Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by mcyr View Post
NFPA 80, Standard for Fire Doors and Other Opening Protectives – 2007 edition, requires documented inspections of fire-rated door assemblies on an annual basis.
Yes, but I cannot find any jurisdictions that have adopted NFPA 80 such that it has the force of law. The existence of the model code alone does not make it a requirement. Mind you, I think it's a fine idea, but I'd be hard pressed to tell anyone it's expressly required. There are some contradictions between NFPA 80 and the ADA which will present interesting puzzles for the inspector.
Reply With Quote
  #17  
Old 1/3/09, 8:29 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by Marc D. Shunk View Post
Yes, but I cannot find any jurisdictions that have adopted NFPA 80 such that it has the force of law. The existence of the model code alone does not make it a requirement. Mind you, I think it's a fine idea, but I'd be hard pressed to tell anyone it's expressly required. There are some contradictions between NFPA 80 and the ADA which will present interesting puzzles for the inspector.
Hi. Mark, It is my understanding from what I found elsewhere, that unless NFPA 80 is listed as an adopted code in the Jurisdition Area of the Inspection, it can not be enforced as such.
What are the puzzles you are talking about as far as contradictions. ?

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #18  
Old 1/3/09, 8:34 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by mcyr View Post
Hi. Mark, It is my understanding from what I found elsewhere, that unless NFPA 80 is listed as an adopted code in the Jurisdition Area of the Inspection, it can not be enforced as such.
Yes, that's what I mean. Don't get me wrong... If I was an inspector, I'd be point to all these model codes to try to get people to let me inspect these fire doors. Hell, I'd inspect the fake plants in hotel lobbies if I could point to something official sounding that seemed to indicate they should be inspected.

Quote:
Originally Posted by mcyr View Post
What are the puzzles you are talking about as far as contradictions. ?
I've bumped into a few over the years, but the one that sticks in the front of my mind is the 5 or 6 pound opening force requirement from the ADA, and the fact that the fire door codes normally require a lot stouter closer than that. The door may be within the opening force requirements in a building that is positively pressureized, but when the alarm goes off the f/a shuts down, and smoke fans come on, and the opening force becomes much greater. Nothing like trapping in 'the least of these'.
Reply With Quote
  #19  
Old 1/3/09, 8:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by Marc D. Shunk View Post
Yes, that's what I mean. Don't get me wrong... If I was an inspector, I'd be point to all these model codes to try to get people to let me inspect these fire doors. Hell, I'd inspect the fake plants in hotel lobbies if I could point to something official sounding that seemed to indicate they should be inspected.

I've bumped into a few over the years, but the one that sticks in the front of my mind is the 5 or 6 pound opening force requirement from the ADA, and the fact that the fire door codes normally require a lot stouter closer than that. The door may be within the opening force requirements in a building that is positively pressureized, but when the alarm goes off the f/a shuts down, and smoke fans come on, and the opening force becomes much greater. Nothing like trapping in 'the least of these'.

This may answer your question;

Resolving Code Questions in a Less-Than-Perfect World

Meeting positive pressure, ADA and other requirements isn’t always a cut-and-dried proposition. Look to the application for guidance when it comes time to make a tough decision or resolve an apparent conflict of regulations.

By Kurt Roeper, Fire & Life Safety Program Manager and Ron Ratell, ADA Program Manager
Exits, Closers & Doors Category
Carmel, IN 46032
Ingersoll Rand Security Technologies
Carmel, Indiana

What do you do when two code requirements seem to be in conflict? Or when two different regulations influence the design of an opening? A case in point is when the Americans with Disabilities Act (ADA) Title III, not a building code but a federal civil rights law, calls for accessibility, but life safety and building codes require closed doors if a fire occurs. When must a door and its hardware meet positive pressure requirements or when are they not an issue? This article will look at a few of these apparent conflicts that specifiers and suppliers face in the decision-making process. In the end, the requirements of each specific application will help point toward a conclusion that is unique to that case.

Door Closers, Power Operators and the ADA

Title III of the Americans with Disabilities Act (ADA) requires public accommodations to provide goods and services to people with disabilities on an equal basis with the rest of the general public. Its goal is to afford every individual the opportunity to benefit from our country’s businesses and services, and to allow each to benefit from the patronage of all Americans. For existing buildings, the regulations require that architectural and communication barriers that are structural must be removed in public areas when their removal is readily achievable—in other words, easily accomplished and able to be carried out with out much difficulty or expense. All new and altered buildings also must meet the prescribed accessibility requirements.

The ADA (Title III) defines an "accessible" opening as one that provides a door with a minimum clear opening of 32", easily manipulated handles, a maximum opening force, a minimum closing time, and the capability of being opened to 90°.

Although all entrances or openings in a building need not be ADA-compliant, designated entrances must meet ADA requirements. In cases where the NFPA 101 Life Safety Code applies, it may take precedence over ADA when a choice must be made (check with local authority having jurisdiction). For example, the hardware on a fire-rated door would not have to meet all accessibility requirements if doing so would compromise its ability to meet life safety codes.

When faced with this situation, the specifier must decide what multiple functions an opening has and how to prioritize them. Whether on a new building or a renovation, the questions may include:
  1. Must the opening be ADA accessible (compliant)?
  2. Can this be achieved with a standard mechanical door closer?
  3. Do door conditions, usage, or convenience call for a power operator?
  4. What security requirements apply, and will they require card readers, biometrics, electric strikes and other electrical or electronic interfaces?
There are several ways to make an opening ADA compliant when it comes to specifying a door closer. For interior doors, the least costly is to use a standard mechanical closer but specify the size with the lowest power (size 1), which requires a force of less than five pounds to open the door as required by ADA code. A closer with adjustable spring power also can be used if it is set at the same maximum required opening force. If the door is in a corridor where the HVAC system creates a high pressure differential, this light force may not be enough to close and latch the door properly. In such cases, a power operator probably will be needed to meet ADA requirements. It also is likely to provide greater convenience for all users, depending on how the opening will be used and the type of operator that is selected. For 3' interior fire doors, NFPA 80 recommends a size 3 closer, which underscores the fact that fire doors need not comply with the 5-pound ADA requirement.

Exterior doors are another case. Neither ADA nor ICC/ANSI A 117.1 give an opening force limit for exterior doors. Because they may be subject to high wind conditions or other external influences, a power operator may be the best way to ensure both ADA compliance and effective operation.

For power operators in particular, it may be necessary to consider product design and its effect on the application. Some power operator designs are driven by a motor and gears and sometimes separated by a clutch. Even when the doors are being operated manually, the motor and gears are being turned, and this could shorten their life on a high-usage opening. Unless the door will be operated automatically most or all of the time, it may be better for these applications to select a power operator that is built around a standard mechanical hydraulic door closer with the addition of a motor and clutch. Then it will function as any other mechanical closer most of the time, with a pushbutton-operated power assist available when needed.

Power operator features and options make it possible to meet a variety of application situations. Power operators that are designed for primarily automatic opening can be opened manually when needed. Even fully automatic sliding doors (high-energy doors) can be pushed open manually in an emergency (called full break out feature). Many power operators can be tied into a building’s fire alarm system so they will fail-safe and automatically close if the alarm is activated; thus maintaining the fire wall or fire barrier integrity. However, they can be opened manually under these conditions to allow safe egress.

Building Codes and Positive Pressure Requirements

The push for positive pressure began under the jurisdiction of the International Congress of Building Officials (ICBO), which had produced the Uniform Building Code, in the early '90s and was adopted in 1996. During this same period, a move developed to combine the three model building codes into a single, national code, by a model code group known as the International Code Council (ICC). The ICC would combine model codes produced by the BOCA (Building Officials and Code Administrators), SBCCI (Southern Building Code Congress International), and ICBO into a single model code. The working draft of the International Building Code was published in May, 1997, with a statement allowing the test protocol to be determined by the local authority having jurisdiction.

Further impetus was added with the recent publication of NFPA 5000, the first building code developed through the American National Standards Institute (ANSI) –accredited process. NFPA 5000 is an integral part of the Comprehensive Consensus Codes™ (C3) set, which currently is being developed by NFPA and several partner organizations. This model code recognizes positive pressure testing for fire doors and provides yet another option for municipalities and states looking to update their building codes. An online review of NFPA 5000 is available at
www.nfpa.org

Since positive pressure requirements first were introduced, the initial concerns have been answered, and gaps in information have largely been filled. As more jurisdictions have begun to adopt UL10C standards for UBC 7-2, earlier concerns about how to meet them have been replaced by an awareness of where and when they apply. UL 10C is a positive pressure fire test that is designed to replicate more closely what happens to a door in an actual fire and to verify that the door and hardware are in compliance with the positive pressure requirements set forth in the Uniform Building Code under UBC 7-2. In the test, door hardware over 40" high is affected more than in the previous test, and the intent is to improve its ability to provide fire and life safety in the event of a fire.

Under the previous fire test, no internal pressure was applied to the door opening. Instead, air was pulled from the non-fire side of the door into the chamber on the fire side of the door. If there were small gaps between the door and frame, the air flowing through them, from the non-fire side to the fire side and out the exhaust, would prevent most flame transfer to the non-fire side. The positive pressure test reverses this flow, drawing the air in through the sill and forcing it out through the operating clearances between the door and door frame. This makes it much more likely that there could be some flame transfer through any gaps between the door and the frame, especially at the top of the door where most closers are mounted.

Higher temperature levels from the test may cause the closer’s hydraulic fluid to expand and escape from the closer or the closer cover to melt. Although the closer is often mounted on the non-fire side of the door, the test determines whether the hydraulic fluid could leak enough or the cover to melt enough to support combustion and cause the fire to spread to the non-fire side of the door. It is useful to know that some manufacturers supply UL10C approved product as standard, while other manufacturers upcharge for the UL10C approved product. If compliance with UL10C is required, this should be considered when comparing alternatives.

Architects and specifiers should check the following points to ensure compliance with UL10C:
  1. Check current projects to determine whether UL10C compliance is required.
  2. Make sure that UL10C compliance is written into the master specification.
  3. Get a letter of certification from the manufacturer to ensure that products specified are in compliance.
  4. Make sure the products submitted and installed are in compliance. Look for the compliance label "Conforms to Standards UBC 7-2 (1997) and UL 10C."
Although they are far from universal, building codes that include positive pressure compliance gradually are being adopted as the standard by more and more state and local municipalities. Most manufacturers have revised their fire labels to show that specific products have been approved by Underwriters Laboratory (UL) or Warnock Hersey and comply with positive pressure tests under UBC 7.2 (1997) and UL 10 C, making it easy to select the right door, frame and hardware.

Getting the Information and Support You Need

Today more than ever, it is imperative to provide every facility with the highest applicable levels of safety and security. At the same time, it is necessary to comply with an ever-growing list of building codes and other regulations, including ADA, the NFPA 101 Life Safety Code, NFPA 80 Standards for Doors and Windows, and other federal, state and local building codes. With this in mind, it can be helpful to partner with manufacturers that follow these changing requirements closely and can provide guidance in resolving seemingly conflicting demands. As you look to develop such partnerships, consider whether the manufacturer has the ability to work with you in creating a multi-level, layered approach to key management, access control and security. Such an approach begins with mechanical access and egress, including doors and their hardware, mechanical locks, keying systems and portable security; it progresses through electronic access control and key management, including standalone and hard-wired systems; networked access control and biometrics are added to manage perimeter and controlled public openings; and a final layer of facility integration encompasses management of both assets and people, including access control, time and attendance, and personnel scheduling. This foundation will enable a facility’s security to grow with its needs, with a broad-based resource for solving safety and security dilemmas.

Note: A brochure on meeting ADA accessibility requirements is available through Ingersoll Rand distributors or from Ingersoll Rand Security Technologies, 877-840-3621.

Hope this helps.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #20  
Old 1/3/09, 9:32 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,597
Default Re: www.FireDoorInspector.org

The author is assuming that the pressure required to close and latch a door is equal to the pressure needed to open it. It often isn't. This is becaue a fully open door's momentum increases as it closes or falls (as the momentum of all falling things do), to a maximum, just before latching.



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #21  
Old 1/3/09, 9:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by gromicko View Post
The author is assuming that the pressure required to close and latch a door is equal to the pressure needed to open it. It often isn't. This is becaue a fully open door's momentum increases as it closes or falls (as the momentum of all falling things do), to a maximum, just before latching.
Door closing speed

Door latching speed

Backcheck

All three are settings on a commercial closer whether ADA or not.
Latching speed would be the beholder on the Fire safety part of it.

Door closing speed to meet ADA requirements

Opening speed force is different than the closing force of the closer.






Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #22  
Old 1/3/09, 9:48 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,597
Default Re: www.FireDoorInspector.org

Yes. Closing speed as well as door weight contribute to closing pressure.



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #23  
Old 1/3/09, 10:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by gromicko View Post
Yes. Closing speed as well as door weight contribute to closing pressure.
Nick, Door closers are usually classified in class 1-6, which is then matched in the design stage by the hardware consultant to make sure the closer is strong enough for the weight of the door.

The classes range from 3, 5, 8, 11, 14 # pressure measured 30" from the hinge.

So the weight of the door is really errelevent when the closer is sized for the weight.
It will only close as fast as the valve setting allows it to.
It is all about hydraulics dear Watson.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #24  
Old 1/4/09, 9:18 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: www.FireDoorInspector.org

Great info. Marcel. As far as the sidecar goes, lets wait till spring!!!!!
Reply With Quote
  #25  
Old 1/4/09, 9:52 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by prussell View Post
Great info. Marcel. As far as the sidecar goes, lets wait till spring!!!!!
Considering the temperatures we have been getting, you might be right.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #26  
Old 1/4/09, 11:28 AM
Chris McDonald Chris McDonald is online now
InterNACHI Member
 
Join Date: Mar 2007
Location: Jaffrey, NH
Posts: 69
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by Marc D. Shunk View Post
Yes, but I cannot find any jurisdictions that have adopted NFPA 80 such that it has the force of law. The existence of the model code alone does not make it a requirement. Mind you, I think it's a fine idea, but I'd be hard pressed to tell anyone it's expressly required. There are some contradictions between NFPA 80 and the ADA which will present interesting puzzles for the inspector.
NFPA 80 is adopted under NFPA 101 (Life Safety Code) as a referenced publication. According to NFPA 101: "The documents or portions thereof listed in this chapter (Chapter 2: Referenced Publications) are referenced within this code and shall be considered part of the requirements of this document."
Therefore, for jurisdictions that have adopted NFPA 101, NFPA 80 does have the force of law when the Authority Having Jurisdiction conducts a life safety code inspection unless the jurisdiction has determined that the requirements for NFPA 80 is excluded from that inspection.



Chris McDonald, CMI
Vice President, New Hampshire State Chapter, NACHI
McDonald Home Inspection Services, LLC
Jaffrey, NH 03452
Reply With Quote
  #27  
Old 1/4/09, 12:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by cmcdonald View Post
NFPA 80 is adopted under NFPA 101 (Life Safety Code) as a referenced publication. According to NFPA 101: "The documents or portions thereof listed in this chapter (Chapter 2: Referenced Publications) are referenced within this code and shall be considered part of the requirements of this document."
Therefore, for jurisdictions that have adopted NFPA 101, NFPA 80 does have the force of law when the Authority Having Jurisdiction conducts a life safety code inspection unless the jurisdiction has determined that the requirements for NFPA 80 is excluded from that inspection.
That's awesome that you were able to find that. I do have a copy of the life safety code at the office. I'm curious now to read now the entire list of referenced documents.
Reply With Quote
  #28  
Old 1/4/09, 12:43 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Here is the Adoption Map of LifeSafety 101
http://www.nfpa.org/assets/images/NF...doptionMap.gif








Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #29  
Old 1/4/09, 1:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: www.FireDoorInspector.org

Cool, now any of the blue state people have a whole new market. The fire door inspections sounds like a good door opener (no pun intended) for other work. Puts you in their place of business every single year attempt the sale of other services.
Reply With Quote
  #30  
Old 1/4/09, 2:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by jbushart View Post
One day in a NACHI Tv studio hardly equates to five years of education.

If people are being told that this one day course qualifies them to inspect firedoors, it is inconsistent with what Marcel has just published.
Read it again James.

Such individuals most likely will have five years of industry experience, and/or equivalent education of the subject



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:30 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts