#1
|
||||
|
||||
|
http://www.itcnewsletter.com/2008/2008-06.htm
Check out the HVAC article. Is this distributor tube restriction? Or is this just a capacity/load change? Has anyone checked this IR test out? I have not. I do not use my IR outdoors much when it gets hot around here. I am looking for IR scans where actual HVAC diagnostic testing has confirmed the anomaly. Under charged, Over charged, low outdoor ambient, clean coil, dirty coil, high head pressure, ... Please contribute your scans and document the conditions when taken. |
|
#2
|
||||
|
||||
|
I too don't use the IR a whole lot outside on the typical brick home around here in the summer. But after seeing a few different samples of IR finding "miswired" compressors and such I have started viewing all compressor with the IR to try and learn what they typically look like and possibly find anomalies. Cannot say that I have seen anything I think is significant yet.
The talk in the article about clogs is somewhat beyond my AC knowledge. I have seen compressors where the "heat bands" are not equal, but would not feel comfortable making a call on them at this point. As far as the leaking ductwork in attics and between floors, I see that alarmingly often. I have also thought that you might be able to pick up compressor fans running too hot. Seems that on a hot day here, after running for an hour or so, most I look at seem to be 120 - 140 F. Thinking that I might see one that runs really far out of that range and be able to comment on it. Thoughts? Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#3
|
||||
|
||||
|
I have called out some motors but...
there was rust on the side of the motor from heat the amp draw was over nameplate max attached is a motor just slightly over amp draw and heat. also this is what a compressor should look like. There is obvious cool refrigerant coming into the compressor to help cool it. The cool should not reach the bottom of the compressor. this a properly operating reversing valve. Often you can not access these well. there should be a definitive line between the hot and cold stuff in the valve the refrigerant lines should be the same (depending on mode); two cold, one hot. The two of the same temp should be the same. If it is not, hot is leaking into the cool side. Last edited by dandersen; 12/9/09 at 12:24 PM.. |
|
#4
|
||||
|
||||
|
Nice pictures David, thanks.
How did you get the compressor shot? Disassemble the unit? It would seem that with some work this is an area that we could do "cool" things with IR scans. Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#5
|
||||
|
||||
|
Quote:
I have been off line for some time rain and satellites don't mix well dumped 5.2 inches of rain this morning from my Gage Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#6
|
||||
|
||||
|
Quote:
![]() David this is the image from ITC I copied and pasted it here. That image was bothering me the darker band or red just below the name plate is just about the right height for the fan blades to be moving a higher CFM across the condenser. I think the guy was totally off in his call Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#7
|
||||
|
||||
|
I have seen a lot of distributor tube restrictions in Janatrol heat pumps, because their distributor lines are as small as capillary tubes. You can see the restriction in the affected tube as well as on the coil (Frost).
Under low load conditions, the refrigerant in the condenser will slow down and begin to cool off as it passes through the circuit, giving it that striped appearance they posted in the article. The problem I'm having is that all of the stripes are equal. Restrictions are seldom equal in temperature between circuits. Now, if you had one circuit that was totally cold compared to the others, that would indicate a circuit restriction to me. I think this is just another case of factual further evaluation required and not just using IR has in evaluation of system performance. I have seen a lot of reference to identifying refrigeration leaks posted on the Internet. I have yet to figure that one out either! I am also having an issue with "blocked/dirty" condenser coils. HVAC systems change pressure/temperature/amperage draw minute by minute throughout operation. There is no way to say that any reading that you take whether it is electrical, pressure, temperature, infrared is an absolute indication of defect. It's probably a little ironic, but I have not done a lot of infrared research on the HVAC equipment like Charlie has. Maybe because subconsciously I realized the ever-changing conditions of the equipment make changes in the baseline infrared scans which make them useless. The definitive scans that I have taken (and posted above) are pretty absolute, but even the compressor gradient will change with load and length of run time from startup. I guess I'll have to start to catalog some more HVAC conditions and see what we come up with. I'm always looking for ways for home inspectors to be able to evaluate HVAC equipment without dwelling in the forbidden HVAC zone controlled by the EPA. |
|
#8
|
||||
|
||||
|
When checking an AC condenser with infrared, the coil image can tell you a lot about the condition and coolant charge. I know of no other way to detect coil restrictions.
Thermocouple, visual, non contact thermometer. Most units have at least 6 sections, each fed by small (~1/8") tubes. Photo caption says it is a 10 section coil? Is he counting stripes? I have never seen a 10 section coil in residential sized equipment that I can remember. Their size makes them vulnerable to clogging. There is almost always a filter or screen before a capillary type distributed tube and as Charlie pointed out, distributor tubes (not to be confused with capillary tubes on heat pumps) are substantially larger and not prone to blockage. If there is enough crap inside the refrigerant system to block a 1/8" tube, you have other serious problems. If several become restricted, heat dissipation and efficiency are affected. A severe condition can result in liquid coolant re-entering the compressor, This is hogwash in 99.9% of the cases. You can completely shut off the liquid line service valve and block all liquid refrigerant from leaving the condenser coil and it will not back up on the compressor unless the lines that run length exceeds the manufacturers design (in which case a receiver should have been installed in the circuit). resulting in excessive wear and premature failure. This was reported with one of the units shown. (Note: Due to variations of condenser capacity, some manufacturers may not use every coil section, and one restricted section may not constitute a problem.) Anyone have any information on this? Maybe he's talking about a section of coil not even being piped into the refrigeration circuit? A 10 section coil condenser less than one year old. This one has a normal IR signature. Some AC technicians have told me, they charge systems according to coolant line temperatures, rather than pressure. I would certainly hope that 100% rather than some of the technicians would be charging the equipment in this manner! The refrigeration gauges is not like the gas gauge in your car! But you must install them to make sure the thing doesn't blow up in your face! I often used a ΔT of the condenser coolant lines, along with heat rise, and a ΔT of the air across the evaporator coil you all know what I think about this one! to evaluate the operation of central air systems. I have also used this method on commercial chilled-water systems, and residential geothermal units. Using this method in water systems is appropriate because you only have sensible heat in a liquid state. (Of course, copper is not a great emitter. Electrical tape or adhesive paper stickers are necessary for more accurate readings.) P.S. I am not a certified thermographer. I am wondering if he is a certified HVAC Tech either?! I don't think this article is accurate and do not recommend anyone adapting this as a common practice. Last edited by dandersen; 6/10/08 at 8:22 AM.. |
|
#9
|
||||
|
||||
|
David I don't think the guy was certified anything was just listing to what he wanted to hear from some HVAC tech and he did not understand what was being stated. He was just making it up as he went along, sounded good to the unknowing person. That would of made a good field assignment to turn into ITC they would not have known the difference.
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#10
|
||||
|
||||
|
Here is one from today. Opinions? Unit was not cooling.
Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#11
|
||||
|
||||
|
Quote:
BTW a low charge of freon and a low head pressure could give the same results. Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging Last edited by cbottger; 6/11/08 at 1:07 AM.. |
|
#12
|
||||
|
||||
|
Quote:
|
|
#13
|
||||
|
||||
|
Pretty much based on it was not getting cold inside upstairs =) I don't generally try to determine 'why' it is not cooling, just don't have that expertise. But I like learning.
Also noted that the air from the conpressor fan was not hot on this unit, not transfering any heat, when i took the IR pic. Just took the pic because of this thread for you guys to look at. The one thing that seemed a little weird was that the freon line was relatively cold and sweaty (pretty hot humid day.) But there was definately no good cooling going on inside. 20 yo original unit, not in the bestof condition. Professional Inspector Level I Infrared www.AbsoluteInspections.net www.homeinspectorsplanotx.com www.homeinspectorsmckinney.com Absolute Inspections, LLC 972-463-0887 |
|
#14
|
||||
|
||||
|
Quote:
Kevin, You have one hot circuit with a too cool condenser. This would indicate a potential refrigerant distribution problem like the ITC article was trying to show. A cool/wet suction line (which intrigues me) would not be there if it was low on charge or restricted. I would say we are not picking up heat at the indoor coil (did you have air flow?). Dirty coil, frozen/iced coil. If you find out the HVAC guys findings let us know, OK? |
|
#15
|
||||
|
||||
|
I'm grabbing my horse and heading for the mountains. No phone, no internet!
Like the "gone fishing" thread, I turned down three inspections so far and I'm not gone yet! Be back next week! Keep posting pics! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Dr. Shane says every home should be tested for mold. | gromicko | Ancillary Inspection Services & Additional Topics | 106 | 6/7/09 3:36 AM |
| Attic insulation: | bclark | Interior Inspections | 3 | 2/15/08 7:17 AM |
| Reach Charlie Crist Here | pmagrone | Legislation, Licensing & Legal Issues for Inspectors | 3 | 5/4/07 9:28 AM |
| Call Charlie Crist's Office | pmagrone | Legislation, Licensing & Legal Issues for Inspectors | 1 | 5/1/07 12:20 PM |