04070211


http://co.nachi.org/inachiawards/inachiawards551.html
http://co.nachi.org/inachiawards


mcyrhammer@verizon.net

Commercial Builder
Ouellet Associaties Inc.
www.oaconstruction.com
Reply With Quote
  #10  
Old 9/21/08, 5:44 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,624
Dale Duffy .
Default Re: Fire Exit Question

Quote:
Originally Posted by mcyr View Post
Hi. Dale;

Hey, this is not a typical Home Inspector question buddy. ha. ha.

This would be more well directed to an Architectural Consultant.

To answer your question, a copy of the IBC and the NFPA would be a necessity. None of which I have for reference.

What I do know from your description, is that the building would be classified as a Class II or Group B. And this is all from memory and use.

Your answer can be found in the IBC Chapter 3

Every facility, building, structure, or portion thereof shall be provided with exits as required per it's classification.

Exit is a continuous and unobstructed means of egress to a public way and shall include intervening aisles, doors, doorways, gates, corridors, exterior exit balconies, ramps, stairways, smoke-proof enclosures, horizontal exits, exit passage ways, exit courts, and yards.

MINIMUM EGRESS REQUIREMENTS

MINIMUM OF TWO EXITS OTHER THAN ELEVATORS ARE REQUIRED WHERE NUMBER OF OCCUPANTS IS AT LEAST

50

In every facility, building, or structure, exits shall be so arranged and maintained as to provide free and unobstructed egress from all parts of the facility, building, or structure at all times when it is occupied. No lock or fastening device to prevent free evacuation from the inside of any room, space, facility, building, structure or portion thereof, shall be installed.

When serving an occupant load of fifty (50) or less, the corridor width may be reduced to thirty six (36) inches.

Stairways serving an occupant load of forty-nine (49) or less, the stairway width may be reduced to thirty-six (36) inches.

The capacity of means of egress for any floor, balcony, tier, mezzanine, or other occupied space shall be sufficient for the occupant load.

The occupant load shall be the maximum number of persons that may be in the space at any time. The maximum occupant load other than assembly use shall not exceed the capacity of the exits. The occupant load for an assembly building or portion thereof may be increased when approved by building official and the appropriate requirements are met.

If only two (2) exits are required, they shall be placed a distance apart equal to not less than one-half (1/2) of the length of the maximum overall diagonal dimension of the facility, building, structure, or area to be served measured in a straight line between exits.

I believe that one of your questions might be answered here, but not sure.

Rooms may have one (1) exit through an adjoining or intervening room, where such adjoining rooms or areas are accessory to the area served, which provides a direct, obvious, and unobstructed means of travel to an exit corridor, exit enclosure, or until egress is provided from the facility, building, or structure.
In other than dwelling units, exits shall not pass through kitchens, rest rooms, closets, or spaces used for similar purposes.
EXCEPTIONS: Rooms with a cumulative occupant load of ten (10) or less may exit through more than one (1) intervening room.

I believe you could verify all this with the IBC.

I would strongly urge you to consult with the AHJ or a local Architect.

Hope this helps a bit anyways.

Marcel
Yes, 10-4..I know all that ole buddy..I called a city of Scottsdale commercial building inspector, friend of mine (where the building is located, Scottsdale), he will meet me there next week and we will figure out the answer for the buyer when we have all the information needed to make a judgment...I will let the City do that---

And charge for my services of course---
Reply With Quote
  #11  
Old 9/21/08, 5:51 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 10,645
James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute James H. Bushart has a reputation beyond repute
Send a message via MSN to jbushart
Default Re: Fire Exit Question

Quote:
Originally Posted by dduffy View Post
An Investor I have done many inspections for emailed me this question yesterday, I looked at the NFPA website and did not see the answer doing a quick search, maybe somebody here might know.

This is an office building with 6 suites, two stories, but none of the suites are two stories.

Dale,

Here is the question…

The building is 28278sf (two stories) and has an office space on the second story with 4251Sf. The office has only a primary entrance, while the adjacent office has a primary entrance and a rear stairwell. So a door connecting the two offices was put in, to allow access from office 1 to the rear door of office two.

Questions:

1. How large does an office need to be to require a second door (or how far from the front door?)
2.If a second door is needed, can it be to the front lobby (same side of building as primary door?)

Thanks,
Dale,

Table 1019.2 (IBC 2006) defines the buildings allowed to have one exit (one story and two story) but it uses the number of occupants and the travel distance (in feet) to the outside to determine when only one exit is allowed.



James H. Bushart, Certified Professional Inspector

Member, International Code Council (ICC)
Member, American Society of Home Inspectors (ASHI)
Member, International Association of Certified Home Inspectors (iNACHI)
Member, Missouri Association of Building Officials and Inspectors (MABOI)
Member, Missouri Association of Real Estate Inspectors (MAREI)

www.missourihomeinspection.com
Reply With Quote
  #12  
Old 9/21/08, 5:52 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 8,917
Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute
Default Re: Fire Exit Question

Sounds like an equitable plan to me buddy, (for you that is).

Marcel



Cyr Home Inspections
IAC2 Certified
NACHI04070211


http://co.nachi.org/inachiawards/inachiawards551.html
http://co.nachi.org/inachiawards


mcyrhammer@verizon.net

Commercial Builder
Ouellet Associaties Inc.
www.oaconstruction.com
Reply With Quote
  #13  
Old 9/21/08, 6:10 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,624
Dale Duffy .
Default Re: Fire Exit Question

Quote:
Originally Posted by jbushart View Post
Dale,

Table 1019.2 (IBC 2006) defines the buildings allowed to have one exit (one story and two story) but it uses the number of occupants and the travel distance (in feet) to the outside to determine when only one exit is allowed.
Thanks Jim....I will let the City give the man a go ahead in writing, and of course charge for my services.....I think the investor is asking a question which really cannot be answered yet anyway, he plans on remodeling, and really needs an architect to determine what the size of the space will be after improvements are made.

Unless he's going to do work without a permit, which is not unusual here---