Hi All,
Are drip legs required on all gas appliances in California?
Thanks, Tom
Reply With Quote
Need a home inspection in Virginia? Check out InterNACHI's listing of Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/22/10, 7:31 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Drip legs

I seem to recall they are not required in state code there but are required by the IRC.
Still good practice to recommend them and you also should check manufacturers instructions.

Last edited by belliott; 7/22/10 at 7:35 PM..
Reply With Quote
  #3  
Old 7/22/10, 8:08 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip legs

I call them out if they are missing from gas water heaters and gas furnaces. I say nothing about gas ranges and/or gas dryers. As Bob said you should also check manufacturers requirements.

Chuck
Reply With Quote
  #4  
Old 7/22/10, 9:15 PM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Drip legs

I rarely if ever see them down here in San Diego.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #5  
Old 7/22/10, 9:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Drip legs

Any guys in Illinois reading this be sure to call out missing drip legs.
The gas company wants them on before the shutoff.
Reply With Quote
  #6  
Old 7/22/10, 11:24 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip legs

Quote:
Originally Posted by dredding View Post
I rarely if ever see them down here in San Diego.
And do you say anything about them not being in place?

Chuck
Reply With Quote
  #7  
Old 7/24/10, 7:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Drip legs

I never reported the absence of drip-legs until Chuck enlightened me (thanks Chuck). I have since acquired a database (of sorts) of installation instructions for many different appliances and manufacturers.

There are some manufacturers that "require" drip legs, others that "suggest" or "recommend" drip legs and other that make no mention of them at all.

Since CA and most CA utility companies don't require them, I only call them out on the appliances where I know they are required by the manufacturer.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 7/24/10, 8:54 PM
Nolan Kienitz Nolan Kienitz is offline
New User
 
Join Date: Jan 2007
Location: Dallas Home Inspections
Posts: 40
Please Note: Nolan Kienitz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip legs

Just a head's up and sharing only because I've been jumped on by folks smarter than me.

Review codes, definitions, etc. of: drip legs, dirt legs, sediment traps.

They are often used/interchanged all over the place and different parts of the country have their own familiarity.

Drip legs - Typically used when dealing with 'wet' gas and in code books they are used at/near/before the gas meter to a property.

Dirt legs - Used at appliance cutoff valve in front of manifold of same. More often a regional/local term.

Sediment trap - The actual correct term for the device (also known as a Dirt Leg) installed before the manifold at an appliance.

Like JP noted I review for manufacturer's requirements. IRC has required them for years and years and years ... in the D/FW market the local AHJs seldom enforce installation of same, yet they don't 'exclude' them on their municipal documents.

IRC requires them at: Furnaces and Water Heaters.

Sediment Traps - From IRC:
IRC - International Residential Code: G2419.4 (408.4) Sediment trap. Where a sediment trap is not incorporated as part of the gas utilization equipment, a sediment trap shall be installed downstream of the equipment shutoff valve as close to the inlet of the equipment as practical. The sediment trap shall be either a tee fitting with a capped nipple in the bottom opening of the run of the tee or other device approved as an effective sediment trap. Illuminating appliances, ranges, clothes dryers and outdoor grills need not be so equipped.


Drip Legs - From IRC:
G2419.2 (408.2) Drips. Where wet gas exists, a drip shall be provided at any point in the line of pipe where condensate could collect. A drip shall also be provided at the outlet of the meter and shall be installed so as to constitute a trap wherein an accumulation of condensate will shut off the flow of gas before the condensate will run back into the meter.
Drips, often referred to as “drip legs,” are distinct from sediment traps. Modern gas supplies and distribution systems are typically dry; thus, drips would be required only when recommended by the gas supplier.
G2419.3 (408.3) Location of drips. Drips shall be provided with ready access to permit cleaning or emptying. A drip shall not be located where the condensate is subject to freezing.
A drip is not the same as a sediment trap; they are required for different reasons (see Section G2419.4).



What also makes my being "so picky" frustrating is that many manufacturers also label some of their drawings of the trap being installed adjacent to the water heater/furnace, etc.. and they then 'mis-label' it as a "drip leg".

Sometimes you just can't win ... and in the overall scheme of things it is a very small item. Not something to fall on a sword over.

Likely more than anyone wants to know.

And then there are the rules that govern CA. I can't even begin to address those details.




Cheers,

Nolan Kienitz
www.NolansInspections.com
D/FW

Last edited by Nolan Kienitz; 7/24/10 at 9:00 PM..
Reply With Quote
  #9  
Old 7/26/10, 1:30 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Drip legs

Quote:
Originally Posted by Nolan Kienitz View Post
Just a head's up and sharing only because I've been jumped on by folks smarter than me.

Review codes, definitions, etc. of: drip legs, dirt legs, sediment traps.

They are often used/interchanged all over the place and different parts of the country have their own familiarity.

Drip legs - Typically used when dealing with 'wet' gas and in code books they are used at/near/before the gas meter to a property.

Dirt legs - Used at appliance cutoff valve in front of manifold of same. More often a regional/local term.

Sediment trap - The actual correct term for the device (also known as a Dirt Leg) installed before the manifold at an appliance.

Like JP noted I review for manufacturer's requirements. IRC has required them for years and years and years ... in the D/FW market the local AHJs seldom enforce installation of same, yet they don't 'exclude' them on their municipal documents.

IRC requires them at: Furnaces and Water Heaters.

Sediment Traps - From IRC:
IRC - International Residential Code: G2419.4 (408.4) Sediment trap. Where a sediment trap is not incorporated as part of the gas utilization equipment, a sediment trap shall be installed downstream of the equipment shutoff valve as close to the inlet of the equipment as practical. The sediment trap shall be either a tee fitting with a capped nipple in the bottom opening of the run of the tee or other device approved as an effective sediment trap. Illuminating appliances, ranges, clothes dryers and outdoor grills need not be so equipped.


Drip Legs - From IRC:
G2419.2 (408.2) Drips. Where wet gas exists, a drip shall be provided at any point in the line of pipe where condensate could collect. A drip shall also be provided at the outlet of the meter and shall be installed so as to constitute a trap wherein an accumulation of condensate will shut off the flow of gas before the condensate will run back into the meter.
Drips, often referred to as “drip legs,” are distinct from sediment traps. Modern gas supplies and distribution systems are typically dry; thus, drips would be required only when recommended by the gas supplier.
G2419.3 (408.3) Location of drips. Drips shall be provided with ready access to permit cleaning or emptying. A drip shall not be located where the condensate is subject to freezing.
A drip is not the same as a sediment trap; they are required for different reasons (see Section G2419.4).



What also makes my being "so picky" frustrating is that many manufacturers also label some of their drawings of the trap being installed adjacent to the water heater/furnace, etc.. and they then 'mis-label' it as a "drip leg".

Sometimes you just can't win ... and in the overall scheme of things it is a very small item. Not something to fall on a sword over.

Likely more than anyone wants to know.

And then there are the rules that govern CA. I can't even begin to address those details.




Cheers,

Nolan Kienitz
www.NolansInspections.com
D/FW


Have they been required, in general terms as I understand each manuf. is different, for more than 10 years, 15 years, 20 yrs? Had a 16 yr old Bryant furnace and B&W wh this morning that did not have one.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #10  
Old 7/26/10, 1:34 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip legs

Bradford White requires them as a manufacturer.

Chuck
Reply With Quote
  #11  
Old 7/26/10, 1:47 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,918
Default Re: Drip legs

Make things simple on your selves guys.
Just recommend them on all furnace and HWH lines.
Reply With Quote
  #12  
Old 7/26/10, 2:22 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Drip legs

Most HVAC contractors and plumbers here install them. It's the Harry the Homeowner installers that don't install them because they don't come with the flexible gas line installation kit.
Attached Thumbnails
drip-legs-bonk-inspection-030.jpg  

Last edited by ldapkus; 7/26/10 at 2:27 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Drip Legs tlemasters General Inspection Discussion 11 6/3/10 9:15 PM
Drip leg on gas supply line dmonte Plumbing Inspections 5 10/22/09 12:33 AM
Drip legs Scott Schultz Plumbing Inspections 7 3/31/07 7:46 AM
Condensate in the Drip Pan Skip Erwin Inspecting HVAC Systems 4 7/20/06 11:45 AM
Lack of aluminum drip edge Brenda Exterior Inspections 26 6/16/06 7:28 AM


All times are GMT -4. The time now is 6:04 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts