Default Delta T

Hi Folks, I am having a real difficulty with the lack of delta T when trying to use my camera during an inspection this time of year. When there is no AC, not cool enough to run the heat with the temp outside and inside at 80 degrees. I had some success with getting in early, but hard to get RE agents on site and owners out of house at 6 AM! In the evening it just doesn't cool quick enough. I am offering a scan with each home inspection but end up looking goofy and unprofessional trying to explain why I can't scan at this time, come up with clear pics of water intrusion and spending a ton of time testing with moisture meter. Any tricks or tips?



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 5/23/09, 9:30 AM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: Delta T

Ralph,

You must establish a delta T of at least 10-15 degrees when performing an IR inspection.

I get summer month IR requests all the time, but I always ask if they have air conditioning, before I schedule the inspection. Without A/C in the summer months, you might as well put your camera way.

I'm still using my IR camera today. I had a request last week for locating hot water pipes encased in concrete and one yesterday for locating a freon leak in an A/C line.
Reply With Quote
  #3  
Old 5/23/09, 9:34 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,663
Default Re: Delta T

I showed up at an IR inspection the other morning after having the delta-t discussion with the client and he had it...the house was 82 degrees.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 5/23/09, 6:16 PM
Ron Bibler Ron Bibler is offline
InterNACHI Member
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 382
Default Re: Delta T

Get a small space heater and work each wall as needed and every floor as needed. even if it 100Degrees out you can work a wall. with a space heater.

Best

Ron
Reply With Quote
  #5  
Old 5/24/09, 8:36 AM
Ralph M. Smith Ralph M. Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 152
Default Re: Delta T

Thanks for the feedback folks. Dave, I still use my camera for showing heat loss in the heating system ducting/piping and missing ceiling/attic insulation. It just bugs the hell out of me when there is not sufficient Delta T to do a scan. Larry, LOL! Did you thank him? Ron, that would be helpful with an energy audit type application but would turn a standard inspection into an all day event. I guess I will have to deal with the limitations of the technology and the agents unwillingness to think outside the box.



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com
Reply With Quote
  #6  
Old 5/24/09, 3:13 PM
James W. Hicks James W. Hicks is offline
InterNACHI Member
 
Join Date: Mar 2009
Posts: 15
Default Re: Delta T

In my opinion, home inspection is not usually a practical use for thermal imaging. A few months ago, I purchased a Flir B-60 and took the level one training. I have used the camera on many inspections and although it has a great "Wow" factor, it still cannot beat my experience and a simple moisture meter. I have found many areas of moisture penetration which the thermal imaging had showed no sign.
The problem is of course, the lack of Delta T. In my area, where the year round temperature is close to 68-70 degrees, and there is no air conditioning, it is impractical to heat a home to 90+ degrees prior to inspecting. Even during our rare heat waves, I have found the use of thermal imaging very limited.
I have not put any effort into advertising the use of thermal imaging during inspections to avoid the embarrassment of using this "great new technology" only to show my client a blank screen. I will only bring out the camera, unannounced and when the conditions warrant it's use, which is rare.
I am scheduled to attend energy auditing training which may have a practical use for the thermal imager, but until then, I really have what amounts to a very expensive toy.
Fortunately, I am extremely busy, but if I purchased the IR camera in hopes of increasing business, I would have been very sorely disappointed. I would encourage those of you thinking about purchasing a thermal imager, to consider the limitations of the tool prior to plunking down the cash. I have no regrets for purchasing the tool. When practical, it is a great tool, unlike any other. But it is just that, a tool, when you need it it is great to have, but it certainly is not the center piece of any inspection.
I realize that two months of use is not much, and level one training is minimal. I am still experimenting with the use of the thermal imager and hope to find more uses as time goes on.
Reply With Quote
  #7  
Old 5/24/09, 3:20 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,672
Default Re: Delta T

Quote:
I am offering a scan with each home inspection but end up looking goofy and unprofessional trying to explain why I can't scan at this time, come up with clear pics of water intrusion and spending a ton of time testing with moisture meter. Any tricks or tips?
Quit giving away the IR. Only schedule it when the conditions are conducive. The national weather service (NOAA) has all kinds of charts and grafts to plan your inspection. Your IR trainer should have taught you that you can not do IR 24/7/365... If you explain the concept of IR to your client there should be no egg on your face.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #8  
Old 5/24/09, 10:53 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 7,261
Default Re: Delta T

Quote:
Originally Posted by rsmith5 View Post
Hi Folks, I am having a real difficulty with the lack of delta T when trying to use my camera during an inspection this time of year. When there is no AC, not cool enough to run the heat with the temp outside and inside at 80 degrees. I had some success with getting in early, but hard to get RE agents on site and owners out of house at 6 AM! In the evening it just doesn't cool quick enough. I am offering a scan with each home inspection but end up looking goofy and unprofessional trying to explain why I can't scan at this time, come up with clear pics of water intrusion and spending a ton of time testing with moisture meter. Any tricks or tips?
Delta T is the 900 pound gorilla that thermographers must respect.
Reply With Quote
  #9  
Old 5/24/09, 11:36 PM
Justo Mickey Rivera's Avatar
Justo Mickey Rivera Justo Mickey Rivera is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Shirley, NY
Posts: 1,309
Default Re: Delta T

Quote:
Originally Posted by jmckenna1 View Post
Delta T is the 900 pound gorilla that thermographers must respect.
I like that one

Mic



Physical strength can never permanently withstand the impact of spiritual force.
FRANKLIN D. ROOSEVELT 32nd U.S. President
Reply With Quote
  #10  
Old 5/25/09, 7:29 PM
Michael A. Gillingham Michael A. Gillingham is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Walker, IA
Posts: 23
Default Re: Delta T

Me too...John know what he is talking about on that one. All I can say is thank goodness for HVAC.
Reply With Quote
  #11  
Old 5/26/09, 12:35 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,734
Default Re: Delta T

David -

Weather charts are nice, BUT as you well know in many parts of the country there are several months where the I/S and OS are too close to get a decent Delta T / AND a Real Estate Transaction DOES NOT stand still. They had 5 / 7 / 10 days to get ALL inspections done - AND now that some RE Markets are moving again - MANY Agents and Sellers are giving no grace period. So what the man said was a real valid point.
Reply With Quote
  #12  
Old 5/26/09, 12:51 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 7,261
Default Re: Delta T

When stuck in a poor delta T condition, I choose the black & white pallet
and adjust the scan to a narrow window... in order to draw out more
anomalies. If there is just a delta T of 2 degrees between inside and
outside... you can still find defects.

Double up on the moisture meter as well.
Reply With Quote
  #13  
Old 5/26/09, 11:08 AM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 276
Default Re: Delta T

Quote:
Originally Posted by jmckenna1 View Post
When stuck in a poor delta T condition, I choose the black & white pallet
and adjust the scan to a narrow window... in order to draw out more
anomalies. If there is just a delta T of 2 degrees between inside and
outside... you can still find defects.

Double up on the moisture meter as well.
This is great advice. I prefer to use the black and white to find anomalies, then take the picture in high contrast (Fluke's high contrast). For the report I find that clients can visualize more with a vivid color palette. Black and white is by far the easiest to focus in and find problems with, IMO.

Jason Kaylor – JJ
VP of Specialty Products
877/207-1244
AC Tool Supply
Fluke Thermal Imagers
Testo Infrared Cameras
HotShot Hi-Rez Infrared Cameras

Fluke TiR1 Resources
FLIR B60 Resources
Retrotec Duct & Blower Door
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #14  
Old 5/26/09, 6:40 PM
Donald T. Belmont Donald T. Belmont is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Barre, VT
Posts: 520
Send a message via Yahoo to dbelmont
Default Re: Delta T

Things to do to get some delta T.

1. Around here the nights are generally cold enough to get plenty. Arrange to scan early even if you do the visual later on.

2. Arrange for a closed house on a hot day. (shades down, doors closed, windows closed etc) The exterior temp should rise faster then inside. I'm still experimenting with this as it depends on how hot/ how sunny outside. But it should give you a window of several hours.

3. Use a portable space heater and push heat into a wall. I use a 2 burner gas powered unit. The radiant heads will heat up a surface pretty quick.

4. Turn on the heat. As long as it's working properly there's no reason to not turn up the heat.

5. Experiment with span and range. Even under less then ideal conditions the span and range can help resolve an image. (I learned this doing horse scans.

6. As others observed use black and white.


I don't understand the embarrassment using a moisture meter. Even if I find a glaring anomaly I'm going to confirm with the meter in any case. As long as you don't overblow the IR as some magic wand then using a meter is not an issue.



Don Belmont
email: don@wisehi.com

Are your home inspections priced for profit?
The Service Business Profit Pricing Modeler can answer that question.
Easy, Fast, Accurate, Affordable
Special Pricing for InterNACHI members.
Send me a Private Message for the discount code.

WiseEyes Home and Property Inspections Inc.
Vermont Equine Thermal Imaging
Vermont Home Energy Tune-up



Reply With Quote
  #15  
Old 5/27/09, 6:52 PM
David Sorge's Avatar
David Sorge David Sorge is online now
InterNACHI Member
 
Join Date: Oct 2008
Location: Jacksonville Fl
Posts: 289
Default Re: Delta T

Quote:
Originally Posted by jmckenna1 View Post
When stuck in a poor delta T condition, I choose the black & white pallet
and adjust the scan to a narrow window... in order to draw out more
anomalies. If there is just a delta T of 2 degrees between inside and
outside... you can still find defects.

Double up on the moisture meter as well.
Ditto plus...

Its rare that I don't have an AC to play with but when I don't, I scan anyway. DT is a limitation that should be spelled out in your agreement and it is what it is on the day of the inspection. So should the fact that the use of IR doesn't imply that all defects can be discovered.

We can't find roof leaks with a standard inspection when it hasn't rained for 2 months but we don't reschedule the inspection because of it.



David Sorge (USN Retired)
NACHI / ASHI Certified
Director, Florida ASHI
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Delta Surge Protection HELP! gliebig Electrical 4 9/27/08 5:24 PM
Delta T can be tough cbottger Thermal Imaging, Infrared Cameras & Energy Audits 0 5/7/08 11:07 PM


All times are GMT -4. The time now is 8:41 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146