Default False positives

One of my biggest problems are the false positives I get from insulation issues. In cathedral ceilings, there are areas around the trusses that are hard to seal off with fiberglass batts only. These areas are frustrating as they show all over the ceiling. Prior water damage is another as the fiberglass never returns to the pre-wet condition. Did a house that near every lower chord, gusset and diagonal brace it showed cold, like it was wet. None were wet, the roof was new and when asking the owner, the ridge vent had been leaking. I determined that the water was running along the upper chord, hitting diagonal braces, soaking the insulation that would compress it to allow heat to escape. Of course I could not see it to verify. Would this be likely or is there something I am missing. I hate to assume things, but would not even had a reason to think about it without the camera. I would not even know there was anything to worry about!
Reply With Quote
Find an InterNACHI certified Maine Home Inspector (and anywhere else in North America)
  #2  
Old 4/12/09, 9:50 AM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,719
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False positives

Got any pictures Ralph?
Reply With Quote
  #3  
Old 4/14/09, 8:38 AM
Ralph Smith Ralph Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 197
Default Re: False positives

Linas, sorry about the delay. These pics have a small span to get the result. The clarity is poor when yougo from 648KB to 28KB.
Attached Thumbnails
false-positives-ir000309.jpg   false-positives-ir000311.jpg   false-positives-ir000312.jpg  
Reply With Quote
  #4  
Old 4/14/09, 2:57 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: False positives

Not always false. Remember, the camera shows HEAT, not WATER.

Cold areas CAN be water intrusion or leaks, but not always. Back it up with a deep probing water meter, ALWAYS.

Cold is not always a defect, just an indication.

Check this out. Exterior wall. What is the cause of the two cold spots?

Answer to follow once some guess.

On second thought, seems that my label gave this away.
Attached Thumbnails
false-positives-light-fixture-interior-normal.jpg   false-positives-light-fixture-interior-ir.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!

Last edited by wdecker; 4/14/09 at 2:58 PM.. Reason: Correction.
Reply With Quote
  #5  
Old 4/14/09, 3:19 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,719
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: False positives

Could it possibly be air infiltration around the exterior light and light switch???
Reply With Quote
  #6  
Old 4/14/09, 4:00 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: False positives

Quote:
Originally Posted by ldapkus View Post
Could it possibly be air infiltration around the exterior light and light switch???
You got it. Bottom was the interior light switch. The top one was an exterior light box. Cold air infiltration but no moisture.

Remember, cold means cold. If you suspect moisture. use a moisture meter.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #7  
Old 4/14/09, 6:01 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: False positives

Will is absolutely correct. Potential "false positives" are part of almost every inspection. As Will said, they are not really false positives, they are thermal anomalies that could be moisture, or could be other things. It is worse in the winter with regard to temperature anomalies that COULD be moisture. I end up carrying a moisture meter around with me through the whole house to double check all the air infiltration anomalies that are questionable. It is a little easier in the summer with regard to finding moisture, but you can still get cold spots from HVAC ductwork leaking. With experience you will get a feel for the way moisture looks and the "normal" places that you find air infiltration, but it still requires a lot of double checking.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #8  
Old 4/14/09, 6:31 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: False positives

And then we can make things more complicated by bringing in "Condensation" issues, which can be both moisture and air infiltration (cold causes high moisture readings as a result of condensation).

A "False Positive"; An incorrect result of a test which erroneously detects something when in fact it is not present.
You are not seeing a false positive because it is in fact there.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission

Last edited by dandersen; 4/14/09 at 6:38 PM..
Reply With Quote
  #9  
Old 4/16/09, 8:30 AM
David Sorge's Avatar
David Sorge David Sorge is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: Jacksonville Fl
Posts: 342
Default Re: False positives

I don't really care for the term "false positive" as David has stated but it looks like in one of those photos you're possibly looking at t-bridging from drywall fasteners close to the surface and a tie plate on a truss.

My best advice is to get used to picking these things out or you're going to be chasing your tail on every inspection. What your seeing most of the time with your camera is normal stuff...you have to learn what normal looks like. I'd also advise against using different palettes or excessive image manipulation to highlight anything. Most of the time, moisture will stick out like a sore thumb.



David Sorge (USN Retired)
FL License HI142
Infrared Certified Thermographer
Inspect-It 1st of Northeast Florida
Serving Jacksonville and surrounding communities
904-484-4847
dsorge@inspectit1st.com
http://www.dsorgeinspects.com

http://www.linkedin.com/profile?view...US&trk=tab_pro

We see RED...InfraRED



When we see RED...
You see $GREEN$


Ask us how?
Reply With Quote
  #10  
Old 4/18/09, 9:06 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,033
Default Re: False positives

When dealing with insulation, especially fiberglass, some of the delta-T's are simply the result of improper installation by installers. Many times its air pockets or simply compressed, under insulated areas or simply where insulation has fallen away from the wall cavity, especially in cathedral ceilings.

Having a keen knowledge of building principles and common practices will go along way in helping one understand what they are truly looking at, especially when dealing with insulation and framing applications.

Jeff
Reply With Quote
  #11  
Old 4/20/09, 10:18 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 1,893
Default Re: False positives

The diffuse edges around these areas are not typical of moisture. Moisture will typically give you fairly sharp, well defined, edges like what you see below.
Attached Thumbnails
false-positives-ir_0565.jpg  



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #12  
Old 4/24/09, 9:54 AM
Ralph Smith Ralph Smith is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Canastota, NY
Posts: 197
Default Re: False positives

Thanks for the feedback folks. This is a real learning process. People think you just look and report what it shows! How wrong that is!



Ralph M. Smith; CMI, CHI, CI, CEO
S.H.I.R.E. Inspection Services, Inc.
"Your Home is Our Business"
http://shireinspect.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
getting false ground... david spain Electrical Inspections 6 1/13/09 8:52 PM
False Ground / Bootleg Ground mmorris Electrical Inspections 12 5/17/07 1:11 PM
False posters rwand1 Canadian Inspectors 5 1/15/07 9:26 PM


All times are GMT -4. The time now is 4:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts