Default Wire Nuts in the Main Panel

I have a main panel with a wire nut connecting the wire from the breaker to two wires going up the conduit into the house. (how do I post a pic here?) I've been told that it's not code but it is done. Does it need to be fixed immediately.
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/1/10, 12:59 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Wire Nuts in the Main Panel

It sound like a pigtail which would be fine and would not need to be fixed.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 2/1/10, 1:06 PM
Owen Brennan
Guest
 
Posts: n/a
Please Note: is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire Nuts in the Main Panel

Thank you!
Reply With Quote
  #4  
Old 2/1/10, 3:13 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,041
Default Re: Wire Nuts in the Main Panel

[QUOTE=lkage;615780]It sound like a pigtail which would be fine and would not need to be fixed.[/QUOTE]


As long as it was installed correctly.
Reply With Quote
  #5  
Old 2/1/10, 10:47 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Wire Nuts in the Main Panel

Yes, of course...

Where is that picture?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 2/1/10, 11:21 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,041
Default Re: Wire Nuts in the Main Panel

[QUOTE=lkage;616122]Yes, of course...

Where is that picture?[/QUOTE]

I don't think this thread allows pic's
Reply With Quote
  #7  
Old 2/2/10, 9:19 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Wire Nuts in the Main Panel

Yes, of course. (It doesn't allow emoticons either) ...grin...razz



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 2/2/10, 9:31 PM
James A. Levy's Avatar
James A. Levy James A. Levy is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,673
Default Re: Wire Nuts in the Main Panel

If it is what it sounds like, I think it is the equivalent of a double tap. It sounds like one pigtail wire is feeding two home runs. If that is the case, then that would need to be separated. If there is no room left in the panel, then a tandem breaker may be in order. If it is a three wire home run then a two pole breaker is necessary.

Can you get this up in the general discussion thread so we can see a pic? :)
Reply With Quote
  #9  
Old 2/2/10, 10:35 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Wire Nuts in the Main Panel

Jim,

It does not sound like a double-tap at all, and does not need separation.

For clarification, so long as there is room in the panel, splices are permitted. In fact, the NEC does not even require that spliced cabled be terminated in the main panel at all. Yep. The panel can actually serve as a pass-through.

There is a lot of mis-information out there regarding what is permissable and what is not.
Reply With Quote
  #10  
Old 2/2/10, 11:21 PM
James A. Levy's Avatar
James A. Levy James A. Levy is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,673
Default Re: Wire Nuts in the Main Panel

I do realize that the panel box may be used as a splice box. I thought the original post stated that two wires exiting the panel box were being fed from a single pigtail to a breaker. IF THAT is the case, it sounded like the equivalent of a double tap. That is why it would be nice to see a pic.

If that is the scenario, what would be the difference between a pigtail servicing two home runs and the home runs being terminated directly at the breaker? I don't think the pig tail would be long enough to need to be derated, but that would be another set of problems.
Reply With Quote
  #11  
Old 2/2/10, 11:25 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Wire Nuts in the Main Panel

James,

If the breaker terminal is not rated for two wires it is not permitted.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #12  
Old 2/2/10, 11:53 PM
James A. Levy's Avatar
James A. Levy James A. Levy is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,673
Default Re: Wire Nuts in the Main Panel

I found the answer here http://www.justanswer.com/questions/1c9tv-is-double-tapping-a-circuit-breaker-acceptable-and-if-so

Is double tapping a circuit breaker
acceptable and if so where is it covered in NFPA 70

Accepted Answer
What you will find in the code is that it will state NO - unless the breaker is listed and approved for the purpose. In addition - if you look at the breaker and it states for use with 2 wires - then that breaker can be used for that.

Now the only breakers that I am aware of that can be used in such a way is the square d qo and qod breakers.

There is a way around the requirement of 1 wire per terminal if the breaker is not rated for more then 1 wire. We will take a 6" tale off of the breaker, and then wire nut other wires to it as needed. This way you meet the requirement of the 1 wire per terminal, and splicing in the panel is perfectly acceptable. So your covered on both ends.
Reply With Quote
  #13  
Old 2/2/10, 11:53 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,041
Default Re: Wire Nuts in the Main Panel

Test
Attached Thumbnails
wire-nuts-main-panel-elect-shock.jpg  
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/2/10, 11:55 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,041
Default Re: Wire Nuts in the Main Panel

Owen,

If you have a digital photo, feel free to email me and I will post it for you.

Jeff

jrjonas@jrjconsultants.net
Reply With Quote
  #15  
Old 2/3/10, 4:23 AM
Unregistered
Guest
 
Posts: n/a
Please Note: is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Wire Nuts in the Main Panel

I am a member here but I couldn't sign in here for some reason.
I will post this on the message board. It's one wire coming from the breaker into two wires with all three tied together with a wire nut.
Reply With Quote
Reply

Thread Tools



All times are GMT -4. The time now is 10:19 AM.

no new posts

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274