#1
|
|||
|
|||
|
Are all the outlets in the kitchen supposed to be gfci?
|
| Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Depends on the year of the structure and the area that the structure is located in.
House 2 Home LLC 503-602-1420 HomePros@House2HomeLLC.ORG Protecting Peace of Mind One House at a Time IAC2 Certified IR Certified A favorite place on Google Maps |
|
#3
|
|||
|
|||
|
i believe it is 6 feet from the sink and any outlets that are over the counter.
|
|
#4
|
||||
|
||||
|
Russell,
No, not all receptacles in a kitchen are required to be GFCI protected. Only the ones serving the countertop requirments. Now 6' ( as far as dwellings go ) only came into play with regards to wet bar, utility and laundry sinks. However, in the 2008 NEC in OTHER than dwellings saw the requirement of GFCI protection on ALL sinks within 6' come into play which was a major change for the NEC. Now if you are speaking of a Kitchen OTHER THAN A DWELLING then all 15 and 20A 125V receptacles outlets would require GFCI protection within the kitchen space and that would include all.....not just any countertop devices. Remember however that we are talking about an OTHER than dwelling environment. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |