When are smoke detection devices required in a bedrom of an apartment dwelling unit?
Are they supposed to be supplied by a separate circuit breaker or fused or are batteries OK? |
| Find an InterNACHI certified Wisconsin Home Inspector (and anywhere else in North America) |
[QUOTE=Alan J. Cohen;532258]When are smoke detection devices required in a bedrom of an apartment dwelling unit?
Are they supposed to be supplied by a separate circuit breaker or fused or are batteries OK?[/QUOTE] Here's the information that you need. ICC, INTERNATIONAL RESIDENTIAL CODE. SMOKE ALARMS PART III, BUILDING PLANNING AND CONSTRUCTION. SECTION R313 SMOKE ALARMS R313.1 Smoke detection and notification. All smoke alarms shall be listed in accordance with UL 217 and installed in accordance with the provisions of this code and the household fire warning equipment provisions of NFPA 72. Household fire alarm systems installed in accordance with NFPA 72 that include smoke alarms, or a combination of smoke detector and audible notification device installed as required by this section for smoke alarms, shall be permitted. The household fire alarm system shall provide the same level of smoke detection and alarm as required by this section for smoke alarms in the event the fire alarm panel is removed or the system is not connected to a central station. R313.2 Location. Smoke alarms shall be installed in the following locations: 1. In each sleeping room. 2. Outside each separate sleeping area in the immediate vicinity of the bedrooms. 3. On each additional story of the dwelling, including basements but not including crawl spaces and uninhabitable attics. In dwellings or dwelling units with split levels and without an intervening door between the adjacent levels, a smoke alarm installed on the upper level shall suffice for the adjacent lower level provided that the lower level is less than one full story below the upper level. When more than one smoke alarm is required to be installed within an individual dwelling unit the alarm devices shall be interconnected in such a manner that the actuation of one alarm will activate all of the alarms in the individual unit. R313.2.1 Alterations, repairs and additions. When alterations, repairs or additions requiring a permit occur, or when one or more sleeping rooms are added or created in existing dwellings, the individual dwelling unit shall be equipped with smoke alarms located as required for new dwellings; the smoke alarms shall be interconnected and hard wired. Exceptions: 1. Inter connection and hard-wiring of smoke alarms in existing areas shall not be required where the alterations or repairs do not result in the removal of interior wall or ceiling finishes exposing the structure, unless there is an attic, crawl space or basement available which could provide access for hard wiring and interconnection without the removal of interior finishes. 2. Work involving the exterior surfaces of dwellings, such as the replacement of roofing or siding, or the addition or replacement of windows or doors, or the addition of a porch or deck, are exempt from the requirements of this section. R313.3 Power source. In new construction, the required smoke alarms shall receive their primary power from the building wiring when such wiring is served from a commercial source, and when primary power is interrupted, shall receive power from a battery. Wiring shall be permanent and without a disconnecting switch other than those required for overcurrent protection. Smoke alarms shall be permitted to be battery operated when installed in buildings without commercial power or in buildings that undergo alterations, repairs or additions regulated by Section R313.2.1. AM104.3 Location. A detector shall be located in each bedroom and any room that is to be used as a sleeping room and centrally located in the corridor, hallway or area giving access to each separate sleeping area. When the dwelling unit has more than one story, and in dwellings with basements, a detector shall be installed on each story and in the basement. In dwelling units where a story or basement is split into two or more levels, the smoke detector shall be installed on the upper level, except that when the lower level contains a sleeping area, a detector shall be installed on each level. When sleeping rooms are on the upper level, the detector shall be placed at the ceiling of the upper level in close proximity to the stairway. In dwelling units where the ceiling height of a room open to the hallway serving the bedrooms or sleeping areas exceeds that of the hallway by 24 inches (610 mm) or more, smoke detectors shall be installed in the hallway and in the adjacent room. Detectors shall sound an alarm audible in all sleeping areas of the dwelling unit in which they are located. Signed, Frank Carrio, CMI Certified Master Inspector & Consultant Certified Commercial Building Inspector Certified, WDI Inspector Founder & Current President, New Hampshire State Chapter NACHI NACHI, State Representative for Legislative Affairs Retired: ICC Certified Member Retired: Code Compliance Inspector. Retired: ASTM Committee Member New Hampshire License #0096 |
Are they supposed to be supplied by a separate circuit breaker or fused or are batteries OK?[/QUOTE] I would check local codes. |
I agree with Robert, check with your local codes. Most of my area has no requirement.
Check with your local codes. Just for safety, install one in each bedroom.
Gary Oleski Home Inspections Home Inspections Connecticut Connecticut . 06610 NACHI04012833 CT#HOI.341 C M I
[QUOTE=goleski;532633]Check with your local codes. Just for safety, install one in each bedroom.[/QUOTE]
Massachusetts codes have the strictest codes out there. Smoke and Carbon monoxide detectors are required...one per level and within 10 feet of each bedroom. Also, if there is a direct vent in the basement, they require them in the area of the direct vent as well. |
