  #31  
Old 1/4/09, 4:36 PM
Keith Runquist Keith Runquist is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 212
Send a message via AIM to krunquist
Default Re: www.FireDoorInspector.org

Wow, I never thought I'd be happy that South Dakota was a blue state!
Reply With Quote
  #32  
Old 1/5/09, 6:54 PM
Wilfred O. Hellner Wilfred O. Hellner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Longwood, FL
Posts: 105
Send a message via AIM to whellner
Default Re: www.FireDoorInspector.org

I work in a healthcare facility as a Director, and let me tell you, we have our Maintenance staff them on a Quartely basis. Yes it is correct starting this year all Fire Doors have to be inspected on a yearly basis for the AHJ to look at when they come into your building. This is a great oppertunity for all of us to add to our services.



Will Hellner
Reply With Quote
  #33  
Old 1/5/09, 8:26 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: www.FireDoorInspector.org

I wonder if these fire door inspections are going to require the inspector to operate the fire alarm system to confirm that the hold open devices release?
Reply With Quote
  #34  
Old 1/5/09, 8:49 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by Marc D. Shunk View Post
I wonder if these fire door inspections are going to require the inspector to operate the fire alarm system to confirm that the hold open devices release?
I agree Mark, it is all Builders hardware associated with Fire Doors.
I don't think some realize all the Hardware knowledge that is required to confirm that a Fire Door is functioning properly or will perform like it was intended to.
There are hundreds of different type of Fire door Manufacturers and unbelievable descriptions of Builders Hardware that make them all function to meet the NFPA requirements.

I would hope that this course is intended as Continued Education.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #35  
Old 1/5/09, 8:54 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

This link may help some.

http://www.dhi.org/shared/forms/PDFf...AIBrochure.pdf




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #36  
Old 1/5/09, 8:57 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Talk to people already in the bussiness of inspecting Fire Doors. See what the requirements are.

http://www.fdis1.com/




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #37  
Old 1/5/09, 9:05 PM
Wilfred O. Hellner Wilfred O. Hellner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Longwood, FL
Posts: 105
Send a message via AIM to whellner
Default Re: www.FireDoorInspector.org

The answer is NO you do not have to activate the fire alarm system to do these inspections.



Will Hellner
Reply With Quote
  #38  
Old 1/5/09, 9:31 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Section 5.2.6 of the NFPA says different.

http://fm.colorado.edu/firesafety/do...enance2007.pdf




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #39  
Old 1/6/09, 12:24 AM
Chris McDonald Chris McDonald is online now
InterNACHI Member
 
Join Date: Mar 2007
Location: Jaffrey, NH
Posts: 69
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by mcyr View Post
Section 5.2.6 of the NFPA says different.

http://fm.colorado.edu/firesafety/do...enance2007.pdf
Marcel, I respectfully disagree.
Looking at the standards of practice established for fire door inspections:

16.5 Limitations
It is not the purpose of this standard to establish inspection procedures to determine the fire rating or the degree of protection provided by a fire door or surrounding wall, determine the need for a fire door in any particular location, determine proper placement of detectors, determine the functionality of fire detection systems, heat test fusible links, determine the combustibility of floor coverings extending through doorways, inspect accordion, folding, hoistway, elevator, chute, access, or dumbwaiter doors, inspect fire windows, or inspect fabric fire safety curtains.
IMO, activating the fire alarm system to test fire doors goes beyond (most) of our knowledge and expertise. A fire alarm company is most likely testing these devices when they conduct their inspections of the system. Verify it through documentation. If it isn't documented, advise your client that they need to have this done by a qualified fire alarm testing company, or (even if it has previously been done and this is for a commercial real estate transaction) suggest that they have it done by an independent, qualified fire alarm testing company to verify the previous vendors findings. IMO, our role in regards to the functional testing of fire doors is essentially to verify the operation of the fire door(s) once released from the door holding mechanism, resetting the fire door(s) back into the ready state, and documenting the findings.

Just my 2 cents.



Chris McDonald, CMI
Vice President, New Hampshire State Chapter, NACHI
McDonald Home Inspection Services, LLC
Jaffrey, NH 03452
Reply With Quote
  #40  
Old 1/6/09, 7:25 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Quote:
Originally Posted by cmcdonald View Post
Marcel, I respectfully disagree.
Looking at the standards of practice established for fire door inspections:

16.5 Limitations
It is not the purpose of this standard to establish inspection procedures to determine the fire rating or the degree of protection provided by a fire door or surrounding wall, determine the need for a fire door in any particular location, determine proper placement of detectors, determine the functionality of fire detection systems, heat test fusible links, determine the combustibility of floor coverings extending through doorways, inspect accordion, folding, hoistway, elevator, chute, access, or dumbwaiter doors, inspect fire windows, or inspect fabric fire safety curtains.
IMO, activating the fire alarm system to test fire doors goes beyond (most) of our knowledge and expertise. A fire alarm company is most likely testing these devices when they conduct their inspections of the system. Verify it through documentation. If it isn't documented, advise your client that they need to have this done by a qualified fire alarm testing company, or (even if it has previously been done and this is for a commercial real estate transaction) suggest that they have it done by an independent, qualified fire alarm testing company to verify the previous vendors findings. IMO, our role in regards to the functional testing of fire doors is essentially to verify the operation of the fire door(s) once released from the door holding mechanism, resetting the fire door(s) back into the ready state, and documenting the findings.

Just my 2 cents.

Chris you are probably right, the intent of the code is to verify the the hold opens release on activation of the alarm, but that would be covered under the fire alarm testing of the Building as you state.

The key word here would be like you mention, a documentation of those test should become part of the Fire Door Inspections.

Thanks, Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #41  
Old 1/7/09, 12:11 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: www.FireDoorInspector.org

Help me make sense of this... will the fire door inspector inspect the entire door, but not the functionality of the hold open device? Without operating the alarm, how does the inspector confirm that the hold open device releases? Seems like a shame to have a fully inspected fire door that possibly won't shut when called into service. I guess it's like you say, you're going to count on the alarm guys to confirm that.
Reply With Quote
  #42  
Old 1/7/09, 12:30 AM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 509
Default Re: www.FireDoorInspector.org

When is this to go into action...you would think training would have been held last year in time for the inspector need to be there.

What is the referance of State code that will be used?



Need a Link Exchange? Inspector Links


Seattle,WA Commercial Inspectors

Reply With Quote
  #43  
Old 1/7/09, 7:37 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: www.FireDoorInspector.org

Well, mabe we should all look at this picture and start inspections.
This appears to be a classroom setting in a Commercial setting with a pair of doors equipped with panic devices and surface mounted vertical rod devices.
Equal to or similar to P700 series by Sargent.

It would be assummed that since these open up in a corridor in a public building, that these are 1-hour rated doors.
It looks like they have attached hardware on the bottom to manually hold the doors open.

I blew up the picture and there is no floor surface mounted strike, nor recessed floor strike for the bottom chasis of the vertical rod device. Hmmmmmmmm

Wonder why?





Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #44  
Old 1/7/09, 7:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: www.FireDoorInspector.org

I know a lot of the old warehouses have "fire doors" that are more like tin covered barn doors mounted on a sloping horizontal track. You can roll the doors open and shut, since they are counterbalanced by a stack of weights hung from a chain around a couple pullies. In the middle of the chain is a fusible link of some sort of lead alloy. When that link melts, the door comes racing down the track to slam shut. I'd hate to be in the way when that happens. You'd get hurt pretty badly. The tests of those doors are sometimes destructive. I've seen pieces fall off the door, or the door totally blast the stop blocks/hooks off the wall.


Reply With Quote
  #45  
Old 1/7/09, 10:14 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: www.FireDoorInspector.org

We used discount the fire link let close with the counter weight, The magnect device was energized to see if it closed , Panic bars 9 newtons If i remember right Aprox 2 to 3 lbs
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:15 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts