Default Heat Vents

During a new-construction inspection a few weeks ago I found this "hot spot," created from the water heater vent traveling up through the second floor.

The heater had only been operating for a few minutes and I suggested that the vent clearances may not have been maintained.

As it turned out (I learned today), the builder opened up this wall to find that the B-vent hadn't been properly secured in the wall cavity and was in direct contact with the drywall.
Attached Thumbnails
heat-vents-bwv3.jpg   heat-vents-bwv2.jpg   heat-vents-bwv4.jpg   heat-vents-bwv1.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 2/12/08 at 11:56 PM..
Reply With Quote
  #2  
Old 2/13/08, 12:21 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,749
Default Re: Heat Vents

Wow...



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #3  
Old 2/13/08, 12:45 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,526
Default Re: Heat Vents

Quote:
Originally Posted by bkelly2
Wow...
Good catch, Jeff.

also look for furnace vents and, I don't know if you have these in California, steam or hot water pipes for steam or circulating hot water heating systems.

I once found a leaking steam pipe in the wall of an old condo conversion. The whole wall was hot. Old plaster and lathe. I will see if I can find it and post it.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #4  
Old 2/13/08, 1:15 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Heat Vents

I take all kinds of pictures
Attached Thumbnails
heat-vents-manif1.jpg   heat-vents-manif2.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 2/13/08, 11:15 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 7,398
Default Re: Heat Vents

Good catch.
Reply With Quote
  #6  
Old 2/14/08, 6:50 PM
Jeremiah Anderson's Avatar
Jeremiah Anderson Jeremiah Anderson is offline
InterNACHI Member
 
Join Date: May 2003
Location: Blaine, MN
Posts: 54
Default Re: Heat Vents

Great catch, glad to hear that the problem was resolved.
Reply With Quote
  #7  
Old 6/29/08, 10:32 PM
Justin Watts Justin Watts is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Rancho Santa Margarita, CA
Posts: 762
Default Re: Heat Vents

Hey Jeff,
I really like the FLIR... Do you charge your clients extra for using it on inspections?????? I am assuming that most inspectors will be using them in the future, and the prices are already coming down due to competition.

I think FLIR's are great screening tools, I am sure there will be some legal issues in the future once more inspectors are using them.... Its a fine line between finding concealed defects, and not finding them..... And I am sure inspectors will come under scrutiny in the future. Ofcourse we come under scrutiny for visible defects as well.

Please do let me know if you charge extra for a FLIR inspection..
Thanks!
Justin

Last edited by jwatts1; 6/29/08 at 10:35 PM..
Reply With Quote
  #8  
Old 6/30/08, 12:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Heat Vents

Quote:
Originally Posted by jwatts1
Hey Jeff,
I really like the FLIR... Do you charge your clients extra for using it on inspections??????
I use it as just another tool. The client isn't given a choice as to whether or not I use it, so I don't charge an additional fee for inclusion of thermal imaging.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Services & Additional Topics 12 2/13/08 12:33 PM
efficiency of 15 yr old peerless afrost HVAC 11 11/19/07 10:51 AM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
Second thoughts about Transite heat vents kswift HVAC 6 6/14/06 9:55 PM
Radiant Heat Transfer rmyers1 Structural 0 6/1/06 12:21 AM


All times are GMT -4. The time now is 12:45 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts