Default Hot!

What might cause this?

hot-ir000659.jpeg



Inspecting Norfolk and Hampton Roads
www.procraftinspections.com

Energy Audits in Norfolk

www.procraftgreen.com
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/7/11, 8:15 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Hot!

Loose connection?
Reply With Quote
  #3  
Old 11/7/11, 8:44 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,196
Default Re: Hot!

Quote:
Originally Posted by ldapkus1 View Post
Loose connection?
My thought also.
Reply With Quote
  #4  
Old 11/7/11, 9:01 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Hot!

So why aren't the bare conductors "hot"?




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #5  
Old 11/7/11, 10:04 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,187
Default Re: Hot!

They're poor emitters and are reflecting the background.
Reply With Quote
  #6  
Old 11/7/11, 10:40 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Hot!

Quote:
Originally Posted by ldapkus1 View Post
They're poor emitters and are reflecting the background.
At the same color range?
You would think they would be different to some degree. The wire sheath and metal would reflect different.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #7  
Old 11/7/11, 10:42 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Hot!

Whats the possibility of OX paste on the wire preventing the exposed alum from showing a heat reading?




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 11/7/11, 11:15 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Hot!

Quote:
Originally Posted by bbrinke View Post
What might cause this?

Attachment 49542
Probably a loose or high resistance connection at the terminal. It would be easier to determine without the fusion. Would like to see a plain IR image with more of the conductor showing. You will likely see rapid heat dissipation the further you move up the conductor away from the connection.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #9  
Old 11/7/11, 11:17 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Hot!

Quote:
Originally Posted by wwarner View Post
So why aren't the bare conductors "hot"?
My money says it is. But why doesn't it look like it is?



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #10  
Old 11/8/11, 3:49 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hot!

My money is on a loose terminal and a time factor but just guessing I would think the amp load had just been increased and the wire itself had not had time to heat as much as the loose terminal connection and the outer insulation. Would be nice to know the amp draw and when it was applied was it a constant load or variable inquiring minds want to know



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 11/8/11, 4:55 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Hot!

Quote:
Originally Posted by cbottger View Post
My money is on a loose terminal and a time factor but just guessing I would think the amp load had just been increased and the wire itself had not had time to heat as much as the loose terminal connection and the outer insulation. Would be nice to know the amp draw and when it was applied was it a constant load or variable inquiring minds want to know
Yup...


Is the lug really that hot or are we seeing part of a reflection from some other heat source like an incandescent bulb above the panel or behind the inspector? What was the reflected background temp measurements?

Interesting thermal exception that sure leads to a lot of additional unanswered questions!

Give a man a fish, he eats for a day... teach a man to fish, he eats for a lifetime.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #12  
Old 11/8/11, 5:54 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,196
Default Re: Hot!

Quote:
Originally Posted by wwarner View Post

Give a man a fish, he eats for a day... teach a man to fish, he eats for a lifetime.
Only if he can find a shovel to dig the worms!
Reply With Quote
  #13  
Old 11/8/11, 6:07 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Hot!

Quote:
Originally Posted by jjonas View Post
Only if he can find a shovel to dig the worms!
Well... true dat!




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/8/11, 6:11 PM
Brad Brinke Brad Brinke is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Hampton Roads, VA
Posts: 189
Default Re: Hot!

Thanks for the responses fellas. I took several pictures at different angles and the temp never changed on the lug. The breaker for the water heater was in the 150 degree range as well. This was actually a re-inspection after it was "fixed" from about a month ago. You can see the other side is not warm at all. There was a small amount of OX paste on the wire. I sent this image to the electrician so he could see what I was looking at.



Inspecting Norfolk and Hampton Roads
www.procraftinspections.com

Energy Audits in Norfolk

www.procraftgreen.com
Reply With Quote
  #15  
Old 11/8/11, 6:25 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hot!

Quote:
Originally Posted by bbrinke View Post
Thanks for the responses fellas. I took several pictures at different angles and the temp never changed on the lug. The breaker for the water heater was in the 150 degree range as well. This was actually a re-inspection after it was "fixed" from about a month ago. You can see the other side is not warm at all. There was a small amount of OX paste on the wire. I sent this image to the electrician so he could see what I was looking at.
Nothing takes the place of being on site all we can do is guess



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 8:11 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts