David,

I don't understand your focus on the screw or the presumption that the screw is probably loose and the source of the problem. You seem to be missing the obvious here. You already know that indirect reading of the surface of the breaker is, itself, yielding excessive temperatures.

The screw is showing hot because it provides the most accurate direct reading of the temperature that is occurring in the panel. While the buss itself is polished, low emissivity and highly reflective of the much lower ambient temperatures and cooler specific objects in the garage, hence it is a very poor source for obtaining the most accurate temps in the panel. While the screw which secures the buss to the non-conductive back plane is dark in color (high emissivity) and not very reflective, hence it provides a much closer representation of the maximum temperatures being obtained inside the panel. If the buss and screw were both black bodies, I would expect them to yield the same apparent temperature. When you were a little tyke, the nurse took your temperature in your butt, not because she thought there was something wrong with it, but because it yielded the most accurate/reliable reading.

I don't take service load readings during home inspections, so no matter how many times or how many ways you ask for that information, you will not get it here. Nor is it necessary to make the appropriate assessment.

The 800lb gorilla in the room is that components in the panel are too hot (by a large margin) and that an in-depth analysis and diagnosis by a licensed, qualified electrician is warranted. Do you really think that the electrician who is not a thermographer is going to consider your assertion more credible because you make references to reflected apparent temperature inside a garage?

Notice that there's a gorilla standing in front of you, don't get caught up in trying to figure out what kind of fleas he has.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 4/24/09 at 10:28 PM..
Reply With Quote
Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America)
  #32  
Old 4/25/09, 5:05 AM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Electrical Service

Quote:
Originally Posted by dandersen View Post

David,

Where do you find the tool above?



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #33  
Old 4/25/09, 11:33 AM
Jason Kaylor Jason Kaylor is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Tempe, AZ
Posts: 970
Send a message via Yahoo to jkaylor
Default Re: Hot Electrical Service

Probably from FLIR John, it has an ITC label on it.

Jason Kaylor – JJ
VP of Sales
877/207-1244
AC Tool Supply
Fluke Thermal Imagers
Fluke TiR Infrared Camera
HotShot Hi-Rez Infrared Cameras

Testo 880 3 Infrared Cameras
Testo 327 Combustion Analyzers
Retrotec Duct & Blower Door
Reply With Quote
  #34  
Old 4/26/09, 5:54 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,924
Default Re: Hot Electrical Service

Quote:
Originally Posted by jmckenna1 View Post
David,

Where do you find the tool above?
John, Don't concern yourself with it.
It's just something some guy with a PhD in Physics threw together.

Chuck has made it all too clear that Home Inspectors are above all this crap.
Quote:
I don't take service load readings during home inspections, so no matter how many times or how many ways you ask for that information, you will not get it here. Nor is it necessary to make the appropriate assessment.
Check in with him and see how he does it.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #35  
Old 4/26/09, 9:45 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Electrical Service

Chuck,

Good find. It was an easy call with an IR camera. Not much to
question about it.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
Secured electrical service hmcbride Electrical Inspections 10 9/26/08 3:24 PM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM
NACHI.TV producing "Panel from Hell" show: How to inspect an electrical service panel gromicko Miscellaneous Discussion for Inspectors 17 12/5/07 2:32 PM
question on electrical service Coral Chesney Electrical Inspections 6 2/24/07 9:35 AM


All times are GMT -4. The time now is 5:51 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts