Default First IR picture for a buzzing breaker

Found 2 breakers buzzing and took an infrared picture of it.

First picture with the two wires is a double pole breaker going to the electric stove with one wire being 131 degrees and the other 86 degrees.

The second picture with four wires is one of two double pole breakers going to the electric furnace. One wire is 128 degrees and the the other wires are around 97 degrees.

Thought you might be interested.
Attached Thumbnails
first-ir-picture-buzzing-breaker-ir000221.jpg   first-ir-picture-buzzing-breaker-ir000223.jpg  
Reply With Quote
Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America)
  #2  
Old 10/20/09, 12:02 AM
mlehman mlehman is offline
New User
 
Join Date: Aug 2007
Location: la porte, IN
Posts: 79
Please Note: mlehman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: First IR picture for a buzzing breaker

Good Job Kevin!!!
Put that on the back of your Cube.
Reply With Quote
  #3  
Old 10/20/09, 12:11 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: First IR picture for a buzzing breaker

Quote:
Originally Posted by kluce View Post
Found 2 breakers buzzing and took an infrared picture of it.

First picture with the two wires is a double pole breaker going to the electric stove with one wire being 131 degrees and the other 86 degrees.

The second picture with four wires is one of two double pole breakers going to the electric furnace. One wire is 128 degrees and the the other wires are around 97 degrees.

Thought you might be interested.
Hi Kevin,

I think if you ran that info by a Licensed Electrician he may shake his head...in case you think this might be significant issue.

Circuit Breakers making noise is not uncommon, and the temperature difference is certainly nothing I would make an issue about.

Many times a loose breaker and loose connection could cause the issue, I think I would have turned the breaker off and checked the connection at the bus and conductor before having someone come to the property especially for this item.

But you may have done that....nice find though.

Never hurts to check them, that's for sure.
Reply With Quote
  #4  
Old 10/20/09, 12:20 AM
mlehman mlehman is offline
New User
 
Join Date: Aug 2007
Location: la porte, IN
Posts: 79
Please Note: mlehman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: First IR picture for a buzzing breaker

Dale, its not our job to turn anything off and check. Kevin did the right thing.
Reply With Quote
  #5  
Old 10/20/09, 12:24 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: First IR picture for a buzzing breaker

Quote:
Originally Posted by mlehman View Post
Dale, its not our job to turn anything off and check. Kevin did the right thing.
You do what you feel is right, and I'll do what I feel is right.

It might be the reason I have other Inspectors working for me and am booked a week in advance every month of the year...try it, you may like it.

PS. I have called Paul Abernathy years ago about this exact issue, I posted what Paul told me, I learned something that day, just passing the info along to someone who may not know the reasons stated above.
Reply With Quote
  #6  
Old 10/20/09, 12:36 AM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: First IR picture for a buzzing breaker

Quote:
Originally Posted by mlehman View Post
Dale, its not our job to turn anything off and check. Kevin did the right thing.
Funny, sounds like an inspector's version of building code. "I inspected your house to the standards I am legally required to meet."

To each his own though. To exceed or not to exceed.
Reply With Quote
  #7  
Old 10/20/09, 12:53 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: First IR picture for a buzzing breaker

Good job.

BTW... what was the ambient temperature?



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 10/20/09 at 12:58 AM..
Reply With Quote
  #8  
Old 10/20/09, 1:00 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: First IR picture for a buzzing breaker

Quote:
Originally Posted by jmckenna1 View Post
Good job.

BTW... what was the ambient temperature?
127---
Reply With Quote
  #9  
Old 10/20/09, 1:19 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,851
Default Re: First IR picture for a buzzing breaker

Quote:
Originally Posted by dduffy View Post
Hi Kevin,

I think if you ran that info by a Licensed Electrician he may shake his head...in case you think this might be significant issue.

Circuit Breakers making noise is not uncommon, and the temperature difference is certainly nothing I would make an issue about.

Many times a loose breaker and loose connection could cause the issue, I think I would have turned the breaker off and checked the connection at the bus and conductor before having someone come to the property especially for this item.

But you may have done that....nice find though.

Never hurts to check them, that's for sure.
Sound advice Dale!





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #10  
Old 10/20/09, 4:59 PM
kluce kluce is offline
Active Poster
 
Join Date: Oct 2003
Location: Highland, Indiana
Posts: 265
Please Note: kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: First IR picture for a buzzing breaker

Quote:
Originally Posted by dduffy View Post
Hi Kevin,

I think if you ran that info by a Licensed Electrician he may shake his head...in case you think this might be significant issue.

Circuit Breakers making noise is not uncommon, and the temperature difference is certainly nothing I would make an issue about.

Many times a loose breaker and loose connection could cause the issue, I think I would have turned the breaker off and checked the connection at the bus and conductor before having someone come to the property especially for this item.

But you may have done that....nice find though.

Never hurts to check them, that's for sure.
It sounds like you would handle this differently than I am. In my opinion, the buzzing sound by itself is a red flag. Something is causing that buzzing sound and if it is from a loose connection, it should be addressed. It sounds like we can agree that the sound and one of the two legs being hotter than the other leg is likely due to a poor connection. While I did take an amp reading on each leg and tried to tighten the screw connection, I do not turn power off to a circuit and remove breakers to inspect, adjust and/or clean the connections. Regarding the IR picture, I feel the picture gives my client a good visual understanding then trying to explain amperage to her.

Regarding this comment
Quote:
It might be the reason I have other Inspectors working for me and am booked a week in advance every month of the year...try it, you may like it.
I hope this comment doesn't make you feel superior? Because having employees by itself doesn't mean **** in my eyes.


Best to all.

Last edited by kluce; 10/20/09 at 5:02 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Breaker Question rsole Electrical Inspections 6 11/23/08 9:57 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM
Double Tapped Breaker tjohnson3 Electrical Inspections 8 4/20/07 9:04 AM


All times are GMT -4. The time now is 5:43 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts