  #1  
Old 1/28/08, 9:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Is this type of penetration ok (not x rated)

Just wondering if it is ok to have roof penetrations thru the middle of a hatch?

type-penetration-ok-not-x-rated-dscn4373-small-.jpg.JPG
Views:	85
Size:	48.9 KB
ID:	18053type-penetration-ok-not-x-rated-dscn4387-small-.jpg.JPG
Views:	107
Size:	44.4 KB
ID:	18054

Two commercial chillers on a 100 unit residential.
Reply With Quote
  #2  
Old 1/28/08, 11:12 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Is this type of penetration ok (not x rated)

If the hatch is needed for roof acces, then no. If it is abandoned or had been modified for this specific purpose for cause, then it's probably okay.

In a perfect world, no roof penetrations of any type would exist...
Reply With Quote
  #3  
Old 1/28/08, 11:32 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Is this type of penetration ok (not x rated)

Thanks , could not think of anything against it but wanted to make sure.
Reply With Quote
  #4  
Old 1/29/08, 6:43 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Is this type of penetration ok (not x rated)

The chiller lines don't appear to be sealed (at the penetration) and why would they use roll roofing verses EPDM?

This is a leak waiting to happen (unless it doesn't rain out there in Illinois)
Reply With Quote
  #5  
Old 1/29/08, 7:53 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,793
Default Re: Is this type of penetration ok (not x rated)

David, this just looks like another lazy unprofessional mickey mouse way of doing a job right.

It is a patch job, they do not know of a pipe boot for pipe penetrations and obvciously the wrong type of insulation for the exposure.

Marcel
Reply With Quote
  #6  
Old 1/29/08, 8:41 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Is this type of penetration ok (not x rated)

The question was whether installing it through a roof hatch was okay. it is, even though this particular installaton may suck.
Reply With Quote
  #7  
Old 1/29/08, 9:32 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,793
Default Re: Is this type of penetration ok (not x rated)

In a perfect World, there would be nothing at all on the roof.

Unfortunately, there is and there are procedures on how to do it so they don't leak, this one will whether or not it is ok to go through an abandoned hatch.

Question is, Does this installation meet the Installation standards of the roof Manufacturer Warranty if there is one? The answer would be no.

And if there is no ongoing Warranty in affect, Well, you won't get one either.

Marcel

Reply With Quote
  #8  
Old 1/29/08, 10:30 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Is this type of penetration ok (not x rated)

Marcel who's warranty.
Roofers?
Reply With Quote
  #9  
Old 1/29/08, 11:40 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,793
Default Re: Is this type of penetration ok (not x rated)

Bob, roof warranties are usually assessed to a flat roof by the Manufacturer of whatever type of membrane is used or system.

Around here, if it is a membrane roof or a five ply built up roof the warranties by the Manufacturer will be between 20 and 25 years.

Most buildings will have the roofs redone a few years before the warranty runs out. Or the owner of the roof will push it to complete failure and beyond repair.

I always check and see if there is an ongoing warranty on a flat roof that will continue with a new owner or if it is disclosed.
In this case of your pictures, I do not know as to how it would relate to the overall condition of the roof.
If the remeinder of the roof system looks like that, then it would be easy to not woory about something that is makeshift.

Doing such work and patch on a warrantied roof would void it immediately and if no warranty exists, then if this work were executed by a roofing contractor none would be provided by that installer if the client at the time insisted to have it done and repaired in an unorthodox manner as such.
This is a makeshift roof penetration and is not acceptable for any roof systems that I have encountered.
To say that this is OK, I do not agree and would reccomend an eval by a Roofing Company with possible repairs required.

I am sorry, but I would call this out. CYA

Marcel

Reply With Quote
  #10  
Old 1/29/08, 12:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Is this type of penetration ok (not x rated)

Hi Marcel
They supposidly had the roof redone for years ago, but the rehab (condo) was done 8 years ago.
I guess that tells you something.
The coping was cement and parapet flashing was substandard.
Thanks for the help.
Reply With Quote
  #11  
Old 1/29/08, 7:40 PM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: Is this type of penetration ok (not x rated)

the penetrations look ok, I guess but the insulation on the lines is completely poor. not water proof or sun proof. needs either metal jacketing or vinal jacketing. water leaks into asj insulation, freezing then well uget it...
Reply With Quote
  #12  
Old 1/29/08, 7:57 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Is this type of penetration ok (not x rated)

They appear in good shape if put on in 1999 as the plate said.
Did not include that pic.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
Fire rating abolt Structural Inspections 13 9/21/07 8:45 PM
Roof type & excessive leaking dmacy Exterior Inspections 7 9/12/06 12:07 PM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM