Default Bonding issue (posted by Bill Sims)

[ASKNACHI]This question was posted on [I]AskNACHI.org[/I] by [B]Bill Sims[/B] (from Valley, Al). [/ASKNACHI] House has a utility meter with ground rod common to neutral. 3 wire service ran to main disconnect panel on other side of house. A separate EG ground rod with #4 Bare running from rod to EG Bar. Neutral is not bonded.
Should neutral and EG be bonded in this panel since there are 2 separate ground rods.
Reply With Quote
  #2  
Old 7/31/08, 12:29 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Bonding issue (posted by Bill Sims)

Yes,

The neutral and ground should be bonded in the panel that has the first point of disconnect.

The ground rod at the meter is all that is needed. The other one is installed incorrectly.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 7/31/08, 10:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding issue (posted by Bill Sims)

You know....I have been doing this MANY years and I totally can't understand what was just asked...lol.....and I do this for a living.

If the meter has a Grounding Electrode Conductor coming out of it to the ground rods...then that portion of the grounding electrode system is complete. Now, what is confusing is you said a main disconnect was all the way on the other side of the house........

So is their a disconnect at the meter or did they just run the service cable all the way around the house( hopefully not under to through the house in violation of 230.70(A)(1)....)

Anyway.....Yes you bond the grounded and grounding at the main service disconnect...At a remote distribution panel you do not...the grounded conductor is insulated from the enclosure.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 7/31/08, 11:06 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,929
Default Re: Bonding issue (posted by Bill Sims)

[quote=pabernathy]You know....I have been doing this MANY years and I totally can't understand what was just asked...lol.....and I do this for a living.

If the meter has a Grounding Electrode Conductor coming out of it to the ground rods...then that portion of the grounding electrode system is complete. Now, what is confusing is you said a main disconnect was all the way on the other side of the house........

So is their a disconnect at the meter or did they just run the service cable all the way around the house( hopefully not under to through the house in violation of 230.70(A)(1)....)

Anyway.....Yes you bond the grounded and grounding at the main service disconnect...At a remote distribution panel you do not...the grounded conductor is insulated from the enclosure.[/quote]Well Paul for not understanding it, you explained it pretty well. ;-) I think.....lol



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January
Reply With Quote
  #5  
Old 7/31/08, 11:12 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bonding issue (posted by Bill Sims)

He simply said that the other panel is a sub-panel. (old terminology)

I think the question related to at what point is it not a sub-panel.

I know that a garage or seperate structure gets it's own ground, but at what point is it ever needed in the same structure?
Reply With Quote
  #6  
Old 8/1/08, 10:59 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Bonding issue (posted by Bill Sims)

[quote=relliott]He simply said that the other panel is a sub-panel. (old terminology)
[/quote]

Sorry......I did not get the SIMPLY part of the format of the question...but then again what do I know...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools



All times are GMT -4. The time now is 3:30 PM.

no new posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274