Default Air leaks remediation and house tightness

Out of all the websites I visited which write about air infiltration into houses and the corrective measures to be taken to correct that situation, only 2 ( and I visited over 40) mentioned that making a house too tight can cause new problems.
If I was to find the sources of air leaks into a house I would explain that sealing ALL air leaks could be worse than leaving them in place, but if one really wants to stop all air leaks (or most of them) I would recommend an HRV or ERV be installed.

Any comments would be appreciated.

Gabe
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/31/11, 1:51 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Air leaks remediation and house tightness

Air sealing ceases when additional air sealing is not cost-effective, when the air-leakage-reduction target is reached, or when the minimum ventilation level is reached.

None of this can be determined without a blower door test.

Ideally, a house is completely air tight with all required amounts of fresh air provided through mechanical means where it can be conditioned and filtered. Rarely is this ever achieved.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 1/31/11, 10:29 PM
ggal's Avatar
ggal ggal is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Toronto. Canada
Posts: 31
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by jbushart View Post
.....
None of this can be determined without a blower door test.
......
Hello James
My point was that most of the websites I visited and who use infrared cameras, are talking about finding leaks and lack of insulation or the presence of moisture and the fact that finding the above and correcting them will save the home owner money and make the house more comfortable.
Except for 2 sites, no site mentioned that making a house too tight could make the situation worse.
Also, practically non of the infrared camera users mentioned the use of a blower door test.

Gabe
Reply With Quote
  #4  
Old 1/31/11, 10:34 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by ggal View Post
Hello James
My point was that most of the websites I visited and who use infrared cameras, are talking about finding leaks and lack of insulation or the presence of moisture and the fact that finding the above and correcting them will save the home owner money and make the house more comfortable.
Except for 2 sites, no site mentioned that making a house too tight could make the situation worse.
Also, practically non of the infrared camera users mentioned the use of a blower door test.

Gabe
That is because an infrared camera is insufficient to address what you are referring to as "house tightness". It is like attempting to photograph the wind and use your photo to judge its speed and volume.

Lack of insulation has nothing at all to do with air leakage. Insulating an air bypass simply filters the conditioned air as it leaves the building.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #5  
Old 1/31/11, 10:42 PM
ggal's Avatar
ggal ggal is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Toronto. Canada
Posts: 31
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by jbushart View Post
That is because an infrared camera is insufficient to address what you are referring to as "house tightness". It is like attempting to photograph the wind and use your photo to judge its speed and volume.

Lack of insulation has nothing at all to do with air leakage. Insulating an air bypass simply filters the conditioned air as it leaves the building.
So you are OK with inspectors going into houses with their IR cameras, pointing out air leaks and moisture and suggesting that the air leaks should be eliminated without telling the home owner about the consequences of on overy tight hosuse without make-up air systems?
Reply With Quote
  #6  
Old 1/31/11, 10:47 PM
ggal's Avatar
ggal ggal is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Toronto. Canada
Posts: 31
Default Re: Air leaks remediation and house tightness

"The sealing of air leakage is very cost effective and can pay for itself in the first year from energy savings that the sealing will generate."

This is a quote from an inspector's website.

No mention of the consequences....
Reply With Quote
  #7  
Old 1/31/11, 10:56 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by ggal View Post
"The sealing of air leakage is very cost effective and can pay for itself in the first year from energy savings that the sealing will generate."

This is a quote from an inspector's website.

No mention of the consequences....
There are no "consequences" if you do it right. A blower door test is essential. An infrared camera is an optional tool to use in addition to a blower door.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #8  
Old 1/31/11, 10:58 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by ggal View Post
So you are OK with inspectors going into houses with their IR cameras, pointing out air leaks and moisture and suggesting that the air leaks should be eliminated without telling the home owner about the consequences of on overy tight hosuse without make-up air systems?
No, I am not. Blower door tests are the only means of quantifying air leaks and measuring the effectiveness of sealing them. Not cameras.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #9  
Old 1/31/11, 11:08 PM
ggal's Avatar
ggal ggal is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Toronto. Canada
Posts: 31
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by jbushart View Post
No, I am not. Blower door tests are the only means of quantifying air leaks and measuring the effectiveness of sealing them. Not cameras.
No Offence but if your blower door test tells you that the house could be tighter (based on whatever standard for air changes per hour you use) do you start sealing different areas and you perform a blower door test after every stage to see if you achieved the desired effect?
We don't have an equivalent to BPI in Canada (unfortunately) but we have NRCAN which is somewhat similar but without the teeth .
Also, what do you use to find the actual leak locations when you use a blower test?

Thank you for your replies so far

Gabe
Reply With Quote
  #10  
Old 1/31/11, 11:22 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by ggal View Post
No Offence but if your blower door test tells you that the house could be tighter (based on whatever standard for air changes per hour you use) do you start sealing different areas and you perform a blower door test after every stage to see if you achieved the desired effect?
We don't have an equivalent to BPI in Canada (unfortunately) but we have NRCAN which is somewhat similar but without the teeth .

Maybe you should go with someone who does one and you will understand better.
James already answered your question. Most homes that lack the most modern building methods will be impossible to completely seal up. Even the smallest cracks will allow bypass, so unless you start from scratch you may never see this.

Also, what do you use to find the actual leak locations when you use a blower test?

I found you hands work pretty well, and once again once you do a couple you will understand better..


Gabe
Thank you for your replies so far




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #11  
Old 1/31/11, 11:39 PM
ggal's Avatar
ggal ggal is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Toronto. Canada
Posts: 31
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by sfogarty View Post
Maybe you should go with someone who does one and you will understand better.
That would be great except that people are afraid to share thier knowledge in the immediate area surrounding them probably because they are afraid of losing business.
That is why I post here because hopefully people would not be threatened by someone far away.

Gabe
Reply With Quote
  #12  
Old 2/1/11, 10:17 AM
rspermo rspermo is offline
Active Poster
 
Join Date: Feb 2009
Posts: 155
Please Note: rspermo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Air leaks remediation and house tightness

Gabe,

You are correct! Many home inspectors do not totally understand the actual complexities of house air leakage. Every change to a house must be viewed in relation to what it may do to another part of the house. For example, to foam the rafters of an existing house without looking at the HVAC sizing would be a mistake. James is correct - the only way to actually quantify the home's leakage and air change per hour is to do a blower door.
Reply With Quote
  #13  
Old 2/1/11, 12:07 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by ggal View Post
Hello James
My point was that most of the websites I visited and who use infrared cameras, are talking about finding leaks and lack of insulation or the presence of moisture and the fact that finding the above and correcting them will save the home owner money and make the house more comfortable.
Except for 2 sites, no site mentioned that making a house too tight could make the situation worse.
Also, practically non of the infrared camera users mentioned the use of a blower door test.

Gabe
No house is too tight. Airtightness improves comfort and saves energy. Since 98-99% of the interior house vapour that moves into wall and celing cavities is air leakage, proper airsealing may save prevent a mould/rot situation in areas of air leakage. Once a house is airtightened, it will need supplemental mechanical ventilation, sometimes as simple as a good bath exahust fan on a timer, or possibly a timed whole house exhaust system. Here's a brochure that I worked on and updated in the 1990's:
http://www.conservens.ca/resources/p...lder-Homes.pdf

In the 1980's while running an insulation/airsealing company, we were installing good exhaust systems and instructing our customers on controlling interior moisture problems from basement dampness, not drying clothes inside/venting dryers to exterior, not storing wet firewood inside, covering aquariums, not too many plants, etc
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/1/11, 1:53 PM
ggal's Avatar
ggal ggal is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Toronto. Canada
Posts: 31
Default Re: Air leaks remediation and house tightness

Quote:
Originally Posted by Brian A. MacNeish View Post
Thank you for the brochure Brian.

As for your comment that NO HOUSE IS TOO TIGHT, why else would newer houses need mechanically assited air exchangers (HRVs)?

Too tight is obviously a relative term but let's assume that an older home can be sealed to the level of a new house, wouldn't you agree that if an HRV is not added that house WILL be too tight to the point that it will be uncomfortable.

Gabe
Reply With Quote
  #15  
Old 2/1/11, 3:39 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Air leaks remediation and house tightness

Re: The House as a System
http://www.mitsubishielectric.ca/en/hvac/m-series/specifications.html

Heat Pumps


MSZ-FE12NA
Y
2,800 ~ 12,000
3,000 ~ 21,000

We had an energy audit on our 1400 sq. ft. Home Electric Base board heat .
Fully Finished Basement Gas fire Place .
Sealed and insulated as recomended

On recommendation of audit Person we put in a Mr. slim heat pump.
it heats our home upstairs great ,Electric heat kicks in at about 14°F/-10°C.
I think we save about 70~ % on our heating and the AC is I think 23 seer and it is great .
Easy 3 hour insulation no changes in Basement cost in Canada about $3,300.00 and about $1,400;00 return from the Government .
Attached Thumbnails



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
IAQ pumps eziminsky General Inspection Discussion 16 12/28/10 3:10 PM
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 4:50 PM
Meth House? tallen General Inspection Discussion 27 4/6/09 6:21 PM
Family's house is infested with mold rspriggs Ancillary Inspection Services & Additional Topics 6 1/28/06 2:05 AM


All times are GMT -4. The time now is 7:13 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts