Default Attic shot strange heat??? take a guess

Figure this one out very strange heat source on the electrical wires



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 11:11 PM..
Reply With Quote
  #2  
Old 1/9/08, 6:29 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Attic shot strange heat??? take a guess

Two more neat shots from the side of the road traveling back from this mornings inspection.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 11:11 PM..
Reply With Quote
  #3  
Old 1/9/08, 6:32 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by cbottger
Two more neat shots from the side of the road traveling back from this mornings inspection.
Oil Refinery / FCCU Reactor



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #4  
Old 1/9/08, 6:40 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,709
Default Re: Attic shot strange heat??? take a guess

It's hottest where the wires touch each other.
Reply With Quote
  #5  
Old 1/9/08, 7:09 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,843
Default Re: Attic shot strange heat??? take a guess

Stress points from excessive bending.
Was this aluminum?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #6  
Old 1/9/08, 7:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by jhagarty
Oil Refinery / FCCU Reactor
You got it Bro

Have to travel right through the middle of the refinery I use to work in when going west and I was just curious if I could pick up the vapor trail off of the reactor. I was about 200+ feet from the unit had to do it quick to keep security off my butt.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 1/9/08, 7:36 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by badair
Stress points from excessive bending.
Was this aluminum?
No Aluminum if you look close there is only one run of romax the other twisted looking wire is just an old coat hanger or some such thing no electrical wire. The clue is on the wood Sheathing The pic was taken looking up at the roof deck from within the attic.
</IMG></IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 1/9/08, 7:49 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by badair
Stress points from excessive bending.
Was this aluminum?
Two more clues moisture intrusion on the ceiling below the area of the first two pics this moisture was only visible with the IR Camera. And yes it was moisture did not have to use the moisture meter after what I found in the attic. The hot appearing electrical wires in the IR shot has nothing to do with over current or electrical heat of any nature,



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 11:11 PM..
Reply With Quote
  #9  
Old 1/9/08, 11:37 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic shot strange heat??? take a guess

Are the wires supporting a dryer or heat duct/flue?
Reply With Quote
  #10  
Old 1/10/08, 3:03 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by Brian A. MacNeish
Are the wires supporting a dryer or heat duct/flue?
Very Close I will show you: The furnace flue vent had seperated in the attic due to improper strapping and was blowing across these wires. The roof sheathing was like a rain forest and had been that way for some time. Attic was full of CO Made me dizzy before I could get out and shut the furnace off. The realtor had stated that an elderly single women had passed away in this home Makes me wonder if it was old age or CO. Hot air rises and the attic was ventilated doubt really that CO was the reason of her passing but one just never knows.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging

Last edited by cbottger; 5/13/08 at 11:11 PM..
Reply With Quote
  #11  
Old 1/10/08, 7:18 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by cbottger
Very Close I will show you: The furnace flue vent had seperated in the attic due to improper strapping and was blowing across these wires. The roof sheathing was like a rain forest and had been that way for some time. Attic was full of CO Made me dizzy before I could get out and shut the furnace off. The realtor had stated that an elderly single women had passed away in this home Makes me wonder if it was old age or CO. Hot air rises and the attic was ventilated doubt really that CO was the reason of her passing but one just never knows.
A few days before a Xmas in the late 1980's (Saint John, New Brunswick), there was a case of an elder lady dying from CO due to a separated flue from her oil furnace in the basement. Her sense of smell was quite poor. She had remarked to a neighbour that her dog was whimpering/whining a bit in the last few days. During a very cold night when her furnace would operate much longer she died from CO poisoning!
Reply With Quote
  #12  
Old 1/10/08, 7:37 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,948
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by cbottger
Very Close I will show you: The furnace flue vent had seperated in the attic due to improper strapping and was blowing across these wires. The roof sheathing was like a rain forest and had been that way for some time. Attic was full of CO Made me dizzy before I could get out and shut the furnace off. The realtor had stated that an elderly single women had passed away in this home Makes me wonder if it was old age or CO. Hot air rises and the attic was ventilated doubt really that CO was the reason of her passing but one just never knows.
Great we all learned . The IR is a tool to help us make a decision.
Love NACHI for things like this . Thanks a heap.

...Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #13  
Old 1/10/08, 9:31 AM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,236
Default Re: Attic shot strange heat??? take a guess

Quote:
Originally Posted by cbottger
Very Close I will show you: The furnace flue vent had seperated in the attic due to improper strapping and was blowing across these wires. The roof sheathing was like a rain forest and had been that way for some time. Attic was full of CO Made me dizzy before I could get out and shut the furnace off. The realtor had stated that an elderly single women had passed away in this home Makes me wonder if it was old age or CO. Hot air rises and the attic was ventilated doubt really that CO was the reason of her passing but one just never knows.
Nicely done Charley!
Proves all isn't as it appears in infrared! We see a lot through our technology but accurately describing what is occurring is difficult.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat Recovery Systems Present Potential Fire Hazards Barrie Inspector Canadian Inspectors 1 2/1/07 4:13 AM
Attic Inspection rbritton Electrical Inspections 19 8/2/06 3:58 PM
Radiant Heat Transfer rmyers1 Structural Inspections 0 6/1/06 12:21 AM
Attic Temperatures Can Pose Serious Risks jtedesco1 Interior Inspections 4 4/2/06 11:17 AM


All times are GMT -4. The time now is 12:56 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts