rpeterson rpeterson is offline
InterNACHI Member
 
Join Date: Nov 2003
Posts: 3
Default carbon monoxide detectors

A real estate friend of mine had an inspection with an FHA inspector and he indicated that per federal law the CO detector had to be mounted on the ceiling or with in 12" of the ceiling in the master bedroom and not in the hall or with in 15' of the bedrooms. Does anyone have any info on this?

Thanks,
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/31/11, 8:01 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: carbon monoxide detectors

According to the 2005 edition of the carbon monoxide guidelines, NFPA 720, published by the National Fire Protection Association, sections 5.1.1.1 and 5.1.1.2, all CO detectors 'shall be centrally located outside of each separate sleeping area in the immediate vicinity of the bedrooms,' and each detector 'shall be located on the wall, ceiling or other location as specified in the installation instructions that accompany the unit.'



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 3/31/11, 8:01 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: carbon monoxide detectors

[QUOTE=rpeterson;766929]A real estate friend of mine had an inspection with an FHA inspector and he indicated that per federal law the CO detector had to be mounted on the ceiling or with in 12" of the ceiling in the master bedroom and not in the hall or with in 15' of the bedrooms. Does anyone have any info on this?

Thanks,[/QUOTE]
Not true as we require 15 feet in Illinois.
Reply With Quote
  #4  
Old 3/31/11, 9:52 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: carbon monoxide detectors

And in Minnesota: "...required within 10 ft of all rooms intended for sleeping". So, depending on the floorplan, a 4 bedroom home would need anywhere from 1 to 4 detectors.
Reply With Quote
  #5  
Old 4/1/11, 10:20 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: carbon monoxide detectors

The question was about Federal Law requirements, and I believe Michael answered it.
Reply With Quote
  #6  
Old 4/1/11, 10:53 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: carbon monoxide detectors

Carbon Monoxide Detector Placement

PLACEMENT OF CARBON MONOXIDE DETECTORS IMPORTANT



Proper placement of a carbon monoxide detector is important. If you are installing only one carbon monoxide detector, the Consumer Product Safety Commission (CPSC) recommends it be located near the sleeping area, where it can wake you if you are asleep. Additional detectors on every level and in every bedroom of a home provides extra protection.



Homeowners should remember not to install carbon monoxide detectors directly above or beside fuel-burning appliances, as appliances may emit a small amount of carbon monoxide upon start-up. A detector should not be placed within fifteen feet of heating or cooking appliances or in or near very humid areas such as bathrooms.



When considering where to place a carbon monoxide detector, keep in mind that although carbon monoxide is roughly the same weight as air (carbon monoxide's specific gravity is 0.9657, as stated by the EPA; the National Resource Council lists the specific gravity of air as one), it may be contained in warm air coming from combustion appliances such as home heating equipment. If this is the case, carbon monoxide will rise with the warmer air.
Reply With Quote
  #7  
Old 4/1/11, 11:22 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,630
Default Re: carbon monoxide detectors

Local code always supersedes HUD/FHA reporting requirements.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 4/1/11, 11:34 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: carbon monoxide detectors

[QUOTE=ccurrins;767652]Local code always supersedes HUD/FHA reporting requirements.[/QUOTE]
Plus there is no National code.
As Mike knows because ws just got a code this year.

I actually have one from NFPA that states outside sleeping rooms but in bedrooms to make it more confusing.

Can't find original with good resolution to read the text but here is a diagram from the 2007 copy I had that matches from Wikipedia.

Did they change the attachments and advanced editing here or something?
Attached Thumbnails
carbon-monoxide-detectors-smokedetectors.jpg   carbon-monoxide-detectors-2011-04-01_222515.jpg  
Reply With Quote
  #9  
Old 4/1/11, 11:43 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,630
Default Re: carbon monoxide detectors

[QUOTE=belliott;767657]Plus there is no National code.
As Mike knows because ws just got a code this year.

I actually have one from NFPA that states outside sleeping rooms but in bedrooms to make it more confusing.

Can't find original with good resolution to read the text but here is a diagram from the 2007 copy I had that matches from Wikipedia.

Did they change the attachments and advanced editing here or something?[/QUOTE]

Those illustrations or for smokes Bob. The question was CO detectors, but you new that.

You're right there is no national code or federal law.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 4/1/11, 11:46 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: carbon monoxide detectors

[QUOTE=ccurrins;767660]Those illustrations or for smokes Bob. The question was CO detectors, but you new that.

You're right there is no national code or federal law.[/QUOTE]

Actually the more clear one was for C/O in wikipedia however I would assume people use combo units more than ever and as we know C/o detectors only last 5 years while smoke on average last 8 years so I go with the smallest common denominator.:)
Reply With Quote
  #11  
Old 4/1/11, 11:50 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,630
Default Re: carbon monoxide detectors

Here is Illinois Law. Note as determined by the local building commissioner


Effective January 1, 2007, every Illinois home is required to have at least one carbon monoxide alarm in an operating condition within 15 feet of every room used for sleeping purposes. Homes that do not rely on the burning of fuel for heat, ventilation or hot water; are not connected to a garage; and are not near a source of carbon monoxide (as determined by the local building commissioner) are not required to install carbon monoxide detectors



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 4/1/11, 11:58 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: carbon monoxide detectors

[QUOTE=ccurrins;767662]Here is Illinois Law. Note as determined by the local building commissioner


Effective January 1, 2007, every Illinois home is required to have at least one carbon monoxide alarm in an operating condition within 15 feet of every room used for sleeping purposes. Homes that do not rely on the burning of fuel for heat, ventilation or hot water; are not connected to a garage; and are not near a source of carbon monoxide (as determined by the local building commissioner) are not required to install carbon monoxide detectors[/QUOTE]

In other words high rises with a boiler in the basement do not need them C/o
I always recommend placement in bedrooms to avoid waking up dead....:)
Reply With Quote
  #13  
Old 4/2/11, 2:51 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: carbon monoxide detectors

Bob, if it's in the bedroom, and the air is cool, you possibly would not hear the alarm go off.
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/3/11, 12:16 PM
rpeterson rpeterson is offline
InterNACHI Member
 
Join Date: Nov 2003
Posts: 3
Default Re: carbon monoxide detectors

thanks for all your help
Reply With Quote
Reply

Thread Tools



All times are GMT -4. The time now is 5:46 PM.

no new posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282