Exclamation Refigeration room problem

I have a client with a commercial refrigeration room. Above the ceiling in the room is an empty space approx 4' high. One wall(cinder block) of this empty space has a boiler room on the other side. The boiler room is very warm at all times. There is condensation building up in the empty space, I suspect because of heat transfer through the concrete block wall. The condensation has been excessive enough to cause the insulated ceiling to get saturated and buckle. My question is:

Which side of the concrete block wall should be insulated? warm side or cold side? Comments please.



Rodney Misener
Trinity Inspection Services

Certified Home Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT Certified Inspector
IAC2 Certified
Infrared Certified
Reply With Quote
Find an InterNACHI certified New Mexico Home Inspector (and anywhere else in North America)
  #2  
Old 8/7/08, 11:43 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,314
Charley L. Bottger .
Default Re: Refigeration room problem

Quote:
Originally Posted by rmisener
I have a client with a commercial refrigeration room. Above the ceiling in the room is an empty space approx 4' high. One wall(cinder block) of this empty space has a boiler room on the other side. The boiler room is very warm at all times. There is condensation building up in the empty space, I suspect because of heat transfer through the concrete block wall. The condensation has been excessive enough to cause the insulated ceiling to get saturated and buckle. My question is:

Which side of the concrete block wall should be insulated? warm side or cold side? Comments please.
Temp always travels from warm to cold If it was mine I would insulate on the warm side prevent the temp from ever transferring into the block.



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #3  
Old 8/8/08, 2:33 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,672
David A. Andersen .
Default Re: Refigeration room problem

Insulation does not stop moisture infiltration.

Heat does not cause condensation.

The ceiling should be insulated.
There should be enough insulation so the exterior does not drop down below the dew point temp.
This will stop condensation.

Air infiltration (which contains the moisture) should be controlled if possible.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Infrared Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Light switch where entering a room. mgault Electrical 19 11/17/07 9:00 AM
Report Writing: Room by Room or System by System by Dr. Keith Swift gromicko Misc. Discussion 0 6/5/06 2:10 PM
Exhaust fan in room with gas water heater and furnace jweinberg HVAC 7 2/18/06 2:23 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 2:53 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics