Default Basement slab radiant heating problem

Had a call from a home owner. He had excessive "gurgling" in the 1st and 2nd floor circulatng hot water heating system.

He also had pipes (flexible copper) in the slab. Older (1965) split level house.

Called me to do a thermal scan to see if there was leakage in the basement slab pipes.

Found it.

He also had other problems. Newly added bathroom in the basement, but the water heater and boiler (both conventionally vented) were located behind a louvered door (bi-fold) in the bathroom.
Attached Thumbnails
basement-slab-radiant-heating-problem-dscf6006.jpg   basement-slab-radiant-heating-problem-ir_0310.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 3/7/08, 3:17 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: Basement slab radiant heating problem

Another successful IR application!

Good job Will!
Reply With Quote
  #3  
Old 3/9/08, 9:51 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Basement slab radiant heating problem

Quote:
Originally Posted by wdecker
Had a call from a home owner. He had excessive "gurgling" in the 1st and 2nd floor circulatng hot water heating system.

He also had pipes (flexible copper) in the slab. Older (1965) split level house.

Called me to do a thermal scan to see if there was leakage in the basement slab pipes.

Found it.
Did you use any other means to determine that was a water leak. Could the pipes at this part of the installation be not buried as deep in the slab, creating a "hot spot" near the surface?
Reply With Quote
  #4  
Old 3/9/08, 11:11 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Basement slab radiant heating problem

Quote:
Originally Posted by Brian A. MacNeish
Did you use any other means to determine that was a water leak. Could the pipes at this part of the installation be not buried as deep in the slab, creating a "hot spot" near the surface?
The point, if I made an error, would be of the pipes were buried too deep, not to close to the surface.

Sorry I didn't put arrows and indicators on the picture.

The intact pipe came into the bathroom (from the large, open basement rec room area, to the right of the picture) into the bathroom. The clearly delineated hot spot at the top, right, is the pipe.

Where it goes into the bathroom (lower, and to the left of the picture) we see a constriction in the pipe and then a large, diffuse area. This is the break (later, when they took of the tile and broke the concrete slab) and the leaking hot water draining into the sub-slab grave.

During the inspection, I monitored the ingoing water temp and followed the pipe's progress.

Deep probing moisture meter registered increased mositure under the tile and slab, compared to the surrounding tile.

Finally, there was a sump pump (interior drain tiles) to the north (extreme left of the picture). After about 1 1/2, the sump started draining warm water that became progressively hotter (bit not real hot). I also documented that the difuse warm area continued to grow, over time.

The hardest part was keeping the owner from walking all over the time floor (bare feet) and leaving latent heat footprints.

any other questions?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 3/9/08, 11:26 PM
Linas I. Dapkus's Avatar
Linas I. Dapkus Linas I. Dapkus is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL
Posts: 3,728
Default Re: Basement slab radiant heating problem

Quote:
any other questions?
Yeah. You didn't have a plumber contractor and HVAC specialist back up your findings??
Reply With Quote
  #6  
Old 3/10/08, 12:01 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Basement slab radiant heating problem

Quote:
Originally Posted by ldapkus
Yeah. You didn't have a plumber contractor and HVAC specialist back up your findings??
The HVAC guy told the client that it was, probably, a leaking pipe in the slab.

I was called in to find the location. I did so. I tld the client that if I couldn't locate the leak, he didn't have to pay me. Sometimes you can't localize it.

I did. I got paid.

The client called in some "handymen" to remove the tile and break the slab where I told them to.

Sure enough, a leak in the pipe.

The Handyman "fixed" it by soldering in a new section, which fixed the leak.

They will be re-pouring the floor and re-tiling, next week.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #7  
Old 3/10/08, 12:25 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 7,398
Default Re: Basement slab radiant heating problem

Good catch Will.
Reply With Quote
  #8  
Old 3/10/08, 8:06 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Basement slab radiant heating problem

Very nice detection, Will.

You've Got Mail.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
something else to chew on john bubber Structural 440 8/24/09 6:03 AM
Moisture in slabs mcyr Structural 7 8/20/07 8:33 PM
bbbb mcyr Structural 1 8/19/07 11:26 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 8:53 PM
Radiant ceiling heat? bmargiotti HVAC 12 3/21/07 1:12 PM


All times are GMT -4. The time now is 12:29 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts