Deck joists that cantilever out past the deck posts, should never overhang the girder they rests on by more than what?
|
| Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
[QUOTE=Unregistered;509179]Deck joists that cantilever out past the deck posts, should never overhang the girder they rests on by more than what?[/QUOTE]
Typically, it is L/4 not exceeding 3'. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
Last edited by lkage; 4/18/09 at 8:19 AM.. |
|
#3
|
|||
|
|||
|
1/3 The joist length. So a 12' joist can cantilever 4'. 6' joist 2' etc.. But check with your local building dept.