How about this......afford what you can reasonably buy at the time......upgrade, when possible, to a point that you are satisfied for what the product does for you.
The main thing is that you know what your a looking at...........its more important to have a keen background in building science not necessarily the best tools without the brains. warm regards Jeff |
|
#32
|
||||
|
||||
|
Quote:
And, if a lug nut in an electrical panel is hot, then the wires gets hot as well. The rubber on the wire has high emissivity, even if the metal lug does not (in some cases). It is not hard to see that a hot spot needs repair. John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. |
|
#33
|
||||
|
||||
|
Quote:
Regarding electrical home inspectors.... If I had to choose between a master electrician with a FLUKE TiR and a novice Level III guy with a $50,000 FLIR... I would choose the master electrician with the FLUKE. Background knowledge makes the inspector. BTW... I have met Level III guys who said they could not do a home inspection. In fact, most of them cannot. Most Level III guys come out of other fields of use. I use a FLIR... so I am not bad mouthing them. John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. Last edited by jmckenna1; 2/18/09 at 12:45 PM.. |
|
#34
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#35
|
||||
|
||||
|
Thank you for all of your help. Even listening to you guys argue (HA HA) has shed some light on my situation. I needed to hear all of the different opinions. So the disagreements were very helpful to me. I understand the education is the key. I was just trying to keep myself from spending too little to get by then regreting it later. This help is 1 more reason to be a NACHI member.
Thanks again |
|
#36
|
|||
|
|||
|
Please Note:
OJ Utter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Here is the article that discusses the real point I was trying to make. http://utterprecision.com/download/T...onceptions.pdf
If you read the original point, I never said HI's WERE OR ARE out making FATAL mistakes, I said they could if they didn't understand or couldn't adjust for it. Enough said. I am glad this all helped Johnathan. If you would like to get a FLIR sometime; let me know. I would be honored to help. If you want a FLUKE you better call Mr. McKenna. Godspeed! OJ Utter Level 3 itc Thermographer www.utterprecision.com |
|
#37
|
||||
|
||||
|
Quote:
enjoyed the discussion. Quote:
John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. |
|
#38
|
||||
|
||||
|
Quote:
Quote:
using a FLUKE camera could possibly make a FATAL mistake, or anyone else for that matter (ie... master electrician) BTW... I do not sell cameras. John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. |
|
#39
|
||||
|
||||
|
I'm sorry John, but relying on patterns alone without accurate temperature measurement in home inspections will get one in trouble. It's that <10% of the time that can cause one improperly trained in IR for residential use that will cause the most grief in my opinion.
With pattern recognition alone, can you tell me definitively if this is a problem or not...
Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#40
|
||||
|
||||
|
Quote:
Back up John your not holding a discussion you are rattling sabers Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#41
|
|||
|
|||
|
Please Note:
OJ Utter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not quite sure why I am still beating a dead horse that is obviously been turned into glue and spread out on my little kids art project but here goes.
![]() ![]() ![]() What we are looking at is a large piece of copper with a flat piece of aluminum on top and a soldering iron heating it up. And as we all know these are the materials use for electrical connections like bus bars that I was talking about in Charley's post at the beginning. And you can see by the difference emissivity settings makes, we can see that the severity can be considered more immediate in picture 2 and even picture 3 than picture 1. And as I noted I have found connections that exceeded the 200-250 mark that failed and burnt up the wire within 3 days of scanning it, that is what I am talking about what could be a potentially fatal mistake. And as William said this is a <10% situation that can cause grief. Hopefully though, since we have covered this subject it for sure won't happen to someone. I also agree with Kevin that you generally have a higher emissivity object near to use but not always. If you have a TiR and have found a way to work around that missing issue great. It is always better to have the ability to do analysis on a situation in the field where you can do more things like add more load to the circuit, etc.... OK. At this point I will just agree to disagree on this subject cuz another bottle of glue just rolled off this post. Clank..Clank! OJ |
|
#42
|
|||
|
|||
|
You two would really benefit from reading a book by Dale Carneige called: How to Win Friends and Influence People. It has nothing to do with sales and yet, I wouldn’t be half the salesman I am, without it.
OJ, I hope you realize that you are insulting every single person that has purchased or is considering purchasing a Fluke camera? Fluke is the probably THE most trusted name in test and measurement. I would love to see you approach the electrical or HVAC/R communities and try to convince those guys that Fluke is junk. John, you are doing the same with people who have purchased FLIR cameras. I can’t figure out why the both of you deny that you are salesmen? You are both selling cameras. Embrace it, you are salesmen. Personally I would be less inclined to trust someone who says they are not a salesman (while trying to sell me something), than someone who is in sales and loves it. I get more calls about the marketing aspects of IR (which is sales) than I do about the cameras themselves. Most of those calls are from people just like those in this forum. These people are also salesmen, looking for a way to increase revenue through sales of their home inspection and/or IR business. Ultimately we could end the camera argument with either of these: http://www.aikencolon.com/Electrophysics-Hot-Shot-HD-B-Infrared-Thermal-Imager-Camera_p_1833.html http://www.aikencolon.com/Electrophysics-Hot-Shot-HD-XT-Infrared-Thermal-Imager-Camera_p_1835.html Please save your comments about the price. These blow the high-end FLIR cameras away – and for 50% of the price. I make money selling Fluke, FLIR and ElectroPhysics thermal imagers. I make money helping business owners expand their ability to generate and maintain work. I use thermal imagers, blower doors and training to do that. I am a salesman…. and I love it. Jason Kaylor – JJ VP of Sales 877/207-1244 AC Tool Supply Fluke Thermal Imagers FLIR Thermal Imagers Fluke TiR1 Resources FLIR B60 Resources Retrotec Duct & Blower Door |
|
#43
|
|||
|
|||
|
Quote:
Jason Kaylor – JJ VP of Sales 877/207-1244 AC Tool Supply Fluke Thermal Imagers FLIR Thermal Imagers Fluke TiR1 Resources FLIR B60 Resources Retrotec Duct & Blower Door |
|
#44
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#45
|
||||
|
||||
|
Quote:
With a IR thermometer or FLUKE camera, one could see the temperature of the conductors (they have good emissivity)... and with an amp meter, one could judge the load vs the heat to arrive at some conclusions. Are you saying that only a FLIR camera could be used to diagnose this issue in the picture you provide and anyone that does not use the FLIR would be open to a FATAL mistake. How would a master electrician diagnose the issue you provided in the picture? Would all master electricians that do not own a FLIR be open to FATAL mistakes? Please do not avoid my questions. John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board 25 Yrs Constr Exp - 13 Yrs Home Inspector Exp American Home Inspection - East Texas. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Mike Boyetts' electrical bond tester | jonofrey | Electrical Inspections | 18 | 2/12/09 9:58 PM |
| Flir Extech i5 We have 5 units in stock | Evan Cirelli | Thermal Imaging, Infrared Cameras & Energy Audits | 6 | 5/12/08 2:42 PM |
| EXTECH i5 From FLIR | krichardson | Thermal Imaging, Infrared Cameras & Energy Audits | 35 | 5/7/08 3:10 PM |
| EXTECH i5 on Sale Now | jmckenna1 | Thermal Imaging, Infrared Cameras & Energy Audits | 1 | 5/7/08 12:31 PM |