Default Blower Door Testing. Please proof this new inspection article.

Blower Door Testing.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/17/10, 11:12 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Blower Door Testing. Please proof this new inspection article.

Preparation must also include inspecting for the presence of asbestos anywhere in the building envelope that could be disturbed. Also, instead of removing ashes from the fireplace or wood stove one can also cover them with wet newspaper since any remaining dust is likely to become airborne.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 9/17/10, 11:27 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Nick,

Is there any need to comment on the fact that things can be drawn into the
building enveloped such as mold, asbestos, allergens, attic dust/insulation,
pollutants, etc... ? Is the inspector liable for any of these issues? To say
these things can NEVER be drawn into the house is naive IMHO.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #4  
Old 9/17/10, 11:51 AM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Blower Door Testing. Please proof this new inspection article.

Nick,

A few items I would address in your article:

-50pa is a standard for BPI or HERS (Resnet) testing procedures. 75pa is the standard for large building (commercial and industrial) testing via ASHRAE, ASTM, USACE and AABA.
-CFM is usually only the starting point for calculations. ACH, EqLA (US and LEED), EfLA (Canadian) and a host of other numbers are usually the end result, not CFM. This also depends highly on the weatherization program as to what number is used at the end of the day. CFM @ air flow (pa is not the only one used, just the most common) is just straight air flow, where many of the other numbers take in consideration the volume or square footage of the structure.
-USACE standard is .25CFM/sq ft at .3in of water gage (75pa). 1500 CFM is a generic number that is often used for a threshold of leakage.
-ASTM (E 2178 ) standard is an air barrier not to exceed .004 CFM/sq ft at .3 in wg (75pa)
-ASTM E-779 is the actual testing procedure that is followed. It calls for an average leakage rate of no more than .25cfm/sq ft at 75pa through depressurization and pressurization. Then divide the average measured air leakage flow rate in both directions by the surface area of the enclosed envelope by the continuous air barrier of the building.
-As a side note to ASTM E-779, there was already an ASTM standard in place for use of thermography before the Resnet standard. That test has to be done in accordance with ISO 6781:1983 and ASTM C1060-90 (1997) and finally ASTM E 1186-03 is the procedure standard for air leakage site detection.
-blower doors have other uses in the clean room integrity testing and fire suppression markets. Those applications have their own set of standards and procedures.
-longer term base lines in conjunction with a longer term testing procedure can also baseline out wind (to a certain point) and other factors...including stack effect.
-In addition to air density and viscosity, items within the structure are resistant to flow and take up volume within the structure (volume is used for ACH and other related numbers). This calculation can be accomplished via the N factor calculation. Some systems have this ability built right in to the unit while others have to use external software for this calculation.
-structures with swamp coolers have to have the supply and/or returns sealed off.
-As James stated, one of the biggest safety concerns is asbestos. Those structures can only be pressurized and even then it really should be abated first.


Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Home Energy Audits
Blower Door
Cellulose Insulation Machine
Tramex Moisture Encounter Plus

Last edited by jkaylor; 9/17/10 at 12:21 PM..
Reply With Quote
  #5  
Old 9/17/10, 12:04 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
Nick,

Is there any need to comment on the fact that things can be drawn into the
building enveloped such as mold, asbestos, allergens, attic dust/insulation,
pollutants, etc... ? Is the inspector liable for any of these issues? To say
these things can NEVER be drawn into the house is naive IMHO.
This is a huge point that should be addressed within the article!

JJ
Reply With Quote
  #6  
Old 9/17/10, 12:26 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
Nick,

Is there any need to comment on the fact that things can be drawn into the
building enveloped such as mold, asbestos, allergens, attic dust/insulation,
pollutants, etc... ? Is the inspector liable for any of these issues? To say
these things can NEVER be drawn into the house is naive IMHO.
The blower door simply simulates (@50 pa) what a 20 mph wind does at one side of the side of a house. It is not creating a condition that is unknown to that environment.

What you would not know, since it cannot be seen or measured by an IR device, is the fact that the pollutants that you are referring to are continuously flowing in and out through air leaks that only a blower door can measure.

The tester does not want to dirty carpets or have draperies knock delicate things from shelves and window sills under his watch, so he will take care to ensure that the condition of the home is as he found it when he leaves. Thus, he will take care to protect these items.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #7  
Old 9/17/10, 12:32 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jbushart View Post

What you would not know, since it cannot be seen or measured by an IR device, is the fact that the pollutants that you are referring to are continuously flowing in and out through air leaks that only a blower door can measure.
That is a valid point James, but the door amplifies these effects in a big way. A BD has "better access" to interior side leaks, that wind may have little to no effect on, as far as stirring up pollutants goes. Your fireplace ash example is a good one. If you leave ashes in your fireplace the wind may blow a few in to your house. Where a blower door throws them everywhere.

JJ
Reply With Quote
  #8  
Old 9/17/10, 1:07 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jkaylor View Post
That is a valid point James, but the door amplifies these effects in a big way. A BD has "better access" to interior side leaks, that wind may have little to no effect on, as far as stirring up pollutants goes. Your fireplace ash example is a good one. If you leave ashes in your fireplace the wind may blow a few in to your house. Where a blower door throws them everywhere.

JJ
I have talked to many inspectors who will no longer perform
blower door testing because they have seen first hand the
health affects it had on their clients and even themselves.
This debate is going on behind the scenes by a lot of people.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #9  
Old 9/17/10, 1:31 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Blower Door Testing. Please proof this new inspection article.

I am with John on this one, I am not as experienced as he is, however my limited exposure to blower doors is similar. I am not sold on the benefits being greater than the risk.
Reply With Quote
  #10  
Old 9/17/10, 1:35 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
I have talked to many inspectors who will no longer perform
blower door testing because they have seen first hand the
health affects it had on their clients and even themselves.
This debate is going on behind the scenes by a lot of people.
yeah but that is highly over exaggerated by people. There were many studies done in the 90's and early 2000's on blower door usage and IAQ issues. The bottom line is the pollutants are there anyway and they need to be dealt with one way or another. If the ASTM procedures are followed, then it is basically a moot point.

The real problem in the industry I see is that people think they can just pick up a blower door, a BPI or Resnet certification and then out and get to work. A strong background or re-education in building science is a must.

JJ

Last edited by jkaylor; 9/17/10 at 1:40 PM..
Reply With Quote
  #11  
Old 9/17/10, 2:13 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Blower Door Testing. Please proof this new inspection article.

I'm sure that the guys claiming to do "energy audits" with nothing but IR cameras will oppose the use of a blower door to anyone who will listen. I just don't happen to be one.

Depressurization within the home is a naturally occurring phenomenon and the use of a blower door to measure air leakage and stop it is safe and effective. To continue to use your clothes dryer and/or air handler to suck in pollutants does nothing to help anything. Neither does taking an IR image of 10% of the 300 different points that need to be sealed.

But the most important use of the blower door comes into use AFTER the leaks are sealed and the need to determine the sufficiency of the remaining ACH to safely operate combustible devices comes into play.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #12  
Old 9/18/10, 12:31 PM
Patrick Carter's Avatar
Patrick Carter Patrick Carter is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Kansas City Area
Posts: 456
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jbushart View Post
But the most important use of the blower door comes into use AFTER the leaks are sealed and the need to determine the sufficiency of the remaining ACH to safely operate combustible devices comes into play.
I agree with this statement, but to add another point, it also assists in keeping the frauds (contractors & pretend EA's with no BD's) at a minimum (before & after tests for work completion verification), those selling and installing windows come to mind... I like IR cameras, but they are only one part of your diagnostic tool chest as an EA...
Reply With Quote
  #13  
Old 9/18/10, 1:38 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
I have talked to many inspectors who will no longer perform
blower door testing because they have seen first hand the
health affects it had on their clients and even themselves.
This debate is going on behind the scenes by a lot of people.
After many blower door tests...... probably close to 100, I have never had a problem with the above and I've worked in some pretty crappy places!!

I usually find these statements are made by people who have not experienced blower door testing and are just assuming.
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/18/10, 1:47 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by prussell View Post
After many blower door tests...... probably close to 100, I have never had a problem with the above and I've worked in some pretty crappy places!!

I usually find these statements are made by people who have not experienced blower door testing and are just assuming.
I have heard it from people that used blower doors for many years.
It is naive to say it never happens and is not a consideration. Did
you do lab test to verify your opinion?

It is common knowledge that leakage in return ducts in the basement
and crawl spaces can introduce indoor pollutants into the rest of the
home, such as dust, radon and mold spores, etc...

Why would a blower door not be capable, in some cases, of introducing
pollutants into the home?



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 9/18/10 at 2:04 PM..
Reply With Quote
  #15  
Old 9/18/10, 3:21 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
I have heard it from people that used blower doors for many years.
It is naive to say it never happens and is not a consideration. Did
you do lab test to verify your opinion?

It is common knowledge that leakage in return ducts in the basement
and crawl spaces can introduce indoor pollutants into the rest of the
home, such as dust, radon and mold spores, etc...

Why would a blower door not be capable, in some cases, of introducing
pollutants into the home?
John, first of all I never said it doesn't happen, just I have never seen it, nor have I heard of anybody in my area that has a problem with it and I belong to a couple of state wide performance organizations. Granted this subject does get brought up in training classes but it is not the problem you make it out to be.

Furthermore, anyone who gets into this business should have the proper training and related experience so if you do run into a situation like you described and you observe a condition that might be hazardous obviously you don't do the test.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New article: Blower Door Testing inxil InterNACHI & RealMatcher Blogs 0 9/17/10 3:30 AM
Aerogel: Please proof this new inspection article. gromicko Green Building Inspections 0 3/15/10 3:38 PM
Lighting Quality. Please proof this new inspection article. gromicko Green Building Inspections 0 2/26/10 11:48 AM
Roy the proof you asked for wdevries Canadian Inspectors 55 7/8/08 10:30 AM
Are electricians supposed to use these tools as per 70E? jtedesco1 Electrical Inspections 27 12/15/07 3:40 PM