Default mitigation system in pennsylvania

My question is about my neighbor's radon mitigation system that is on the outside of his house. I don't want to question my neighbor before I know if I've got a legitimate concern.

Our houses are about 15 ft apart and aside from the white pipe you wouldn't know it was there. However he recently added a back room and now it sounds sort of like a pool filter or one of those electric neon signs. The pipe was above the old roof line but the new roof is maybe 3-4 inches above it now. I wanted to know if, since I think its the air flow that is now altered, could the gases also be not flowing as freely in the air but settling between the houses. Our door, 2 bedroom windows and back porch are all on this side.
Reply With Quote
Find an InterNACHI certified South Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 6/10/09, 12:41 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: mitigation system in pennsylvania

Radon mitigation systems are installed on townhomes too, which are closer together than your house and his. I would be more concerned about whether you have radon in your home than I would be about his system venting fifteen feet from your house.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 6/10/09, 12:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: mitigation system in pennsylvania

Consider a muffler.

Mufflers currently offered for sale.

RadonSupplies has a 1 inch fiberglass lined muffler inside a 6 inch PVC S&D pipe. This muffler provided the least airflow resistance and the greatest DB reduction.

RadonAway offers a 4" PVC pipe lined with 1/2" foam. This muffler has the second greatest flow restriction but provides second best noise reduction.

The RCI baffled muffler is a 5" PVC pipe lined with 1/4" foam. This muffler had the greatest flow restriction and the same noise reduction as the straight through RCI muffler



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #4  
Old 6/12/09, 10:32 AM
Unregistered
Guest
 
Posts: n/a
Please Note: is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: mitigation system in pennsylvania

I didn't even think about it in my own house. I'll have to pull my paperwork to see if we had that done when we bought the house 7 years ago. If it wasn't tested then, can I still do a short-term test during the summer? I read that all windows and outside doors must be closed at least 12 hours before and during testing. We have no air conditioning so our windows and doors are always open.
Reply With Quote
Reply

Thread Tools



All times are GMT -4. The time now is 4:06 AM.

no new posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146