If the conductor Delta-T is 900 degrees above ambient, do you think it's an issue?

I exaggerated, it was really only 870 above ambient. Captured video too.

Had to terminate the inspection because I couldn't finish after turning off the power to the house. Corporate owned relo. Could have easily caused a fire if not found





Video here http://www.youtube.com/watch?v=NHWQOgyRRrw

.
Reply With Quote
Find an InterNACHI certified Connecticut Home Inspector (and anywhere else in North America)
  #2  
Old 11/4/09, 9:42 PM
Kevin R. Weiss Kevin R. Weiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 842
Default Re: Hot wiring in service panel (with video)

I don't know Chuck, don't over step your bounds.....you should probably pulls some breakers and confirm things....

Or from those that don't like IR like you and I, "I could have found that without IR."



Nice find and pics. Better than me, I only found two moisture issues today with my camera.



Kevin Weiss

Professional Inspector
Infrared Imaging Specialist
www.AbsoluteInspections.net
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #3  
Old 11/4/09, 10:36 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is online now
InterNACHI Member
 
Join Date: Sep 2009
Location: Knoxville TN
Posts: 92
Default Re: Hot wiring in service panel (with video)

I like the crispy wires. What would cause a neutral to get so hot?



Sean Fogarty
Fogarty Home Inspection Services
Providing home inspections, Mold Testing and Radon Testing for Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397
www.homeinspectorknoxville.com
Reply With Quote
  #4  
Old 11/5/09, 10:40 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 693
Default Re: Hot wiring in service panel (with video)

Quote:
Originally Posted by kweiss View Post
I don't know Chuck, don't over step your bounds.....you should probably pulls some breakers and confirm things....

Or from those that don't like IR like you and I, "I could have found that without IR."



Nice find and pics. Better than me, I only found two moisture issues today with my camera.
It was obvious to the eye as soon as you looked into the panel, but I couldn't have quantified it without IR.
Reply With Quote
  #5  
Old 11/5/09, 11:25 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,708
Default Re: Hot wiring in service panel (with video)

Quote:
Originally Posted by sfogarty View Post
I like the crispy wires. What would cause a neutral to get so hot?
Dbl tapping the neutral wires.
Causes loose connections.
May produce 240 VAC at the connection...

Good example to keep handy for your reports.

But then everyone knows there isn't any voltage on white wires!!!???

Quote:
It was obvious to the eye as soon as you looked into the panel, but I couldn't have quantified it without IR.
You can't tell if it "is" hot by looking at it, now can we?!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Panel Surround / Exposed Wiring Question thance Electrical 11 2/19/08 10:06 PM
Service Panel Started Fire mashburn Electrical 14 3/30/07 11:12 AM
Electrical Inspection with Temp. Service? dandersen Electrical 16 6/27/06 11:41 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:56 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts