Quote:
Originally Posted by prussell View Post

Furthermore, anyone who gets into this business should have the proper training and related experience so if you do run into a situation like you described and you observe a condition that might be hazardous obviously you don't do the test.
I am talking about issues being created AFTER the test, not before.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 9/18/10, 5:43 PM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
I am talking about issues being created AFTER the test, not before.
John, a blower door doesn't "create" spores, radon, etc out of thin air. The problems were already there. They have to addressed before performing the test.

JJ
Reply With Quote
  #18  
Old 9/18/10, 6:29 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jkaylor View Post
John, a blower door doesn't "create" spores, radon, etc out of thin air. The problems were already there. They have to addressed before performing the test.

JJ
If the blower door draws into the house pollutants that were
not part of the indoor environment, then the blower door
created the problem.

You can have a lot of things outside, in the attic, under the house,
and inside the walls that are not an issue until you draw them
into the indoor dwelling.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 9/18/10 at 6:33 PM..
Reply With Quote
  #19  
Old 9/18/10, 7:37 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
If the blower door draws into the house pollutants that were
not part of the indoor environment, then the blower door
created the problem.

You can have a lot of things outside, in the attic, under the house,
and inside the walls that are not an issue until you draw them
into the indoor dwelling.

You have said stupider things....much dumber things....than this. But this one is very close to the top, Bubba.

Back in the day....when you were inspecting homes....did you report to people that the home had mold in the attic, in the walls, and under the house when you saw it there....but that this was "no issue"? Did you and the real estate salesman conspire to simply omit it from the report or did you find some softer words to describe this "non-issue".

The certification class you wrote a few months after you bought your first camera....do you teach people that moisture detected in the attic, wall or under the house (since it is outside of the "indoor dwelling") is a "not an issue", too? I thought you photographed it and patted yourself on the back for saving them some money? But if mold grows from that moisture and collects within the walls, attic and below the house......that's "not an issue", eh?

When air escapes through a leaking area, Bubba, the same amount of air that leaks out is also drawn in - replaced - through leaking areas.....from the moldy attic, the moldy inner walls, and the moldy area beneath the house. This is what makes people sick, Bubba. Blower doors do not create conditions that do not already exist when the wind blows against the side of the house.

What you say is "not an issue" can actually make people sick from normal air exchange. The blower door simply measures that exchange...before and after retrofitting...by simulating a 20 mph outdoor wind (depressurization @ 50 pa).

People pay you for this advice?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 9/18/10 at 7:51 PM..
Reply With Quote
  #20  
Old 9/18/10, 8:41 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Blower Door Testing. Please proof this new inspection article.

I know very little about blower doors, so this is why I am asking this question:

Why is negative pressure used more then postive pressure with a blower door?
Reply With Quote
  #21  
Old 9/18/10, 8:48 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Blower Door Testing. Please proof this new inspection article.

Where did the author get this data?

"A 15-foot tall building with a 50º-temperature difference between the inside and outside will have a 5-pascal pressure difference from the top of the building to the bottom."

Also, I agree with some of the previous posts in regards to IAQ issues. The author might want to read chapter 10 of the Krigger book.

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared Thermographer®, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com

Last edited by krichardson; 9/18/10 at 8:51 PM..
Reply With Quote
  #22  
Old 9/19/10, 2:08 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jbushart View Post
You have said stupider things....much dumber things....than this. But this one is very close to the top, Bubba.

Back in the day....when you were inspecting homes....did you report to people that the home had mold in the attic, in the walls, and under the house when you saw it there....but that this was "no issue"? Did you and the real estate salesman conspire to simply omit it from the report or did you find some softer words to describe this "non-issue".

The certification class you wrote a few months after you bought your first camera....do you teach people that moisture detected in the attic, wall or under the house (since it is outside of the "indoor dwelling") is a "not an issue", too? I thought you photographed it and patted yourself on the back for saving them some money? But if mold grows from that moisture and collects within the walls, attic and below the house......that's "not an issue", eh?

When air escapes through a leaking area, Bubba, the same amount of air that leaks out is also drawn in - replaced - through leaking areas.....from the moldy attic, the moldy inner walls, and the moldy area beneath the house. This is what makes people sick, Bubba. Blower doors do not create conditions that do not already exist when the wind blows against the side of the house.

What you say is "not an issue" can actually make people sick from normal air exchange. The blower door simply measures that exchange...before and after retrofitting...by simulating a 20 mph outdoor wind (depressurization @ 50 pa).

People pay you for this advice?
See post #7
Quote:
Originally Posted by Jason
That is a valid point James, but the door amplifies these effects in a big way. A BD has "better access" to interior side leaks, that wind may have little to no effect on, as far as stirring up pollutants goes. Your fireplace ash example is a good one. If you leave ashes in your fireplace the wind may blow a few in to your house. Where a blower door throws them everywhere.
See post #21
Quote:
Originally Posted by Kevin
Also, I agree with some of the previous posts in regards to IAQ issues. The author might want to read chapter 10 of the Krigger book.
Some pollutants and mold are invisible or impossible to report
on during a normal home inspection. It is not even legal in
many states to report on items the require an environmental
or lab test to discern (asbestos, mold, allergens, insulation dust,
micro organism, lead dust, residue of old pesticides, etc...)

Many of these items may not be affected by outside wind most
of the time (as far entering the dwelling) A blower door sucks
INTO THE HOUSE in such a unique fashion that it cannot be
reproduced by natural wind or outdoor pressures in some
cases.

Turn on a blower door and release some smoke. Watch
the velocity as it moves. Now do it again on a windy day
and see if you can reproduce the same velocity. You
cannot.

Perhaps you were never trained in IAQ issues or building
science. It might help you to study some thing's outside
the owners manual that came with your new blower door
kit.

Survey for pollutants that may pollute the air during a
blower door test.


The problem is this... a visual survey cannot see the huge
potential and variety of pollutant issues that may be drawn
in to the dwelling. It is assumed that it will happen in such low
enough degrees that it does not matter that much. I do
not buy that premise. I have talked to too many people who
got sick or know of clients who got sick after the blower
door was run.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 9/19/10 at 2:32 AM..
Reply With Quote
  #23  
Old 9/19/10, 5:23 AM
Rodney Misener's Avatar
Rodney Misener Rodney Misener is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Pictou County, Nova Scotia
Posts: 469
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
See post #7


See post #21


Some pollutants and mold are invisible or impossible to report
on during a normal home inspection. It is not even legal in
many states to report on items the require an environmental
or lab test to discern (asbestos, mold, allergens, insulation dust,
micro organism, lead dust, residue of old pesticides, etc...)

Many of these items may not be affected by outside wind most
of the time (as far entering the dwelling) A blower door sucks
INTO THE HOUSE in such a unique fashion that it cannot be
reproduced by natural wind or outdoor pressures in some
cases.

Turn on a blower door and release some smoke. Watch
the velocity as it moves. Now do it again on a windy day
and see if you can reproduce the same velocity. You
cannot.

Perhaps you were never trained in IAQ issues or building
science. It might help you to study some thing's outside
the owners manual that came with your new blower door
kit.

Survey for pollutants that may pollute the air during a
blower door test.


The problem is this... a visual survey cannot see the huge
potential and variety of pollutant issues that may be drawn
in to the dwelling. It is assumed that it will happen in such low
enough degrees that it does not matter that much. I do
not buy that premise. I have talked to too many people who
got sick or know of clients who got sick after the blower
door was run.
I have personally done in excess of 1000 blower door tests on homes in the past 3 1/2 years, and have never had anyone come back to me saying it caused IAQ issues. However, I have refused to do blower door testing on probably a couple hundred homes over the years because of IAQ issues. It all comes down to doing a survey of the home before the testing begins and good 'ol common sense. There are hundreds of thousands of homes tested each year, if someone wants to stop doing them due to possible liability issues from IAQ, then that is more homes for the rest of us to do...go for it. Thats my 2 cents worth.



Rodney Misener, CMI
Trinity Inspection Services
Pictou County, Nova Scotia
http://www.trinityinspectionservices.com

Certified Master Inspector
Certified Level 1 Thermographer
Certified Energy Advisor
WETT eCertified Inspector
IAC2 Radon/Mold Certified
Infrared Certified
Reply With Quote
  #24  
Old 9/19/10, 5:04 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by rmisener View Post
I have personally done in excess of 1000 blower door tests on homes in the past 3 1/2 years, and have never had anyone come back to me saying it caused IAQ issues. However, I have refused to do blower door testing on probably a couple hundred homes over the years because of IAQ issues. It all comes down to doing a survey of the home before the testing begins and good 'ol common sense. There are hundreds of thousands of homes tested each year, if someone wants to stop doing them due to possible liability issues from IAQ, then that is more homes for the rest of us to do...go for it. Thats my 2 cents worth.
Sounds like 20% had IAQ that you could see. How many
have issues that cannot be seen without samples and
lab test? How many people have health issues that
show up and they do not know were their problem came
from?

I am not saying all homes will have IAQ issues, but it is
a concern to think about. Glad to see you are aware
of it when using the blower door method.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #25  
Old 9/20/10, 6:50 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jmckenna1 View Post
Sounds like 20% had IAQ that you could see. How many
have issues that cannot be seen without samples and
lab test? How many people have health issues that
show up and they do not know were their problem came
from?
John:

Don't take that 20% number and run with it. Rodney is dealing with many low income homes through a provincially funded energy retrofit program. As with poverty level owner-occupied housing anywhere, a very much higher % of all problems show up in this socially disadvantaged group.

I did the pilot project for this program under a gov contract. I now do QC under contract at varying periods. During the pilot project, in a sample of 25, there were 2 dwellings that should have been razed and new homes built but another gov dept dealing with the issues other than energy conservation does not always have the funds to build low income housing.

Last edited by Brian A. MacNeish; 9/20/10 at 9:05 PM..
Reply With Quote
  #26  
Old 9/20/10, 7:43 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Blower Door Testing. Please proof this new inspection article.

This is from the 2009 ICC residential energy code. I am attending a seminar for both commercial and residential energy codes in Nov. and will bring this subject up. I tend to think this is not the problem some make it out to be.
Also, this code covers renovation as well.
I believe NH energy code now requires pre and post blower door testing whenever an existing structure's building envelope is altered by 30% or more. This has yet to be enforced yet but will be soon.

402.4.2.1 Testing option.
Building envelope tightness
and insulation installation shall be considered acceptable
when tested air leakage is less than seven air changes per
hour (ACH) when tested with a blower door at a pressure
of 50 pascals (1 psf). Testing shall occur after rough in
and after installation of penetrations of the building
envelope, including penetrations for utilities, plumbing,
electrical, ventilation and combustion appliances.
During testing:
1. Exterior windows and doors, fireplace and stove
doors shall be closed, but not sealed;
2. Dampers shall be closed, but not sealed, including
exhaust, intake, makeup air, backdraft and flue
dampers;
3. Interior doors shall be open;
4. Exterior openings for continuous ventilation systems
and heat recovery ventilators shall be closed
and sealed;
5. Heating and cooling system(s) shall be turned off;
6. HVAC ducts shall not be sealed; and

7. Supply and return registers shall not be sealed
Reply With Quote
  #27  
Old 9/21/10, 11:58 AM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Blower Door Testing. Please proof this new inspection article.

Problem structures can often be pressurized vs depressurized.

At that point IR is out the window (very limited scanning ability)....literally.

JJ
Reply With Quote
  #28  
Old 9/21/10, 7:11 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by jkaylor View Post
Problem structures can often be pressurized vs depressurized.

At that point IR is out the window (very limited scanning ability)....literally.

JJ
Can't be true!!!.............That's going to be hard for John to take.
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 9/21/10, 7:22 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,957
Default Re: Blower Door Testing. Please proof this new inspection article.

Quote:
Originally Posted by Brian A. MacNeish View Post
Can't be true!!!.............That's going to be hard for John to take.
Don't worry, Brian. Bubba has never allowed truth or fact to interfere with his hyperbolic promotion of his IR certification class....a class he wrote and advertised for students within just a few months after buying his first camera.

No doubt that IR devices are good tools and I think that the variety of levels of skill makes certification a necessity. Their value in an energy audit, however, is over rated unless they are being used in parts of the country with severe differences in outdoor/indoor temps.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #30  
Old 9/21/10, 7:58 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Blower Door Testing. Please proof this new inspection article.

Everyone knows IR is not good in some environments. This is common knowledge.

I see James is climbing the ladder of wisdom, even though he has no IR training of any kind. He now says....

Their value in an energy audit, however, is over rated unless they are being used in parts of the country with severe differences in outdoor/indoor temps.

Several months ago James was saying that an IR camera only worked when the outdoor/indoor temps where exactly the same. Glad to see some progress.

I wonder if the need to turn on the AC or Heater constitutes the sever temp's James refers to?



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New article: Blower Door Testing inxil InterNACHI & RealMatcher Blogs 0 9/17/10 3:30 AM
Aerogel: Please proof this new inspection article. gromicko Green Building Inspections 0 3/15/10 3:38 PM
Lighting Quality. Please proof this new inspection article. gromicko Green Building Inspections 0 2/26/10 11:48 AM
Roy the proof you asked for wdevries Canadian Inspectors 55 7/8/08 10:30 AM
Are electricians supposed to use these tools as per 70E? jtedesco1 Electrical Inspections 27 12/15/07 3:40 PM


All times are GMT -4. The time now is 7:15 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts