[ASKNACHI]This question was posted on [I]AskNACHI.org[/I] by [B]Steve[/B] (from Sparks, NV). [/ASKNACHI]what gauge electrical wire do you need for a 100 amp breaker
|
|
#2
|
|||
|
|||
|
[quote=AskNACHI.org][asknachi]This question was posted on [I]AskNACHI.org[/I] by [B]Steve[/B] (from Sparks, NV). [/asknachi]what gauge electrical wire do you need for a 100 amp breaker[/quote]
Typically, #4 CU or #2 AL. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#3
|
||||
|
||||
|
Please Note:
cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
[quote=lkage]Typically, #4 CU or #2 AL.[/quote]
agreed |
|
#4
|
||||
|
||||
|
Becareful.......you can't apply 310.15(B)(6) if it is a feeder to a subpanel
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 9/17/07 at 12:23 PM.. |