AskNACHI.org » Pipe instead of ground rod
Old 7/2/09, 7:01 AM
Charles Martz
Guest
Posts: n/a
Default Pipe instead of ground rod
Can a 1/2 inh plumbing pipe or rebar be used near the seashore instead of a ground rod and what purpose does it serve?
Find an InterNACHI certified Maine Home Inspector (and anywhere else in North America)
Old 7/3/09, 12:29 AM
Joe Funderburk, CMI's Avatar
Default Re: Pipe instead of ground rod
GROUNDING ELECTRODE. A device that establishes an
electrical connection to earth.
E3508.1.4 Rod and pipe electrodes. Rod and pipe electrodes
not less than 8 feet (2438 mm) in length and consisting
of the following materials shall be considered as a
grounding electrode:
1. Electrodes of pipe or conduit shall not be smaller than
trade size 3/4 (metric designator 21) and, where of iron
or steel, shall have the outer surface galvanized or
otherwise metal-coated for corrosion protection.
2. Electrodes of rods of iron or steel shall be at least 5/8
inch (15.9 mm) in diameter. Stainless steel rods less
than 5/8 inch (15.9 mm) in diameter, nonferrous rods
or their equivalent shall be listed and shall be not less
than 1/2 inch (12.7 mm) in diameter.
E3508.1.4.1 Installation. The rod and pipe electrodes
shall be installed such that at least 8 feet (2438 mm) of
length is in contact with the soil. They shall be driven to a
depth of not less than 8 feet (2438 mm) except that,
where rock bottom is encountered, electrodes shall be
driven at an oblique angle not to exceed 45 degrees from
the vertical or shall be buried in a trench that is at least 30
inches (762 mm) deep. The upper end of the electrodes
shall be flush with or below ground level except where
the aboveground end and the grounding electrode conductor
attachment are protected against physical damage.
Theodore Roosevelt
Joe Funderburk, CMI
NACHI ID: NACHI05120170
www.aohomeinspection.com
Old 7/3/09, 2:33 AM
James E. Braun, CMI's Avatar
You could have just said NO, Joe. LOL
Old 7/4/09, 12:33 PM
Unregistered
Guest
Posts: n/a
Thank you for the information, the last message was really not necessary! If a question is asked just be kind enough to answer it or shut up and mind your business CMI Dude!
Old 7/6/09, 2:41 PM
Unregistered......he was saying in in fun....he was not snapping on him. Hey Joe...better watch it as You Know Who will say you Cut and Pasted that....lol.....and in the spirit of Cut and Paste..I will do the same....
(5) Rod and Pipe Electrodes. Rod and pipe electrodes
shall not be less than 2.44 m (8 ft) in length and shall
consist of the following materials.
(a) Grounding electrodes of pipe or conduit shall not
be smaller than metric designator 21 (trade size 3⁄4) and,
where of steel, shall have the outer surface galvanized or
(b) Grounding electrodes of stainless steel and copper
or zinc coated steel shall be at least 15.87 mm (5⁄8 in.) in
diameter, unless listed and not less than 12.70 mm (1⁄2 in.)
in diameter.
Paul W. Abernathy
1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282